Heating & Cooling Logo
leonardo montoya Posted on Nov 09, 2019
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
Coleman gas furnace 4066-656 model draft inducer stays on no heat no ignitor on just stays running after a regular cycle it works then it wont
J Rosado
Level 3:
  • Master 1,202 Answers
  • Posted on Nov 10, 2019
J Rosado
Master
Level 3:
Answers
1202
Questions
Helped
500478
Points
3432
Bypass the static pressure lockout switch. If it works, replace the static pressure switch, or the combustion blower motor if its part of the sensor switch.
doughboy0486
Level 1:
Habit-Forming:
  • Contributor 16 Answers
  • Posted on Nov 09, 2019
doughboy0486
Contributor
Level 1:
Habit-Forming:
Answers
16
Questions
0
Helped
2437
Points
26
There are a couple things you can try...
1. On your draft inducer, follow the rubber hose to the vacuum / pressure switch. Pull the hose off of the switch and blow through it... if your unable to, the hole is plugged at the inducer
connection and needs unplugged... if you can, put the hose back on the switch and try again, it is possible that the hole was slightly plugged but clear now...
2. Pull the hose off of the inducer motor and slightly blow into it or pull a slight vacuum on it... if it doesn't hold the pressure or vacuum, the diaphragm inside has a hole and entire switch needs to be replaced
Zach Gabai
Level 1:
Problem Solver:
  • Contributor 8 Answers
Zach Gabai
Contributor
Level 1:
Problem Solver:
Answers
8
Questions
0
Helped
23577
Points
16
Look to see if the pressure switch contacts open close
  • leonardo montoya Nov 09, 2019
    It has no pressure switch its a centrifugal switch that comes with the draft inducer
5 Related Answers
shortyb240
  • 25 Answers
  • Posted on Oct 26, 2009
SOURCE: draft fan keeps on running after furnace shuts
That sounds pretty normal for most furnace/heater products. They run the heating element with fan for a cycle then after the heater reaches temperature it will shut off and the fan will continue to run to cool the element and to circulate the heat that it produced. If you want the manual for this product it looks like you can get it here: http://homeappliance.manualsonline.com/ex/product/headline/m/Coleman%2BEvcon/d/furnace/p/DGATO75BDC
Anonymous
  • 22 Answers
  • Posted on Jan 21, 2010
SOURCE: i have a coleman evcon gas furnace in a 95 trailer
Most Coleman units in a trailer dont have a draft fan. Are you talking about the fan that blows air through the floor registers? If yes, then you will probably need a new fan/limit control. If you do have a draft motor, you would probably need a new circuit board or draft fan relay.
Anonymous
  • 22 Answers
SOURCE: furnace dont have heat
check for pressure switch trouble or cracked ignitor.
Anonymous
  • 1015 Answers
  • Posted on Feb 20, 2010
SOURCE: I have a Rudd furnace
Well first you want to verify that there is gas pressure coming from the connector. Turn off the valve and disconnect the connector. Then turn on the valve for 1 second and back off. You should get plenty of gas flow. Be careful doing this!. Then inspect the opening at the adapter to the control. There is a screen inside there. Make sure the screen is clear(not plugged with pipe dope,lint ect). When the igniter reaches the 2200 degrees you should hear the gas solenoid valve click open releasing gas. If you hear it click and no gas is released you will need to inspect the burner orfices. The orfice has an extremely small hole and there is a posibillity that they are plugged with debris. You will need to use a very small wire(like a tie strap) and insert it into each hole and see if there is anything in the orfice. If you do not hear the gas valve click then it might not be getting the signal it needs due to a weak igniter or flame rectification sensor. Does your furnace have a stand-by pilot that is lit by the hot surface igniter or does the igniter directly light the burner assembly?
Robert
  • 1036 Answers
  • Posted on Feb 24, 2011
SOURCE: I have a Ducane MPGA100B4B gas furnace. The
Hello, sounds like the limit switch is opening on the furnace.Usually when a furnace goes off on its high limit is becuase the airflow is being restricted making the furnace overheat. a limit switch is there to protect the furnaace from overheating, most cuases are either dirt or the blower motor not running up to speed, anything that cuts down on the airflow will cause the high limt switch to open.
Furnace was working fine and just stopped working...it reacts to raising the thermostat but doesnt actually flame on
This is probably a ignitor.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Please leave feedback... Thanks...
Doesnt blow any heat we checked all connections furnace clicks on but never gets warm we think maybe its the heating element but we are not sure how to get to it to check
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem.The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
1helpful
Heater turns on and heats garage to set temperature, than shuts off. when the temperature drops, the unit kicks on again. everything starts working again but only for a few seconds and than shuts off. it...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor.If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
My furnace wont lite
Problem: Your furnace will not ignite the gas to produce heat for your home.The following is the sequence of operation and probable cause:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch (or circuit breaker ) back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands (use gloves). If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
1helpful
Have a ruud achiever 90 plus furnace. the flame goes out after the igniter quits. any ideas
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Induction fan motor cycles on and off , with no call for heat
Rheem 3204-80D furance. Turns on and fan starts. Then in about a minute the fan shuts off.
I AM WORKING ON A CARRIER 90% FURNACE. IT WILL NOT FIRE UP. IT SHOWS A 34 CODE. THE IGNITOR DOES NOT ENERGIZE FROM THE BOARD. NO POWER COMING FROM THE BOARD. I HERE A CLICK AS IF IT IS TRYING BUT NO...
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Hot surface ignitor won't ignite,I replaced the igniter and it still won't.
Top Coleman Heating & Cooling Experts
Paul Carew
ZJ Limited
ZJ Limited
Mike Cairns
Mike Cairns
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others