2answers

I have a dayton model 3e240e propane heater. I have replaced the thermocouple and the gas valve and burner will not ignite. The pilot lights and stays lit. The fan works as well. All what am I missing?

A safety is holding out the main gas valve from opening when call for heat ,check all safety switches to make sure they are closed
3/9/2019 11:54:45 PM • Dayton Heating &... • Answered on Mar 09, 2019
0helpful
1answer

What is the proper high limit fan setting for a 1994 York Stellar gas furnace? It is currently set to 150 and that allows it to run on a 10 mins on/4 mins off cycle. Is that about right?

The High temperature limit controls how much heat your furnace will deliver. The higher the temperature the hotter the air it delivers. At the same time, the higher the temperature, the hotter the exhaust that is wasted energy. The amount of heat you need relates to outside temperature. Some more sophisticated controls would adjust the high limit to change with outside temperature However, with a fixed limit, the lower the limit the more efficient your operation. If you are looking for maximum efficiency, then you should lower the limit to the point where the fan runs continuously on a cold day. If the fan shuts down, it means that you are making more heat in the furnace than you need. You might want to change the high limit to be higher in the colder part of the winter when you need maximum heat, and then lower it when the outside temperature worms up. If you are getting adequate heat at 150 Deg. you should not go higher, because the higher the limit, the lower the efficiency and the greater the stress on the furnace.
3/2/2019 7:27:53 PM • Dayton Gas... • Answered on Mar 02, 2019
0answers
0helpful
1answer

Dayton LR22132 4hp motor can it be rewired to 120v

No.
2/10/2019 7:21:07 PM • Dayton Heating &... • Answered on Feb 10, 2019
0helpful
1answer

How to hook up a Dayton heavy duty electric unit heater 2YU69 to a external thermostat (Nema 4x, SPDT line voltage part# 4E636 Voltage 24-277 Vac

I am seeing that this tstat says it handles 24-277 volts but when specs are pulled this tstat is a high voltage tstat. Obviously it could be done but what you really need is a simple 24 volt tstat wired to r and w. You can also get a tstat that doesnt have batteries if you wired in the C terminal.
2/8/2019 1:33:29 AM • Dayton Heating &... • Answered on Feb 08, 2019
0helpful
1answer

Have only two wires for my 480 which block terminals to use top and bottom ? its a dayton 2yu63

Doesn't matter, both work correctly. This is for looping the wires through, but both are connected internally.
1/16/2019 1:00:01 PM • Dayton Heating &... • Answered on Jan 16, 2019
0helpful
1answer

Just acquired dayton heater I know where hot leads connect where do neutral and ground connect

Usually the nutural is in the power cord box beside the hot. The ground is also there but is a screw that you fatsen the ground to
1/15/2019 4:12:49 AM • Dayton Heating &... • Answered on Jan 15, 2019
0helpful
3answers

I have Dayton 3E250 ceiling hung heater. It was originally LP but was converted to NG. I want to convert it back to LP. Does the gas valve also need to be replaced? Thanks

if its a dual setup no if it was changed out before than yes need different valve unit
12/19/2018 9:14:20 PM • Dayton Heating &... • Answered on Dec 19, 2018
0helpful
1answer

I need a manual for a Dayton 4LX56 heater

try dayton or online search using make and model
12/13/2018 1:45:11 PM • Dayton Heating &... • Answered on Dec 13, 2018
Not finding what you are looking for?
Dayton Logo

1,144 questions posted

Ask a Question

Usually answered in minutes!

Top Dayton Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Brad Brown

Level 3 Expert

19187 Answers

ZJ Limited
ZJ Limited

Level 3 Expert

17989 Answers

Are you a Dayton Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...