Siemens QF230A keeps tripping after installation.

So likely you have a 3 wire dryer cord and a 3 wire branch circuit. The dryer neutral is bonded to the dryer frame and the third wire of the dryer plug.

There were code exceptions for dryers and stoves that allowed timer motor circuits to use the neutral as a current carrier and frame ground.

To use the GFCI for the dryer you will be required to add an additional conductor (new 3 wire+ground cable) and separate the neutral to frame bond in the dryer and use a 4 wire dryer cord.

Likely you also have some GFCI single pole breakers and replaced ungrounded receptacles with grounded (another code exception) and they work OK. The dryer and stove are different as there is current on the third wire where as on the ungrounded receptacle GFCI there is no 3rd wire.

In breif, the neutral (current carrier conductor) from the dryer must be isolated from the dryer frame and dryer ground (fault current carrier conductor).

Or just leave it the way it was.

Check with local authority with jurisdiction for local code requirements.
6/24/2020 10:23:46 PM • Siemens... • 166 views • 1 helpful votes
0helpful
2answers

Main breakers keeps blowing what is the reason i

Add up all the amps from active breakers. Do they add up over 200? If not, then I suspect a bad main breaker. If they do, then you need a larger service box and or main breaker.
9/24/2017 4:21:02 PM • Siemens 200 Amp... • 617 views • 0 helpful votes
1helpful
1answer

How do I lock out a 200 amp Siemens circuit breaker ?

Check garvin Industries website. they offer a multiple of different lock systems for breakers
8/23/2017 3:44:39 PM • Siemens... • 322 views • 1 helpful votes
0helpful
1answer

Siemens 200amp Load Centre will not reset and no power to box after a short in the bathroom?

It sounds like the breaker at the metering base is tripped. You will need to locate the meter base outside to find the breaker. You can also call your local utility company service provider and report a power outage. they typically will come out free of charge to verify power.
4/17/2017 5:42:03 AM • Siemens... • 252 views • 0 helpful votes
1helpful
1answer

I have a Siemens Outdoor Load Center W0408ML1125. It has the neutral bar but not the ground bar. Where do I attach the ground?

Yes it's correct the Ground Bar connects to the metal box, scrape some paint off to make a good bond, this also requires 4 wires to be correct, green ground, white insulated neutral, black L1 and red L2
2/24/2015 2:27:40 AM • Siemens... • 1,375 views • 1 helpful votes
0helpful
1answer

What are the circuit breaker part numbers for a Siemens Ite G3030MB1200 Panel

Go to any home store and ask them, they will have the breaker or one to use as a replacement
9/4/2014 4:13:36 PM • Siemens... • 527 views • 0 helpful votes
0helpful
1answer

I had a house inspection and in the main panel I have a 20 amp QT breaker that is rated from 15-35. I have a 20 gauge wire and and a 15 gauge wire running to this breaker. Inspector says I need a 15

He is correct. I'll not go into the particulars but the fact is, you have two separate circuits connected to the same breaker. Separate the two circuits by installing another 15-Amp breaker. Although I understand your situation, please understand wire gauge and electrical amperage are two different animals. Breakers are rated in Amperage and electrical conductors are sized by wire gauge. That said, the 20 gauge wire you speak of is actually a 12 gauge conductor and the 15 gauge wire as you say is a 14 gauge conductor. Have a good day.
8/30/2014 3:34:13 PM • Siemens Ite Twin... • 210 views • 0 helpful votes
0helpful
1answer

Need a Wiring diagram for w0204ml1060u

4/26/2014 7:40:14 PM • Siemens... • 390 views • 0 helpful votes
0helpful
1answer

20 amp AFCI

The breaker has gone bad . You no longer have arc fault protection .
3/18/2014 5:13:59 PM • Siemens 2 single... • 150 views • 0 helpful votes
0helpful
1answer

