Siemens main breaker won't shut off. It's a 200

the breaker needs to be replaced, sometimes you could take the back of a screwdriver and tap the front of the breaker and that may help release the mechanism but more than likely you will have to replace
9/30/2010 1:32:12 AM • Siemens Main... • Answered on Sep 30, 2010
0helpful
1answer

Have 15 amp siemens breakers

This does not appear to be an issue with the current recall action. (More info here: http://www.usa.siemens.com/pluginrecall )

Please contact an authorized electrician for assistance diagnosing your issue.
9/23/2010 6:51:57 PM • Siemens 2 single... • Answered on Sep 23, 2010
0helpful
1answer

Is there a recall on

Hi. I'm a Siemens employee directly involved in helping customers with this situation. You may check the following website for information on the breakers affected. Please use the response form there if you need further assistance:

www.usa.siemens.com/pluginrecall

Also, you may check with your local distributors for assistance with replacements. They have quarantined the affected breakers and should be able to sell existing unaffected stock.

https://www.sea.siemens.com/us/Sales/Pages/Distributor-Locator.aspx

Enter your zip code and choose Residential Products or Murray depending on the branding of your circuit breaker.
9/23/2010 6:49:44 PM • Siemens 2 single... • Answered on Sep 23, 2010
0helpful
1answer

I want internal diagram or application of simens

The replacement for the 3UN8004 is a 3RN1010-1CM00 Here is a linke to the Siemens manual for this newer version.
http://support.automation.siemens.com/WW/adsearch/pdfviewer.aspx?HitsPerSite=10&ehbid=html_76%2Fehb%2F35681283%2Ehtm&lang=en&nodeid=38823237&siteid=cseus&query=3RN1010-1CM00 &page=1&view=new
8/27/2010 1:26:03 AM • Siemens... • Answered on Aug 27, 2010
0helpful
1answer

When i download the hw conf. in the plc im151

Re-check your hardware configuration.Make sure you correctly configured each slot ast to the type of hardware that is there. Make sure your program is not calling for a function (block transfer etc) to a module that isn't there.
7/25/2010 3:26:09 PM • Siemens ENERGY &... • Answered on Jul 25, 2010
0helpful
1answer

Need to know how to wire 50amp 220v breaker into a

It depends on the type of panel. Hook the breaker to the hooks that run along the out side of the bus area, then If it's a stab lock panel just snap the breaker down into place. If it's a bolt on panel once you have pushed the breaker down into place you'll need to start and tighten the screws that connect it to the bus, at your experience level DO NOT try to connect the breaker with the power on. Once the breaker is in place connect one of the hot wires to each of the breakers lugs. If you have a Neutral (white) connect it to the Neutal bus first. If this is a sub panel with a separate ground bus you'll need to connect the gound there.
If your hooking up a motor and it runs backwards just reverse two of the hot leads.
7/7/2010 3:09:16 AM • Siemens 100 Amp... • Answered on Jul 07, 2010
0helpful
1answer

Coiled neutral out of arc fault breaker is hot and

The white coiled wire should be connected to the neutral bar with all the other white wires. The neutral from the circuit it controls should then be connected to the breaker. If you're reading your meter between the hot conductor (black wire) and the neutral (white wire) that would be normal. If you remove the wire from your neutral bar to test it, and you have a load on the circuit you will be reading voltage out through your load and back on the neutral and it would "appear" to be hot. But why would you remove the white wire? What is the original problem, is the breaker triping?
7/1/2010 5:25:39 AM • Siemens Seimens... • Answered on Jul 01, 2010
0helpful
1answer

Half of the appliances and outlets quit working

Go to your electrical panel and check your circuit breakers. You can check each one by turning each breaker off - then back on again. You should get back some of your electricity. Also, you probably have a GFI circuit breaker located in your kitchen (near the sink) and in your bathroom's (near the sink/basin). Make sure to push in the reset button (make sure it holds when you press it in). This will explain why you have some receptacles that are out in other parts of your house.  Why receptacles are wired through GFI's, etc... are to provide extra grounding protection. I hope this works for you. If not, feel free to contact me again with more information. Good Luck to you!
5/25/2010 10:54:45 PM • Siemens #MP120GF... • Answered on May 25, 2010
0helpful
1answer

HOW TO WIRE

A single pole ground fault breaker has a screw terminal on one side for the black wire to the ciorcuit, a white curly pigtail that goes to the panel neutral/ground bar, and a screw terminal near the white wire for the white neutral wire from the circuit.

A 2 pole GFI breaker is similar, But it has another screw terminal for the other hot wire in the circuit.
For a 220 volt, 2 pole, GFI protected circuit, you need to run a 4 wire cable. black, red, white, green.

