Leviton 8599 GFCI Receptacle Logo
A
Anonymous Posted on Jun 18, 2011
I have 2 gfi outdoor outlet with orange lights on and cannot reset
A
Anonymous
GFCI is designed to detect ground faults, and will not reset if ground fault is detected, or if device is bad.
Seems odd that both GFCIs will not reset unless both are outside.
If GFCI is outside, they get dirty and wet, and the GFCI goes bad.
If GFCI will not reset, open following links:
http://waterheatertimer.org/pdf/GFCI-outlet-will-not-reset.pdf
http://waterheatertimer.org/How-to-wire-GFCI.html
I plugged a 30 amp power supply cord from an rv to a 15 amp house outlet to run a/c to rv . gfci tripped and wont reset. damaged gfci or something else?
A GFI outlet works independently of sensing an overload condition. Overloads are dealt with by the circuit breaker or fuse in your electrical panel. The GFI simply compares the current on the hot terminal (black or red wire) with the current on the neutral terminal (white or gray wire) and interrupts the current if there is more than 5mA (0.005 Amps) difference between the two.
Remove the load - in this case the RV plug - from the GFI outlet and attempt a reset. Make sure you're pressing the RESET button and not the TEST button. If it resets - you're all set. Reconnect the RV plug to a different outlet - preferably NOT a GFI type.
If it still wont reset, it is important to know that GFI outlets can be wired in such a way that any circuit extended to other outlets (lights, too) via the LOAD terminal screws will also be protected by the GFI. We need to be sure that there wasn't something else causing the fault. Check other nearby outlets for functionality. Remove plugs from any outlet found not working and attempt to reset again.
If it will not reset - it is possible that the internal sensing circuitry has been damaged due to such a large amount of current trying to pass. In this case, replacing the GFI outlet will be needed.
My microwave is not heating
Are you sure you have power at the outlet? If not check your circut breaker box. You may have a GFI circut. The GFI outlets are very sensitive. They have reset button and test button. If other "non GFI" outlets are on the same cirute they are affected by the GFI outlet. The GFI outlets do fail at times, and need to be replaced. Have you had recent power outage? Sometimes our "smart devices" are too smart.
If you have power, I'd unplug for a few hours and see if that might reset it's "brain" If that doesn't help you may have a panel problem. Owner's manual? Check troubleshooting section. Warranty?, pursue that. Age of microwave? Consider the cost of repair vs. finding a lightly used "working" microwave.
Is a house plug with a cfic braker light suppose to be red or green
Most are green when functioning properly. Many have no lights at all. Try depressing the reset and see if the outlet works again. If not there are other things to look for. Often times one GFI outlet feeds multiple more outlets from the "load" connection on the back side of the GFI. If there is something wet, overloading the rating, or something with a fault in any of the outlets multipled off the single GFI it will trip. Disconnect all devices then attempt to reset. If that doesn't work and you possess some electrical skills pull the GFI outlet and disconnect the wires going to the "load" connection (While power is off) Re-energize and attempt to reset the GFI Outlet. If it resets your problem is beyond that outlet in the circuit of what you disconnect. You may not have found all the affected outlets. FYI if you have a 15amp GFI the rule of thumb is you can put more devices on outlets working off or through the GFI that add up to more than 1500 watts. If it is a 20amp GFI a quick rule of thumb is no load over 2000 watts. Space heaters, blow dryers, and hair curlers are often 1800 watts each. One alone and can trip a 15 amp GFI.
1helpful
Home fuse box breaker issue
Hi Rex,
It sounds as if the upstairs bathroom outlet and the outdoor outlet are on the same circuit. There's a very good chance that these are GFI or "ground fault interrupter" type outlets, as these locations (and others) have required this type of protection for over 30 years. It was a common practice to run a circuit from the panel to one of these locations (or another) and then run from here to the next outlet and then on to the next. Since the GFI outlet could be purchased for around $10 instead of $30 for a GFI breaker, electricians would install outlets instead - both offered the same protection. A "regular" breaker would supply power to this circuit - but the very first outlet would get a GFI type outlet. It would be wired to the LINE terminals and the cable that feeds the rest of the outlets on this circuit would be connected to the LOAD terminals. If there was a ground fault condition, this GFI outlet would trip, but the circuit breaker would remain on. You would locate and RESET the tripped GFI outlet to restore power. The only time the circuit breaker would trip is if the circuit was overloaded. Overloads would NOT cause the GFI outlet to trip.
Now that you understand how it was typically wired years ago (and still a lot of times today), you should check all the outlets outside your home, in bathrooms, basements, garages, and inside your home next to doorways that lead directly to grade of your lawn or deck. These are required places for GFI protection. Press the RESET on any tripped GFI outlet to restore power. If the outlet will not RESET, there is a condition where the hot wire (black, red or blue insulated wire) is in contact with ground, or a device or appliance connected to the circuit has a problem. Unplug anything connected to the circuit and attempt to RESET again. If still unable to reset, open the outdoor outlet again and carefully pull it out and away from the box. Inspected for damaged or crushed insulation and repair / tape as needed. Before reinstalling, try to reset again. If it holds, trip the GFI by pressing TEST button. The RESET button should pop out. Reinstall the outlet and make sure the wires are not crushed or cut. Press the RESET button again. If it trips, you will have to remove the outlet again and take more precautions against damage to the insulation. it is also possible that the GFI outlet itself has failed, in which case it should be replaced.
