1993 goodman status light 4 times blinking

I have 1993 goodman gas furnace. the furnace is blowing with cold air. no flame. the thermostat is running on battery. the status light on goodman is blinking 4 times. seems open limit switch on the panel description. I replaced the air filter. still no heat coming while fan is blowing. your help appreciated in advance

  • 4 more comments 
  • atlgeek Jan 25, 2008

    the limit switches (1 main and 1 aux )are attached onto the furnace and I see there are 4 rollout switches ( round and two wire attached and the other side has a switch with pink mark) around the furnace (top, 2 sides and 1 bottom). The filter was dirty and is replaced. is the rollout faulty?

    What would be the correct sequence to reset the system?
    thx

  • Anonymous Mar 11, 2014

    Toyota twincam 4age doesn't idle

  • Anonymous Mar 11, 2014

    car shuts down while driving may or ay not start have replaced distributor cap, rotory button, wires, and oter pt

  • Anonymous Mar 11, 2014

    i have just had gearbox, clutch and associated parts replaced on an 02 Peugeot 206. all was fine at first but now battery light has started randomly coming on whilst driving. no problem starting, as yet!.

  • Anonymous Mar 13, 2014

    model DGAA056,furnace, blows the 3 amp fuse, if both of the limit switches are hooked up, but if you unhook one of the switches the blower fan comes on and the light code reads 4 flashes, open limit switch, also made sure both switches where normaly closed.

  • Anonymous Mar 13, 2014

    model DGAA056,furnace, blows the 3 amp fuse, if both of the limit switches are hooked up, but if you unhook one of the switches the blower fan comes on and the light code reads 4 flashes, open limit switch, also made sure both switches where normaly closed.

×

3 Answers

Anonymous

Level 1:

An expert who has achieved level 1.

Problem Solver:

An expert who has answered 5 questions.

  • Contributor 1 Answer
  • Posted on Dec 30, 2008
Anonymous
Contributor
Level 1:

An expert who has achieved level 1.

Problem Solver:

An expert who has answered 5 questions.

Joined: Dec 30, 2008
Answers
1
Questions
4
Helped
1975
Points
1

I have a goodman GMP075-3 that won't turn on. I think it is the pressure switch since I do not have a vent blockage. What is a venter and where can I find it??

Anonymous

Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

  • Master 447 Answers
  • Posted on Jan 25, 2008
Anonymous
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

Joined: Sep 27, 2007
Answers
447
Questions
5
Helped
355861
Points
1420

If the code description for four flashes is an open limit switch, than you will need to figure out how many limit switches (they shut the furnace down in case of overheating) your unit has. They look like small discs with 2 wires attached. Look around the burner tubes for the limit. If there is a little red button than you lucked out it is a manual reset kind, if there is no red button than it will have to be replaced. You can try putting the two wires on the switch together just to test. Of course it is very dangerous to leave it bypassed. Also im sure air filter was so dirty that is why overheated??

  • Anonymous Jan 25, 2008

    I would use a volt-ohm meter to test all for continuity.

×

Ad

Anonymous

Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Genius:

An expert who has answered 1,000 questions.

  • Master 1,067 Answers
  • Posted on Jan 25, 2008
Anonymous
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Genius:

An expert who has answered 1,000 questions.

Joined: Jan 06, 2008
Answers
1067
Questions
0
Helped
419554
Points
2624

Witch blower is running, the inducer or the systems blower?
System blower could mean the the high limit is opening and shutting down the systems gas train, I would check this out first.

The other problem could be with the pressure switch for the gas train, it is supplied from the inducer motor, check to see if it is operating fully.

HSI boards do go from time to time, this sounds more like a system control problem.

  • 4 more comments 
  • Anonymous Jan 25, 2008

    "4 blinks =open limit

    check main open limit or aux. open limit"

  • Anonymous Jan 25, 2008

    High limit is a normal closed position, and stays that way. Limits open in the event of a filter blockage or a coil blockage.

    High limits are located in the upper portion of the unit, locate it and jump that puppy out and see if she runs from there.

    Limits are cheap,$6.00 boards on the other hand can run up some cash, $120.00 and up depending on your unit.

  • Anonymous Jan 25, 2008

    On - OK
    1 Blink - Ignition failure. Check Gas flow, gas pressure, gas valve, flame sensor.
    2 Blinks - Closed pressure switch. Check pressure switch (stuck in closed position).
    3 Blinks - Pressure switch - failre to close. Check venter, pressure switch, vent blockage.
    4 Blinks - Open limit switch. Main limit or aux limit are open. (My comment - Means overheating in chamber. Often result of blocked intake air. Bad filter. In my case, plastic wrap had been sucked into the intake. )
    6 Blinks - False flame sensed. Check sticking gas valve.
    Rapid continuous blinking - Incorrect twinning, incorrect primary polarity. Reverse transformer secondary leads, reverse primary wires.