Please Vote !!
5/15/2010 9:35:38 PM • Siemens 50 Amp... • Answered on May 15, 2010
0helpful
1answer

What does bq mean

BQ means it's a bolt-on type circuit breaker.
4/10/2010 2:55:54 PM • Siemens /ite Bq... • Answered on Apr 10, 2010
0helpful
1answer

Siemens mccb vl160x is not holding its on position

Sounds like a bad breaker. Sometimes, breakers appear to be in a trip position, but they're actually in the on position. If you've had this breaker working for a while, and it began tripping under load - then I'd replace it. If you just purchased this breaker and are assuming it's not holding in the on position, then I'd install it - because it could just appear that way. Or, you can bring it to your local electrical supply store for a second opinion. They're pretty knowledgeable, and will help you for free. But, giving you credit - I'm sure it's a bad breaker. This is usually a pretty good indicator of it going bad. If you have any further questions, etc. that you'd like to ask or share - feel free to contact me again and I would be willing to help you. Good Luck! Jim
4/7/2010 8:40:16 PM • Siemens /ITE... • Answered on Apr 07, 2010
0helpful
1answer

We have a wet location with a need for a 3 pole 30

I see you're looking for a 3 pole 30 amp Siemens BL cir. brkr.? I don't believe they make a this type of breaker in a 3 pole. In a 2 pole yes, but not a 3 pole. Also, I see on top of your message, it says Siemens #MP120GF 20 amp SP GFI Breaker. Now, if this is what you're looking for, I do know they have one. If you're working out of a home, I'm sure you have a 240 volt service, and a 3 pole wouldn't work here anyway. I'm just checking, but do feel free to contact me for this, or any other questions you may have. Good Luck to you, and I hope I was able to help you in some way. - Jim
4/4/2010 10:00:30 PM • Siemens #MP120GF... • Answered on Apr 04, 2010
0helpful
1answer

Are washing machines required to be on arch fault in orlando fl

No! I know for sure out here in California it's NO for sure. But as a licensed electrician over the years, anytime you have a device (such as a motor) that is plugged into a receptacle that has arc fault protection, ground fault protection, etc. - you run into the problem of these breakers tripping at a high rate. Now, I'm not sure why this arc fault protection breaker was put in the first place? But I'd be interested in hearing the reasoning behind it (such as for natural gas, etc). A regular circuit breaker should be sufficient enough, and if you have any further question's, etc. - feel free to contact me again. Good Luck to you, and I hope this has helped you. - Jim  
4/4/2010 8:59:59 PM • Siemens 20Amp... • Answered on Apr 04, 2010
0helpful
1answer

Need star delta control wiring daigram

49fb442.jpg STAR/DELTA MOTOR WIRING.
This is the wiring you need to follow.
2/11/2010 6:58:48 AM • Siemens Seimens... • Answered on Feb 11, 2010
0helpful
1answer

Can't find any ite bl circuit breakers.

YOU CAN CALL ITE FOR A DEALER NEAR YOU
1/8/2010 4:32:04 PM • Siemens /ITE... • Answered on Jan 08, 2010
0helpful
1answer

20 amp breaker pops with only a light (60watts)

I have been an electrician for 11 years and when these breakers came out in 2005 what a nightmare. These circuit breakers are extremely sensitive. They are designed to sense loose connections and to protect your house from fires caused by them. By increasing the load (ie. more lights or tv) it increases the size of the "arc" created by the loose connection and the circuit breaker trips before the 20 amp maximum. What I normally find as the cause is a loose connection in one of the receptacles or switches on the circuit. A lot of times, installers will use the "quick stab" inserts on the back of the outlets or switches instead of the side screws. Usually, if you "side screw" all of the receptacles and switches it will resolve the nuisance tripping. One other item that can cause them to trip is too many dimmers on the arc circuit but it doesn't sound like that is the problem you're having.
11/16/2009 6:11:51 AM • Siemens 20Amp... • Answered on Nov 16, 2009
0helpful
1answer

How to install arc fault circuit interrupter

connect the neutral from the circuit to the afci breaker, and run the neutral that came on the afci breaker to the neutral bar in the panel. Make sure that the neutral that you connect from the circuit to the afci breaker is the one that belongs to the circuit that you're protecting or the afci wont work.
10/10/2009 3:53:39 PM • Siemens Seimens... • Answered on Oct 10, 2009
0helpful
1answer

I tried to replace my 15 amp 2 pole breaker with a

probably picked up wrong breaker for panel put then side by side for comparison if not same return get correct one
10/7/2009 3:00:33 PM • Siemens... • Answered on Oct 07, 2009
0helpful
1answer

240 w/60 a outside breaker with test switch wont'

Inside the controller box is a red button to reset it but most likely the heater element is shorted out so replace the heater element first. Cost $100.00 at any pool or spa shop. Post here if you need more help.
9/28/2009 1:24:36 AM • Siemens 12 ... • Answered on Sep 28, 2009
0helpful
1answer

Wiring diagram

What are you doing???

Are you installing a 220 V GFI breaker in your main or sub panel?

Judging by the picture, you have a breaker that wants to have a direct connection to the ground buss. Have you tried that?

I have some experience with a similar CH breaker. I installed the breaker, hooked the two wires representing the line to the breaker, put the white to the neutral buss bar and everything was cool.

Let me know what happens

A
9/21/2009 2:50:18 AM • Siemens #MP120GF... • Answered on Sep 21, 2009
Not finding what you are looking for?
Siemens Logo

119 questions posted

Ask a Question

Usually answered in minutes!

Top Siemens Electrical Supplies Experts

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

CJ Rock
CJ Rock

Level 3 Expert

4429 Answers

Are you a Siemens Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...