SOURCE: I have a Powerware 9120 2000 UPS battery failure message
After you replaced the batteries did you perform a manual battery test?
If not do so.
Regards
Alan Hood
ami-man
UK
SOURCE: Battery Packs for Powerware 9355 UPS
If you battery packs are all at 130volts DC, then all of the packs will have become dead, and the batteries are not recoverable. Your battery DC bus voltage on a Powerware 9355 20 to 40kVA rated UPS is nominal 432 volts DC - 36 batteries in series in each string at 12 volts DC per battery. If batteries go below 10.5 volts DC each, or 378 volts DC bus voltage, no amount of charging will recover these batteries. You should not be recycling the DC battery breaker, unless you felt the battery breaker was faulty. The UPS would have given you an alarm message of either battery breaker Off, Charger Failure, or Low DC Bus Voltage long before the these batteries failed.
The battery test will not proceed if the batteries are dead.
The charger board has failure. Model already obsolete. Propose to buy a new unit
