Condenser Fan and Compressor not turning on.

This is an older model 38L carrier a/c unit. The condenser fan was stopping after about twenty minutes of operation. I replaced the condenser fan and the 30uf/5uf dual run capacitor, with no results. I next replaced the motor start capacitor, with no results. The contactor is engaged when powered up, but nothing happens, no humming, nothing. I rechecked my connections, fuse box, etc. The schematic is too worn to read on the service panel, any help would be appreciated. -Jim

  • 1 more comment 
  • Anonymous Jul 08, 2010

    Hello augie, no results means what? The new motor does the same thing or runs for 20min & shuts down Does the compressor run?

  • augie1458 Jul 08, 2010

    martin, Sorry, The new motor makes no attempt to turn on, it is not receiving power. The compressor does not run either. They were both operational last week. When I turn the thermostat on, in my house to cool, the contactor is engaged outside on the unit , but neither motor turns on. I was careful to make notes for the connections on the dual run capacitor. Could it be wired differently? I used the same Dayton motor that was in unit. Any info is appreciated.-augie

  • Anonymous Jul 08, 2010

    Jim DO you have a volt meter?Check for power at the contactor.Is there power to the unit ?Check the curcit breaker in the house panel & check the disconnect box next to the unit outside for 220volts.

×

1 Answer

Thomas Woodburn

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Carrier Master 2,638 Answers
  • Posted on Jun 05, 2017
Thomas Woodburn
Carrier Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Mar 07, 2016
Answers
2638
Questions
1
Helped
1251992
Points
7008

Are you sure you have high voltage going to the unit? One wire from fan lands on top left of contactor, the other two go to C and Fan on capacitor. Manually push in contactor, if no fan than no high voltage.

If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79

  • Thomas Woodburn
    Thomas Woodburn Jun 05, 2017

    Also make sure you have the jumper from the top right of contactor to the C on capacitor

×

5 Related Answers

Anonymous

  • 182 Answers
  • Posted on Jul 29, 2008

SOURCE: Carrier Synergy 2000 Condenser fan does not turn on

the mfd is stamped on the side of the capacitor.Be careful to kill the power and to NOT touch the terminals.The capacitor is capable of holding a charge even after power is disconnected.

Ad

HANK MCNEIL

  • 252 Answers
  • Posted on Sep 07, 2009

SOURCE: Carrier AC condenser unit stopped working. Power

if all is as you say you probably have a bad "dual motor run capacitor"

Anonymous

  • 1515 Answers
  • Posted on Jan 22, 2010

SOURCE: We require condenser fan motors for Interclisa

Hi, this is an odd voltage 380 volts. Is it a 3 phase unit? To get a 220 volt 50hz condenser fan motor, you will have to go through a refrigeration/air conditioning parts house and order this. 60hz you would have no problem finding one in stock. Carrier is a good unit, and have been around for many years. You shouldn't have any problems locating one.
Sincerely,
Shastalaker7
PS You will need to go through a wholesale parts house.

Anonymous

  • 7 Answers
  • Posted on Apr 15, 2010

SOURCE: the condenser fan for carrier xarios 300 is not

there is a run capacitor is probably bad.
you can purchase a replacement one from slakey brothers. However the capacitor will still have a charge after the power and wires are removed. after turning off the breaker use a long bladed screw driver and ground the electrical leads to discharge the capacitor before removing. take it with you to the supply house along with the model and serial number of the condensing unit.

Anonymous

  • 77 Answers
  • Posted on Jan 20, 2011

SOURCE: Carrier Model 38YCC030300 Completely frozen up Fan

Usually air fond froze if not moving enough air inside I.e. Dirty filter Or plugged coil ......or low on refrigerant

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

2helpful
2answers
1helpful
1answer

My son has a noisy condenser fan on the carrier condensing unit, model is a BRC060360 and Im puzzled on this unit seer rating, any ideas? Also looking for a budget condenser fan for it?

Condenser fans are usually not very expensive, so I suggest you go to a carrier dealer and buy one as a spare part. Have you check that the fan is clean and none of the blades are damaged.
0helpful
1answer

When the heater is on, should the fan outside on top of the unit also be working along with the blower from the heater ? When the heater is off, cold air is comming from the vent's, can I cover the

No. This is strictly a gas package unit, not a heat pump. the condenser fan motor should NOT run when their is a call for heat from the thermostat. The condenser fan only runs with the compressor on a call for cooling. Hopefully the compressor is not running @ the same time, but if it is, it would make sense that the contactor for the compressor & condenser fan motor is stuck closed OR the low voltage cooling wires are shorted straight to a 24Volt control wire.
0helpful
1answer

Carrier model 38cks air conditioner compressor fan

sounds like you need to replace the condenser fan motor. It has a thermal overload inside the compressor and will shut it off before it harms the compressor. The only way to get it to reset is cool down the compressor with a water hose.
0helpful
2answers

Power went out for 3 seconds electric storm warnings but did not see/hear any lightning strikes. Central air-conditioning fans spins But the compressor doesn't turn on. There is one condenser and looks...

