First are you sure the other outlet is actually grounded?
Article 250.130 (C) Non grounding Receptacle Replacement or Branch Circuit extensions.
The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connect to any of the following.
(1) Any accessible point on the grounding electrode system as described in 250.50
(2) Any accessible pint on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the branch circuit for that receptacle or branch circuit originates.
(4) For grounded systems, the grounded service conductor within the service equipment enclosure.
(5) For ungrounded systems, the grounding terminal bar within the service equipment enclosure.
Or you can see 406.3(D) replacing with a ground fault receptacle
I am sure the "grounded outlet" is in fact grounded. I tested it.
I appreciate the code references but don't really understand what they say.
Can I do what I originally proposed?
Tom Rohr
If you noet item 3, it sould go to the gronding bar where your circuit originates. If your grounding conductor on the grounded receptacle that you propose goes back to this same point, then it should be ok. If in fact your grounded receptacle is grounded to some other point (like a water line) then no, you should run a grounding conductor back to the source and connect to the equipemnt grounding terminal. The other safety option would be to install a GFCI receptacle and label it as ungrounded. This is also permissable. Oh and wasnt' that effort worth more than one thumb???
Thank you.
You response will solve my problem. Yes. You are right. The first answer should be more than one thumb.
With this second response, let's make it a full four thumbs.
Tom Rohr
×