Amana 80 SSE. Unit has power, but only clicks and runs the motor for 3-4 seconds then shuts off.
Flame sensor cleaned, igniter replaced. 8 blinking lights suggests either the ground or igniter. The ground is in place Any suggestions?
    Top Expert:
  • Amana Master
  • 10,371 Answers
Check for flame below flame sensor possible blockage of tube
Posted on Oct 19, 2019
3 Suggested Answers
6ya staff
SOURCE:
Therinnaiguy
Chandler Ede
  • 1420 Answers
SOURCE: Amana Air Command 80 SSE gas furnace will not stay running
In the path of the flame on the last burner that starts, there will be a small rod. That rod is the flame sensor. Take a scrub pad and polish it. Also check the electrical connection that goes back to the circuit board. Disconnect any ground wire from the circuit board to furnace cabinet, sand it and replace it.
Posted on Mar 14, 2010
Rod MacNeil
  • 25 Answers
SOURCE: Just replaced an inducer motor
replace the fuel nozzel.....if its plugged or restricted it will do this....change fuel filters as well
Posted on Feb 26, 2011
My Amana Air Command 80 SSE IIQ Gas Furnace started up for a few seconds the shut down with no indicator light. I went up and switched disconnect off and on, then checked all connections and fuse on...
Have you cleaned your flame sensor? Take a piece of emery cloth or a piece of light sand paper and sand it a little. It is located in the burner section and it is usually to the left side of the unit and it looks like a L. Hope this helps.
Feb 13, 2012 | Heating & Cooling
Goodman gms80903bna light blinks once fan runs all the time,
I believe this code is ignition failure.
Turn power off and after 20 seconds turn power on with thermostat calling for heat. Vent blower should come on first. After a bit igniter should lite up. You should hear click noise of gas valve open up. If igniter does lite and you hear click noise, flame should come on for a few seconds minimum. If igniter doesn't lite and you hear click noise from gas valve, igniter is bad. If flame lites and then goes out, flame sensor probably needs cleaned. Both igniter and flame sensor are in metal plate under burners. Igniter has 2 wire going to it and flame sensor has one wire. If you think it is flame sensor you can remove with taking it out with 1 1/4" hex screw. Flame sensor will have white film on it if it needs cleaned, clean with steel wool or a dollar bill. If it isn't weither of these it is gas valve or circuit board.
Jan 27, 2011 | Goodman Heating & Cooling
Hello, I have a Amana Air Command 80 model #GHI90A50, 22 years old. This furnace is on its third ingnition module (last one two yeras ago). The symptom I am trying to diagnose has been ongioing since this...
If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 05, 2010 | Heating & Cooling
I have a newer tappan heater and get 4 blinks on led for error code the unit starts up fine and has flame but flame goes off when blower kicks on
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
Carrier 58sxc120 won't ignite and I get a fault code blinking light of short long short don't know what it means.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 24, 2010 | General Heating & Cooling
My goodman furnace keeps lighting for about 10 seconds than goes out lots of clicking sounds
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad igniter what I see most of the time is the following sequence of operation:
Solution: You probably need to purchase and install a new igniter. I would suggest that you inspect your igniter closely for cracks. Make sure you do not touch the igniter with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, roll-out switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
NATE, NCCER, PHCC,HVAC Certified Instructor