My fan will not turn off even if you shut system down

The fan relay is located in the air handler side of the system. Replace it and the fan will shut off normally.
1/16/2016 8:58:11 AM • Rheem Packaged... • Answered on Jan 16, 2016
0helpful
1answer

Why is my heat pump tripping circuit breaker continuously?

Probably a weak breaker. I would change it and see if it happens again. If the problem continues call a hvac guy out
1/10/2016 7:02:19 PM • Rheem 2.5 Ton 13... • Answered on Jan 10, 2016
0helpful
1answer

Emergency heat on, compressor not running

Unit may have have iced up and defrost timer came on which is emergency heat check pressures and refrigerant
12/21/2015 8:47:43 AM • Rheem 3 Ton 14... • Answered on Dec 21, 2015
0answers
0helpful
1answer

Rcba 4882g how much is it to replace the central AC condensing unit

This will be dependent on the capacity (tonnage or BTU/Hr) of the condenser, its location and how much refrigerant will be needed to added / replaced - plus the labor to do it. A typical 2 - 3 ton residential system (air handler / condenser - no duct work, etc.) can run $2k and up.
11/9/2015 7:51:09 PM • Rheem Heating &... • Answered on Nov 09, 2015
0helpful
2answers

Blower on air handler will not turn off?

Can you give me info on the unit I’m happy to help further over the phone at https://www.6ya.com/expert/vincent_f7b7c5f4dedd2565
8/2/2015 6:59:08 PM • Rheem Classic... • Answered on Aug 02, 2015
0helpful
1answer

Heater turning on when system is off

short in thermostat or heat switch
6/8/2015 3:48:37 PM • Rheem Air... • Answered on Jun 08, 2015
0helpful
1answer

WHAT IS THE BTU CAPACITY OF THE AHR42C3XH21B?

42 would be a 3.5 ton I’m happy to help further over the phone at https://www.6ya.com/expert/vincent_f7b7c5f4dedd2565
3/3/2015 6:28:52 PM • Rheem RQPMA037JK... • Answered on Mar 03, 2015
0helpful
1answer

Ice hitting outside fan

It sounds like your system might be low on coolant. Check the pressure of the main line and check it against the specs. You may have a leak in the system.
3/2/2015 6:13:43 PM • Rheem 12,000 BTU... • Answered on Mar 02, 2015
0helpful
2answers

How many pounds of reon do you put In 2011 Rheem Classic packaged ac unit

look on the mane plate on outside unit... has voltage ratings model serial type of freon factory charge etc.
2/12/2015 4:18:36 AM • Rheem Prestige... • Answered on Feb 12, 2015
0helpful
2answers

Burner dont stay lit long enough to put out heat

If this is a reasonabley new style furnace it's because your flame sensor, they get tarnished and you have to follow the Orange wire on the left side of the burners that leads to the screw (1/4" hex) that you have to remove before you can remove the sensor. Once you do you will need to clean the sensor (it's just a rod bent to a right angle) use some fine grain sand paper, or Emory cloth, and put it all back together, and there you go.
1/30/2015 7:46:57 PM • Rheem Heating &... • Answered on Jan 30, 2015
0helpful
1answer

Rheem classic 80 fan motor on furnace hums will not turn on

Have you checked the capacitor? Try spinning the blower wheel by hand, if this gets the motor going you have a bad capacitor. If not, the motor will need to be replaced.
1/9/2015 4:24:06 PM • Rheem Prestige... • Answered on Jan 09, 2015
0helpful
1answer

Why is my air conditioner freezing?

Either lack of refrigerant, stopped up metering device or capillary tube/s, or lack of air flow (due to bad blower motor, or dirty indoor coil)
12/13/2014 10:38:03 PM • Rheem... • Answered on Dec 13, 2014
0helpful
1answer

Rheem classic 90 furnace not turning on

Check thermostat. Check for a burnt out ignitor.
11/28/2014 3:16:39 AM • Rheem Heating &... • Answered on Nov 28, 2014
0helpful
1answer

Rheem furnace shuts off

Need more info
11/28/2014 3:15:50 AM • Rheem Heating &... • Answered on Nov 28, 2014
0helpful
1answer

The blower on my funace, Rheem RGAA-08EA, will not start. The burner lights but the blower doesn't start

Possible bad motor and/or bad capacitor and/or bad blower relay.
11/28/2014 3:15:28 AM • Rheem Heating &... • Answered on Nov 28, 2014
0helpful
1answer

ROLLOUT SWITCH OPEN, COLEMAN EVCON FURNACE

Reset the switch. Check the heat exchanger thoroughly for blockages, cracks or holes. Check induced draft motor for proper operation. Check flue pipe and chimney for obstructions.
11/28/2014 3:13:53 AM • Rheem Heating &... • Answered on Nov 28, 2014
0helpful
1answer

WON'T STAY LIT

Clean the flame sensor.
11/28/2014 3:11:44 AM • Rheem Heating &... • Answered on Nov 28, 2014
Not finding what you are looking for?
Rheem Logo

127 questions posted

Ask a Question

Usually answered in minutes!

Top Rheem Heating & Cooling Experts

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66835 Answers

Larry Ng
Larry Ng

Level 3 Expert

14562 Answers

David Spradling
David Spradling

Level 3 Expert

13520 Answers

Are you a Rheem Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...