5 Related Answers

Anonymous

  • 4 Answers
  • Posted on Nov 04, 2009

SOURCE: goodman model 135-5 furnace fan and induce motor

Is there a thermal Fan/Limit switch in this furnace? If so you may need to tweak the low range setting so it can turn off the blower.

Ad

Anonymous

  • 43501 Answers
  • Posted on Dec 24, 2009

SOURCE: Burner ignites and goes out (Goodman Gas-fired furnace)

Hi,
The problem you have is water in the exhaust pipe.
Check to see if the pipe has sagged anywhere or if there is a trap in the line.
If you hear gurgling then it is definetly water....
Some times can be hard to find, even a pipe 1/4 full will cause problems. They are very sensitive to flue problems.
Make sure that the flue pipe either runs back to the furnace or out to the outside, a continuos slope either way witha high spot in the middle.
Also check the bottom drain of the blower if it has one, have had them plug and trap water also..

I hope that this will help you to solve your problem!

Thanks for using Fixya!!

Heatman101

Anonymous

  • 111 Answers
  • Posted on Jan 31, 2010

SOURCE: Goodman GS9 propane furnace inducer motor runs continuously

it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps

lnbn1975

  • 204 Answers
  • Posted on Dec 05, 2010

SOURCE: Our furnace keeps shutting down soon after burner

Sometimes a "Flame Sensor" gets carboned up and does not detect that the furnace has ignited, so it shuts down the fuel source. Might try cleaning that if so equipped.

Anonymous

  • 43 Answers
  • Posted on Mar 02, 2011

SOURCE: goodman furnaces gxs91155dxaa will not

I would first try to power up the inducer motor by itself. If this works without any issue than the next step is to look at the circuit board. You will need a multimeter. Set it to 120V AC and test the leads on the circuit board that the inducer motor attach to. Turn the system on and see if you get a reading on the meter, if so, then you know the motor is getting power. I would then check the legend of your furnace with the led pattern. You mention it is steady, look up what the steady light means. It may point to a control board error, in that case you will need to replace the board.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
2answers

Why does inducer motor run nonstop on goodman furnace?

possibly a board issue does inducer shut off when no call for heat
0helpful
1answer

Our furnace keeps shutting down soon after burner ignites inducer motor stays running wont heat until reset switch behind inducer motor is pushed

Sometimes a "Flame Sensor" gets carboned up and does not detect that the furnace has ignited, so it shuts down the fuel source. Might try cleaning that if so equipped.
0helpful
1answer

No blinks normal running igniter glows gas comes on wont run

Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
1helpful
1answer

Goodman GS9 propane furnace inducer motor runs continuously

it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps
2helpful
1answer

I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
4helpful
2answers

When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
1helpful
1answer

Hello I have a goodman gas furnace

On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
7helpful
5answers

Goodman furnace I think

Ok, a flashing 3 on a Goodman control board usually means that the pressure switch is tripping. A few things will cause this. One being a restriction in the exhaust or combustion air inlet. The second could indicate a faulty inducer blower motor and the third would be a blocked or bad pressure switch.
 
With the front cover off and door switch taped down, Have a helper turn the thermostat up to 75. You will be watching the circuit board for flashing lights and in a few seconds the inducer motor (the small fan hooked to the exhaust) will start. If this does not happen, we either have a bad circuit board or blower motor. If the fan starts rotating, inspect the hoses going to the small circular pressure switch. Sometimes they may get either water or debris in the hose and not allow the switch to sense pressure. If the hoses look OK, the igniter will glow an orange color and you will see this if you look thru the small viewing port. IF no glow, you could have a bad pressure switch, a bad ignition relay (found on the circuit board) or a bad igniter. OK so if the igniter glows, a few seconds later the gas valve should click open and send gas to the burners. The orange will turn to blue. If this does not happen, you have either a bad gas valve or bad circuit board. Finally if you get flame but it will not stay lit more than a few seconds, you may have a restriction in the burner gas train, a bad gas valve, a dirty or bad flame sensor or not enough gas pressure.
 
Knowing the sequence of operation will give you the needed information to talk with a service technician and cut down on diagnostic costs.
 
Try looking on the back of the furnace access panel for both model number and a diagnostic schematic. This will confirm what the flashing 3 code means for your unit.
 
Sorry, without knowing the model number, this is the best I can do for you. Good Luck!
Not finding what you are looking for?

452 views

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...