GFI circuit breakers and outlets are supposed to be tested monthly by simply pressing the TEST button and then the RESET button. Replace any GFI device that does not test correctly if wiring and devices / appliances connected are OK.
I hope this helps & good luck! Please rate my reply - thanks.
Jan 05, 2012 • Hammering
All circuit breakers good in box. have no power to 3 rooms on outlets or lights . problem started when using a hair dryer hooked too a drop cord in a outlet
the first thing that I would check is to see if there is a GFI outlet inline with the other outlets that are not working,, if there is one then check to see if you can reset it using the little reset button -- if by using the reset button does not fix this problem then there is the chance that the GFI outlet is bad and needs to be replaced. the next thing that comes to mind is that you said the breakers in the box are good, but I have seen sometimes where you need to flip the breaker totally off and then back on and this could reset the breaker. if you are still having troubles then the problem could be that one of the outlets in line has gone bad and needs to be replaced or the breaker in the box could also be bad ( use a meter to check that you have power on the output side of the breaker and trace from there from outlet to outlet until you find the bad one ) ---- could also be just a bad wire and while testing with your meter you should find it as you test the wires to the outlets.
c...
3helpful
2answers
Outdoor electric recepticle GFI tripped (I'm guessing during recent rain) and will not reset. Would this indicate faulty GFI or something wrong in system. This was installed about 2 yrs. ago and has been...
if the outlet was wired right and working fine before -- then ' yes ' the GFI has tripped and it could have failed do to the rain. replace the outlet with a new GFI outlet and I would also suggest that since you have the outlet outside that you install it into a outdoor weather proof outlet box.
c...
Rule H53sp-24 pool cover pump trips GFI breaker
GFI devices are prone to degrade over time. Also, when used outdoors there are additional moisture issues that may cause sufficient current leakage to trip the breaker.
I had a similar problem this Spring. I was using a 20 amp GFI "master" outlet that protected two additional outlets 'downstream' of it (wired to the 'load' terminals on the GFI outlet- I'd have the check the doc. to see what terminology was used here). The pump was plugged into one of the downstream outlets.
Replacing the GFI seemed to solve the problem. I did ante up $20 for an 'outdoor' model of the 20 amp GFI unit, several bucks more than the standard 'indoor' unit - have no ideal if that represented additional value or not.
Note also, that this is the third such pump I have used for my pool cover. The other two failed to come on at all after about a year's use. The mfg replaced them under warranty (I may have had to send back the old pump - I forget!).
Curtis
3helpful
NO POWER
do any of the lights come on when you press the power button? if nothing comes on, then check the GFI outlet and see if it has tripped. quick check would be to unplug the washer from the wall and plug in a lamp. if the lamp doesn't work either, then the outlet doesn't have power.
either the GFI needs to be reset or the circuit breaker at the main panel needs to be reset. one GFI will control a couple of outlets that could be exposed to water (eg, bathrooms, laundry rooms, outdoors, etc). you'll need to find the one and hit the RESET button on the outlet.
if the GFI outlet is reset and still no power to the lamp, then find the circuit breaker panel (usually in a garage, basement or outdoors). open the door and see if one of the breakers has tripped. reset it (or replace if its an old style glass fuse) and see if power is now restored to the outlet cause the lamp now lights up.
if power is there to the outlet, but the washer still will not come on (and either work or display error codes), then one more thing to check is the connection at the machine/motor control unit (connector P13 at the unit). disconnect the washer from the wall outlet. to access P13, you'll have to remove the top console panel (its the one that has all on the buttons on it). its held on with 3 screws on the back that you can get to from the top (no need to move the washer out from the wall). loosen the screws, tip the the panel forward and lift it up. it will be connected to the computer board, so just move it out of the way. P13 will have the large black wires going to it. give it a push to see if its not locked in place. if you hear a "click", then it was not properly connected. you can remove it and reinstall it if you want, but make sure the machine is not plugged into the wall outlet.
put the console back together, plug the washer in and see if it works. if it still doesn't power up, then sounds like the computer board is dead and you'll need a new one. its about $150 from searspartsonline. replacing it is easy, but sears may pay $150 towards labor and $100 towards parts. give them a call.
good luck.
Outdoor outlet
If this is an outdoor outlet and was built a little over a year ago it will most likely have a GFI (ground fault interrupter). There are two push buttons right on your outlet. By pushing one of them it should reset it
good luck-------------tomtaso
Dec 15, 2007 • Dryers
Top Leviton Electrical Supplies Experts
john h
Sean Wright
Sean Wright
CJ Rock
CJ Rock
Are you a Leviton Electrical Supply Expert? Answer questions, earn points and help others