During these storms power gets shut down fora sec and comes back with a tsunami type surge. why? Because the generators are going full blast at the electrical plant in your area. No load is applied anf they sky rocket into Zapland babes! Any slight glitch or momentary outage causes a surge. It goes away but it comes back with a fury. So if your AC's run cap is a little old and tired from workin that condenser like it ain't not thang, Then the resulting surge will zap that puppy and it will look like this:
themobilian_2930.jpgRemove the power from the outside unit and look at that capacitor. It prob has went under. If it is leaky or preggers, it is bad. Replace it and party on! More here

If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61

0helpful
2answers

AC Condenser motor will stop at 1pm but inside unit is still running but no AC. If I turn the AC unit breaker unit off and then an hour later turn it back on. The unit runs fine all day until 1pm. Had a...

Hi, the tech should have been able to figure the stat out with out a manual to see why the condenser is shutting off at 1:00 P.M. This is unusual for this to happen, unless it was winter and this is a heat-pump going into defrost, but just the fan would shut down. Does this unit have a box on it that was installed by your electric company that shuts the unit off during high peak conditions in the summer? This would cause it to shut down at the same time everyday. If not, it would have to be something in the thermostat that is set for it to shut off at that time. It still does not make since, as it would shut both the indoor and outdoor unit off, not just the condenser. Are you saying that just the condenser fan motor is shutting off, but the compressor continues to run until it shuts off on high head pressure when the fan stops, or does the complete outdoor unit shut down fan, compressor and all at that time??. It sounds to me like this outdoor unit has a time delay relay that has a fault in it may be shutting it off at this time daily? Please let me know if its just the condenser fan motor that shuts off, or if the complete unit is shutting off all together, this will help .
Sincerely,
Shastalaker7
A/C, Heating,
0helpful
2answers

I live in south texas overnight the ac stopped GOODMAN MODEL

Is the condenser fan (outside) turning? You mention that it's hot but don't say if it's turning or not.

These fan motors normally run pretty hot, but not so much that they shut down due to internal thermal overload protectors.

Both the compressor and the fan have termperature overload protectors to keep them from burning out the motor in the event of an overheated condition. The condenser fan must be running or high freon pressure will put an excessive load on the compressor and it will 'kick out' the high-temp overload protector.

Turn off the unit by pulling the outside disconnect (in a small box near the outside compressor unit) or flip the AC breakers in the breaker box. Wait about 30 minutes for the unit to cool off and turn it back on. If the compressor and fan both run for awhile then kick back off, or the fan motor seems to be working under excessive strain, you've probably got a bad motor start condenser (inside the unit) that little round can that is connected through the fan motor wiring. If it's swollen or leaking, it's almost surely defective and even if it's not, excessive load on the motor is a classic sign of a bad start condenser.

You can usually find these at electrical supply stores, well-stocked hardware stores, or most certainly at an HVAC parts house. Be sure to replace the old one with one of the EXACT same value (in voltage and Microfarads (mF) capacity. The shape may be a little different, but as long as the electrical characteristics are the same and is rated at the same or higher voltage than the original, it will work.

Connect the new condenser, mount it to the frame, and restart the unit. This should take care of the problem.

Hope this helps.
1helpful
1answer

Evaporator fan turns on. compressor and condenser fan do not turn on.

Sounds like low on refrigerant charge. Low pressure switch keeping the compressor and condenser fan from running.
0helpful
1answer

Central Air Conditioner

Turn the power to the indoor unit off. Remove the cover where the fan is. Feel the motor of the fan. If it is very hot the bearings have likely gone out. If the fan is cool to the touch I would call a service company because you likely have an electrical problem that will require some training to solve.
0helpful
2answers

MODEL # CARRIER 38XD124300

sounds like you had a condenser fan replaced ok you just have verify if the fan is a reversible one there is like a plug type connector on top of fan all you have to do is swap the position of the plug ex. if black / white to white/black that changes the rotation. check against the diagram it should be for the CCW position.
Not finding what you are looking for?

1,517 views

Ask a Question

Usually answered in minutes!

Top Carrier Heating & Cooling Experts

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Grand Canyon Tech
Grand Canyon Tech

Level 3 Expert

3867 Answers

Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...