NEC code for 50 amp service panel

Don't think there is one that small. Are you asking the right question?
2/22/2014 6:44:50 PM • Siemens... • 146 views • 0 helpful votes
0helpful
1answer

Circuit breaker amp

3200 watts or 1600 watts on each terminal.
12/15/2013 10:07:00 PM • Siemens Ite Twin... • 228 views • 0 helpful votes
0helpful
2answers
1helpful
1answer

Installing arc fault interrupter with ground fault

Question is vague. Arc fault and ground fault are slightly different.Are you installing arc fault breaker?http://waterheatertimer.org/How-to-wire-GFCI.html#arc-faulthttp://waterheatertimer.org/How-to-replace-circuit-breaker.htmlCode says Maximum 12 boxes per circuit breaker.Arc fault breaker and GFCI outlet in bathroom?>>> do not connect this way.Do not install 2 fault protections on same circuit.Install the arc fault circuit breaker, and then remove bathroom GFCI, and replace with ordinary outlet, or switch-outlet.How many outlets can be connected to a bathroom GFCI?It depends on total boxes on circuit.Count the boxes. Max 12 boxes per circuit breaker.How many amps can be connected to 15 amp device?15 x 80% = 12 ampsElectricians use 80% rule to calculate safe maximumhttp://waterheatertimer.org/Color-codewire.htmlhttp://waterheatertimer.org/See-inside-main-breaker-box.htmlAdd a comment If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
4/21/2013 9:45:46 PM • Siemens Seimens... • 468 views • 1 helpful votes
0helpful
1answer

Activating shunt trip circuit on vl160n

A shunt is always energized and it has a purpose. The purpose is to bypass some of the load from the main circuit. It would be tripping due to overload
4/26/2013 8:37:40 AM • Siemens... • 330 views • 0 helpful votes
1helpful
1answer

Installing arc fault interrupter with ground fault

If you meant arch fault with ground fault then no, the two types interfere with each other and trip the breaker as one senses an arch and the other grounding. If you meant ground fault breaker with a GFCI. receptacle, you only need one of the two, either GFCI. breaker or receptacle. and for circuits, you can put up to 12 devices (i.e receptacle, light)assuming they consume 1 amp each. Anything over 12 amps or 80% of the rating on the breaker, it will trip/reset. Or if your talking about wires on a breaker then no more than 2 wires recommended. Try adding a junction box outside the panel if your trying to add other branch circuits or tap off of a receptacle.
4/21/2013 9:44:09 PM • Siemens Seimens... • 272 views • 1 helpful votes
0helpful
1answer

Breaker tripped and when reset still no power to outlets. there are 2 with gfci and 2 without niether gfci will reset whats up?

reset the GFCI and they will all work. The other two are down stream from the gfci.
1/5/2013 9:46:45 PM • Siemens... • 537 views • 0 helpful votes
0helpful
1answer

The breaker has 2 lugs for installing a

Yes.See illustrations.http://waterheatertimer.org/How-to-wire-GFCI.html#arc-faultYou have arc-fault breaker with GFCI protection that also mitigates effect of arcing fault. If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
11/8/2012 3:39:36 PM • Siemens Seimens... • 118 views • 0 helpful votes
0helpful
1answer

I have a siemens 40-200 panel. There are 7 knob & tube circuits still in the house that aren't accessible to rewire. Been told that GFI breakers connected to these circuits will pass code. any

Yeah, as long as you run your GFI's on the same circuit then you would probably be good. I say "probably" because I do not know your local codes, but for places I know it would be. Hope I could help.
9/17/2012 2:43:27 AM • Siemens 20Amp... • 337 views • 0 helpful votes
Not finding what you are looking for?
Siemens Logo

119 questions posted

Ask a Question

Usually answered in minutes!

Top Siemens Electrical Supplies Experts

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

CJ Rock
CJ Rock

Level 3 Expert

4429 Answers

Are you a Siemens Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...