Hi i have a panasonic cs28 cassett units both have F27 01 fault codes. have checked power at indoor and outdoor units can i do anything else

1 Answer

R Subramaniyam Iyer

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Master 2,133 Answers
  • Posted on Dec 28, 2010
R Subramaniyam Iyer
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Dec 02, 2010
Answers
2133
Questions
1
Helped
953392
Points
6173

F27- indoor outdoor unit disconnected.
Check power in output of indoor and input of outdoor, if power variation, replace wire.

Normally in this fault code, one of the wire burnt or rat bitten.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Voltas Cassette A/C 2 ton. The indoor light is blinking 8 times. Problem?

What is the error code E8 on Voltas cassette AC unit?

An E8 error usually indicates a fan problem with the indoor or outdoor unit. An E8 error is usually cleared by power cycling both the indoor and outdoor unit by turning power off at the breaker. Be sure to check the indoor air filters are not dirty and blocking air flow from the fan.

Or

https://www.republicworld.com/technology-news/gadgets/voltas-ac-error-codes-list-know-the-meaning-of-all-these-error-codes-right-here.html#:~:text=F8%3A%20This%20error%20code%20shows,with%20the%20outdoor%20DC%20fan.&text=P2%3A%20This%20error%20code%20shows,the%20Compressor%20phase%20current%20protection.

What is the error code F8 on Voltas?

F8: This error code shows up only when there is an issue with the outdoor ambient temperature sensor. F9: This error code shows up only when there is an issue with the outdoor DC fan. P2: This error code shows up only when there is an issue with the Compressor phase current protection.

Mar 24, 2021

Voltas AC Error Codes list: Know the meaning of all these

https://www.google.com/search?q=Voltas+Cassette+A%2FC+2+ton.+blinking+8+times

..
0helpful
1answer

What iam experiencing is immediately I switch on the carrier cassette unit the red light flashes continuously with an error E4.what is it?

Hallo,
Check your model no and find the fault codes here.

https://www.carrierair.com.au/installer-and-technical-support/fault-codes/

Should be either the indoor temp or outdoor temp sensor. Try cleaning the indoor air filter units.
0helpful
1answer

How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR

14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
continuously - • Indoor PCB
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
tection 4 times occurance
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
tion 4 times occurance
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• IPM (Power transistor)
• Compressor

Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
0helpful
1answer

PANASONIC DMR BS850 SHOWING ERROR CODE F5 202 CAN IT BE FIXED

hi,
Fault Code At Remote = F5
Indoor Unit PCB
LED1 = Lit
LED2 = Lit
LED3 = Lit
LED4 = Lit
Outdoor Unit PCB
LED1 = Lit
LED2 =
LED3 =
LED4 =
Measuring Of Fault Code = Signal from RC to ID faulty.

Air Conditioning Fault Codes
0helpful
1answer

Panasonic CZ-RTC2 with a fault code E04 does somebody know what that means?

Hi
This error means that your outdoor unit can not communicate with one of the indoor units.
most probably one of indoor units has a trouble.
1helpful
1answer

I have an LG split system air conditioner model number LSZ244VN-4 it is coming up with a fault code of CS after it has been running for approx 5 minutes

There is no CS code. Please read as C5.
Fault Code 05 and 53 (CH05 is displayed at indoor unit, 53 is displayed at outdoor unit)
This fault code indicates a communication error between the indoor and outdoor units; this is usually caused
by wiring errors or condensate pumps connected to the inter-connecting cable.
The communication between the units is a fluctuating DC voltage commonly called a serial signal, it can be
easily lost if the wiring is not done correctly. If there is a communication error fault CH05 will appear within 5
mins of powering up the system.
Testing
• Check Outdoor and Indoor Power Supply Voltages ( 230V ±10% ) and correct as necessary.
• Check for any mis-wiring or loose connections and correct as required.
• Check the resistance between communication line and GND. (Normal: Over 2M).
• If one Indoor unit operates normally Outdoor PCB is generally normal.
Turn on the power and start the indoor unit in cooling, set the temperature to 18ºC; the serial communication
signal will only be present for the first 3 mins of operation.
Set your meter to DC Volts, Test between terminals 5 (Red probe) and 2 or Earth (Black probe) of the outdoor
unit, you should see a fluctuating 0-72 Vdc.
If the Voltage is not present disconnect the terminal 5 cable, test the Voltage between this wire (Red probe)
and 2 or Earth (Black probe), you should see a steady voltage in the range of -0.1 to -10.0 Vdc. If No Voltage
is present either the cable or Indoor PCB must be faulty. This can be determined by checking the voltage
output on the Comms terminal of the Indoor unit, with the Comms wire disconnected. If No Voltage is present
the Indoor PCB must be faulty, if present, cable must be at fault.
2helpful
1answer

PANASONIC CASSETTE AIRCONDITIONING ERROR CODE NO :- F27-02

f27- indoor outdoor unit disconnected. Check the power output of indoor and input of outdoor.
If no power you have to check indoor room temp sensor through which thermostat send command to outdoor unit. If your sensor is good, you have to repair/replace your PCB
1helpful
1answer

Error code E39 for Mitsubishi Heavy Industry Ceiling cassett type

E39 Fault is thermister, Mitsubishi way of saying im not going to start because there is something wrong. Generlly it is compressor fault or short of gas. Im guessing if you turned the power out. Waited twenty seconds, turn it back on. Now if you go to the outdoor part. Wait exactly 3 mins. If you hear the compressor try to start and fail then it would more then likely be your compressor if you dont hear anything and the unit faults out it will either be a board or short of gas.

Either way If the unit is under five years old get a warrenty agent out to look at it.

Sorry I couldnt tell you for sure but MHI are very vague when it comes to fault codes
0helpful
1answer

System will not start up.

This is a signal fault between the indoor and outdoor first make sure the dip switches are set start with the unit closest to the condensor set as unit 1 then next unit as 2 and so on the dip switches are inside the indoor unit on the pc board if you check the manual it will tell you which swithes to set, if this wasnt done when the units where installed they would have never worked i would also check the signal wiring between the wallmount and the splitter box / bc box and make sure there isnt a loose connection when you have ruled this out id say more than likely it is a faulty indoor board on the wallmounted unt
Not finding what you are looking for?

425 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...