Low side press 78 psi, outside 93 degree
You need to to determine the superheat and subcooling to check for the proper operation of your system when the compressor is running. I ran into a case just yesterday, the breaker kept tripping. Unit had the same readings as yours. This one had a subcooling of >25 degrees and 0 degrees superheat indicating unit was overcharged. I took an extra 8 pounds of r22 out of the system. During the investigation I also determined the filter/drier was blocking the refrigerant flow causing the technician to overcharge the unit. To check filter/drier performance all you need to do is measure the upstream and downstream temperature. The difference should be less than 2 degrees. This one was 7 degrees indicating it was metering flow. If your compressor stops operating before determining superheat and subcooling, you can get a professional tech to recover and weigh out the refrigerant in your system. You can look on the nameplate data on the side of the outside unit and see the ounces of refrigerant it is charged. If the compressor is operable go ahead and adjust charge by recovering the excess refrigerant into a recovery container for that refrigerant. Normal superheat and subcooling is normally around 10 - 15 degrees.
Hope this helps
SOURCE: 5 year old Goodman CKJ48-1A Condenser Unit
do what they said also when those pressures equalizing it might be your compressor going out
SOURCE: Goodman heatpump. Crazy pressure in heat mode
Check the TXV valve on the outdoor unit, it could be stuck closed. We have been experiencing the same problems with the 410 systems and the TXV was the culprit. Good Luck