Freezers Logo
Posted on Nov 01, 2007
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
Normal operating pressures
I have a victory 2 door freezer. r-404a freon, cap tube system.
what is normal pressures
thanx steve
John Tripp
Level 3:
  • Master 4,656 Answers
  • Posted on Nov 02, 2007
John Tripp
Master
Level 3:
Answers
4656
Questions
Helped
1679249
Points
14883
Normal operating pressures will change as the freezer reaches the selected temperatures on the inside. Normals of minus 14 degrees on the inside would be around minus 4 psi on the suction and 150 pis on discharge. Now checking the pressure will require a set of guages that have been purged with the same freon before connecting with the suction line on freezer. If not purged the suction line will draw outside air into the system and cause freezing of air and moisture inside the capillary tube rendering the freezer inoperative, Hope this helps, Sea Breeze
What should the refrigerant pressures be on a reach in freezer that uses 404A refrigerant
Generally, low side is around 20-25 PSI and High side is about 235-250 when unit is close to operating temp. Expansion device effects this to some degree such as a cap tube can restrict and affect pressures as well as the amount of the charge in the system. Compressor efficiency is another.
Jan 19, 2018 • Freezers
Continental Freezer model F2 404A refrigerant not cooling properly. Replaced cap tube, and filter drier, evacuated, and charged. Box temp not going below 32' and ice forming at beginning of evaporator....
Check the compressor efficiency. See if it will pump down. In most cases, a good compressor will pull down to about 15" vacuum. Also, be sure that the refrigerant amount was weighed in and not done by pressures only.
1helpful
What is the normal operational pressure in lo/hi side at the compressor of commercial freezer like dispaly case, reach in cabinet or other any low temp refrigeration uses 502 or408A/404a. is there any rule...
why yes there is. Generally speaking, the head pressure should be around the "ambient +30" rule.
That is, measure the entering air temp to the condenser, say 75 degrees. Now add 30 to that and get 105 degrees. Look at a P/T chart and see what the pressure is for that temp which is about 253 for R-404-A.
The evap on a freezer leads the load so, as a general rule, the evap temp is going to be around minus 10 degrees to get a 0 degree box. Coolers are different. So, the pressure for a minus 10 evap is around 25 or so. But the unit has to be close to operating temp. If the box is warm, naturally the pressure is higher. And what influences the pressure is whether or not it's a TXV or a cap tube system.
If a TXV and no receiver, charge by subcooling. If a receiver, fill by sight glass. If Cap tube, charge by superheat.
Hope that answers your question.
Need to know the design superheat also normal pressures on this unit with 404A refrigerant
The McCall web site has nothing easily found on the 7-7045FT unit.
In answer to you questions, first, what is the expansion device. TXV, Cap Tube, or something else?
Low site pressure will be dictated by the super heat. The high side, in many cases, is usually ambient plus 30, then convert to psi.
Let me know if you need more info. And please double check the model number/ serial numbers.
good luck
I have a ice maker that keep freezing up. the pressures are 50/280 its a 404a system. what are the normal pressures
For a 404 system pressures should be about 60/350 Remember when you recharged always with the freon drum upsidedown so liquid gas is going in to the system.But if it's freezing up could be the thermostat or the timer or the heaters.
11helpful
3answers
Normal Operating pressure for true 2 door Freezer R404A Room Under 80 degrees F Box at -10 degrees F
The pressures depend, somewhat, on the expansion device,i.e. a TXV or Cap Tube. Take a pressure reading, then convert it to a temperature. The evap temp should be right at 10 colder than the box temp. Remember, heat flows to cold so the evap has to "Lead the Load" in order to cool. In many cases, the condensing pressure is usually ambient temp, plus 30, then convert to a pressure. These are general accepted practices that have been used for many years.
Hope this helps
2helpful
My freezer will not hold temperature. Only a year
If what you say is accurate, I would look at either a weak compressor or and issue with the expansion device. (Cap tube, TXV)
What are your pressures and what freon are you using? Does the door(s) seal tight?
4helpful
Evaporator unit keeps on building ice. question what is the nornal operating pressure on low side and on the high side for truee freezer using 404 refrigerant
I'll try to give you the "Readers Digest" version.
First, make sure there is no ice build up on the evap. Light frost is O.K. as long as it does not effect air flow. (Very Important). All fans need to be running. Again, an air flow thing. There should be some product in the box but not too close to the evap. Again, an air flow thing.
The expansion device can effect your pressures to some degree i.e. Cap tube vs. TXV.
As a general rule of thumb, which I use almost everyday when it comes to pressures:
Low side is based on the temp difference between evap temp and condition space in the box. In freezers, it is almost always 10 degrees. If the box is 0 degrees then the evap needs to be at a minus 10 degrees. That is a pressure for R-404A of 24.5 psi. This only holds true when the temp in the box is approching set temp. I would say, about +10 degrees. 0 Degrees for the evap for R-404A is 33.5 psi.
High side should be ambient temp +30 degrees and then convert to a pressure for the refrigerant.
Example: 75 degrees in the room, +30 degrees equals 105 degrees. Now 105 degrees converted to a R-404A pressure is 253 psi. This will get you very close to the desired high side pressure.
I would look at low side first to see if it is within reason. Don't let the high side get too high. Increases the compression ratio and overworks the compressor.
Your icing problem could be a defrost issue and not a refrigerant charge issue.
Good Luck and hope this gets you started.
1helpful
Errattic temperatures in Freezer
Check out "victory-refrig.com" for manuals, diagrams, etc.
Cap tube systems are "critical charge systems". Can be difficult to get right. You did not mention pressures that you had. The split on the evap vs.box temp is almost always 10 degrees for freezers. If you want a -10 box, your evap needs to be -20. As a general rule of thumb, you want the high side to be "ambient +30". This seems to work most every time. Your problem might be operations related. Them leaving the door open alot and so on. It could also be a problem with the evap fan or the control to it. It could also be that since there had been a problem with the unit, they are now constantly checking it. Could be checking during a defrost cycle. When your box is at 0 degrees, your pressure should be about a -10 and no less that a -15 degree for the evap. You may have to babysit this thing and see how far it will pull down. You may have a weak compressor. Also, I have had many Hobart freezers fail due to dirty condensers. This causes the oil in cap tube systems to gel and clog up the cap tubes. The only fix is replacing the cap tube. There are alot of variables here so be patient, it's not going to be a quick fix. One last thing, since R404A can fractionate, you really need to pull the charge out and weigh in the correct charge with virgin refrigerant. This will eliminate 2 things. 1, it will ensure the correct amount of refrigerant and, 2 no chance of having a poor mixture of refrigerant in the system causing inconsistant readings and performance.
Hope this helps. And remember, cap tube systems are performance measured by the amount of superheat just prior to the unit making temp and cutting off.
Top Freezers Experts
ADMIN Eric
ADMIN Eric
ADMIN Andrew
ADMIN Andrew
Are you a Freezer Expert? Answer questions, earn points and help others