Heating & Cooling Logo
Dwayne Sarafinchan Posted on Aug 02, 2016
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
Have american standard model AUD1B060A9361AA fault light has 2 fast flashes - external lockout, retries or recycles exceeded. how to reset?
Thomas Woodburn
Level 3:
  • Master 2,638 Answers
  • Posted on Aug 02, 2016
Thomas Woodburn
Master
Level 3:
Answers
2638
Questions
Helped
1250661
Points
7008
Cycle high voltage at breaker
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Trane Furnace issue: 2 flash external lockout occurs, confirmed due to retries exceeded.
I agree that it sounds like a circuit board problem. So far as I'm aware, shutting off the power and turning it back on should cause the furnace to reset.
But wait and get some additional opinions on this oddball symptom would be my suggestion.
Thanks guys! The Thermostat is applying power. Both limit switches OK. The 2 microswitches attached to the air pressure lines are OK except one stays closed & one open sensing fan air I guess. Zero voltage read between green & white 120VAC input wires. I don't know what else to check. The darn circuit board will not reset and LED gives 2 flashes for lockout, and it means TOTAL LOCKOUT. Could you guys give me an idea how to go about buying a board to try? The only place near me just about doubles the price unless you are a HVAC company. Do I need to replace the part of the board that says "White-Rodgers" on it or just the green circuit board. Thanks again for helping.
Checked for thermostat voltage to Red & W1, checked limit switches, checked for 0 volts between green & white line input voltage, checked for loose connections. Red LED continues to flash 2 times after power recycled for reset.
Gas valve & igniter receive no power. I don't know what else to check. Does anyone have any more ideas to prove circuit board is bad?
My Trane furnace model is XV80, model # TUD100R9V5H6. If circuit board, do I replace the white box labeled "White-Rodgers, Model 50A51-507" or just the small green circuit board labeled "American Standard 21C148501P01?
I appreciate any more help you could give me including where to buy the board.
Thanks! Mickey
How do I fix an error 22 on my American Standard thermostat
I'm seeing 22 as a loss of flame. Unfamiliar with gas and oil, I'm in south Florida. Does say it locks out for 1 hr and will retry, possibly cycling power will reset lockout but unlikely to fix problem.
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Why does my hayward heater have a if error code
the code is IF. it stands for ignition failure.
If the control exceeds the maximum number of ignition retries or recycles the heater will shut down and go into lockout. Automatic reset is 60 minutes.
Why does my hayward h250fd have and if error code? it is a brand new heater
There are a few reasons that this might be happening. They range from air in the gas line to inadequate gas flow. Start by checking the installation
Trane xv95 converted to propane is on system lockout
worth checking over heat temp sensors (klixon ) sensors can cause heater to go into a cool down purge Through an open circuit heat exchanger (Klixon ) temp sensor Ive seen before good luck
There is either a problem with the ignitor or the flame sensor.
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
When i turn on my furance it starts up later it will try again and the system will lockout with one flash on the board indicating retries recycles exceeded any ideals?
check to make sure the gas is on and the flu pipe is clear.  does the draft motor come on at all?  if not, you may have a failed control board.
Top American Standard Heating & Cooling Experts
Steve Sweetleaf
Steve Sweetleaf
Paul Carew
Are you an American Standard Heating and Cooling Expert? Answer questions, earn points and help others