  • Anonymous Jan 25, 2008

    FYI I had a case not long ago of a 6 flash code, found that the ground wire from the control board was not secure. Must of gotton pulled when they replaced the filter

  • Anonymous Jan 25, 2008

    An open limit means the airflow temperature in the heat exchanger was too high or you had a roll out switch trip due to flame entering the burner area. Check your filters and evap coil and make sure they are clean. It would be a good idea to have the heat exchanger check as well for cracks due to how prone GMP-125's were to cracking with poor airflow.

  • Anonymous Jan 25, 2008

    dont forgetto mark me as fix ya ok

×

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Goodman furnace model #capf030b2c 4 blink code blower runs constant but no heat

https://hvac-boss.com/troubleshooting/goodman-furnace-error-codes/

According to this page, you can usually fix this 4 blink diagnosed problem by changing the air filter or tightening wiring (which it has a cautionary warning about tightening such too much) and checking the flue for blockage. The furnace has activated the primary open limit circuit.

Here is a troubleshooting page about the Goodman just blowing cold air: https://temperaturemaster.com/goodman-furnace-troubleshooting/#Goodman_Furnace_Blowing_Cold_Air

Poor air flow in the Goodman caused by blockages can result in the tripping of the rollover switches which would cause it to blow cold air. That is a safety measure. You don't want gas furnaces burning with insufficient air. Think carbon monoxide. Besides the air filter, the flame sensor or the burner could be dirty. The idea of trying to DYI that cleaning job is rather off putting. I hope changing the filter would work.

I trust it is not a fuse in the pilot flame sensor circuit blown. A repairman has the voltage testers for checking the electronics involved.

I can empathize with this. My furnace, another brand, went out recently. The repair man didn't know why it went out but simply adjusted a handle controlling gas flow to a position slightly different from what was recommended and it worked. All for $200.

https://www.repairclinic.com/RepairHelp/Furnace-Repair/36-377--/Goodman-Furnace-Troubleshooting

https://www.youtube.com/watch?v=zO1jKqwXu8s

https://www.goodmanmfg.com/products/gas-furnaces
0helpful
1answer

Furnace running but cold air coming out of vent!

There may be a dirty flame sensor, post the model number
0helpful
1answer

Goodman gmp0503 unit has status light blinking slowly all the time. The indoor blower wont even come on when you switch from auto to fan on thermastat. The status light says for one blink to check gas...

Take a jumper wire and jump out the R and W terminals on the furnace. The heat should come on. If it does not, you have a bad board. A steady blink indicates no call for heat. You may have either a broken thermostat wire or a bad thermostat if unit fires when you jump it.
0helpful
1answer

I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...

Heating Mode (Goodman Service Manual)

· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.

· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
corrected.

· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.

The sequence cannot continue until the pressure switch
closes.

· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.

· After a slight delay the gas valve will open.

· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.

· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.

· The furnace will remain in operation until the demand
for heat is satisfied.

· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.

· The furnace will remain dormant until the next demand
for heat.
0helpful
1answer

I have a RUUD Silhouette II and every once in a while the house gets cold and I check my furnace and the Status Light blinks-pauses-blinks-pauses ect. It is only flashes once so it tells me ''One Hour Time...

You will need to reset the furnace and have it run thru a cycle (or try). After three attempts, it will blink another error code that may tell you more.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
0helpful
1answer

Central heat not working right

You may just have a dirty air filter or your furnace may be flashing an error code that could help you. Look for a small viewing port that looks into the cabinet of the furnace. Look for a blinking light. Count the blinks and then find the wiring diagram pasted to one of the panels. On the diagram it will have a diagnostic chart where you can look up the error code. Read on for some basic info that may help you.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
5helpful
2answers

My heater blows cold air. any ideas?

Your unit has a diagnostic light on the circuit board. You need to look thru a small viewing port to see it. Once you count the number of b links, remove the lower panel and look at the wiring diagram for an error code chart. Then read the following to give you some ideas what to do.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
2helpful
2answers

Goodman furnace blinked 1 time

Furnace attempted to start but failed after so manay tries. This may help you.

Sequence of operation, Gas Furnace.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).

This is why we technicians earn the big bucks!
1helpful
2answers

Blower works but no heat

If in fact you have the above listed furnace, you do not have a pilot but electronic ignition. You will need to remove the front cover on the furnace, tape down the door safety switch and then have someone help you by turning up your thermostat to a very high setting. Watch and listen inside the furnace. There should be some blinking going on at the control board followed by a small blower fan starting up. Then after 10-15 seconds there should be a click followed by an orange glow viewed thru the viewing window to the burner section. In a few seconds the gas valve should click and the burners will ignite. There is a safety switch that will sense flame and then keep the gas going to the burners. If it does not sense it, it will shut it off within 10 seconds. If all is well so far, your blower will turn on in about 90 seconds after flame. There is a diagnostic code chart on the back side of the access door if you get an error code (blinking) on the control board.

Always check little things like air filter, condensate drain and broken or loose wires.
Not finding what you are looking for?

1,985 views

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...