Anonymous Posted on Jan 03, 2014

Generac overspeed on starting cold - Generac Power Systems Electrical Supplies

5 Related Answers

Anonymous

  • 169 Answers
  • Posted on Apr 06, 2009

SOURCE: 10kw Generac shut down overspeed

Make sure that the throttle linkage is all there and not damaged/misadjusted, then get a manometer and check your inlet gas pressure. Gas pressure should be 8 inches of water column and stay there running or not.

Carl

Ad

RSG000

  • 26 Answers
  • Posted on Jul 09, 2009

SOURCE: Attempted to start Generac Guardian 15 kw air

I work on these every day. Its either gonna be the rotor or stater, the voltage regulator, but most likely its a bad stepper motor which is the throttle motor, or control board. Thats all that could be causing that so its one of those. If its the rotor or stater thats bad it causes the generator to RPM up because it thinks its not producing enough power due to that. I had the same problem with the same one we just fixed and it was the slip rings on the end of the rotor so bad rotor.

Bob Janelli

  • 26 Answers
  • Posted on Oct 01, 2009

SOURCE: Generac 43903 standby Generator overspeed indicator on starting

I have a generator that did the same thing. It would start and then stop within a few seconds. The more expensive generators have an oil level safety switch to prevent the engine from burning up. There is usually a wire connecting to the switch on the outside of the engine near the oil fill hole. Remove this wire and try to start the generator. If it runs without a problem then it is the switch. You need to remove the switch and take it apart carefully and clean it. There is a small float inside the assembly. When the oil runs low the float allows the switch to short to ground which kills the spark to the spark plug. Hope that helps.

Bob Janelli

I’m happy to help further over the phone at https://www.6ya.com/expert/bob_62dfa2f81bb55288

Testimonial: "This is good information in the event that the low oil switch is part of the problem."

Anonymous

  • 1 Answer
  • Posted on Jun 07, 2010

SOURCE: Generac Guardian 15 kw overspeed fault

Did you remember to set the overspeed shutdown threshold on the control board?

Anonymous

  • 1 Answer
  • Posted on May 23, 2012

SOURCE: Generac Guardian 12 KW Model 04456-2 shuts down on overspeed in cold weather

Leigh,
See my 5/22/12 comments on my "overspeed fault" problem resolution [Generac 43903 standby Generator overspeed indicator on starting] . If it only runs for a few seconds and then quits, you may have a similar condition to the one my unit had. A good technician should be able to diagnose the problem and determine if you have a similar failure to the one I had, or one of the other causes suggested by RSG000.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Generac guardian rv generator starts and runs but after a couple minutes the power stops.....generator still runs??

Usually the generator will shut down if the ac is not present coming out of the generator. You stated that it still runs but no power on the output. Check your breakers first to make sure they are working properly. Depending on what board you have you can check to see if ac is present getting back to the board as well. If your board does not have this then they are using the frequency as a safety disconnect feature. That would lead you back to the regulator or loose connection or..dirty slip rings if this unit has brushes.
0helpful
1answer

Generac over-speed fault

check your frequency of the ac, if this is high, then adjust the rpms.
If that is fine and it is shutting down, check overspeed adjustment on control board if it has it.
1helpful
1answer

Generac Guardian 12 KW Model 04456-2 shuts down on overspeed in cold weather

Leigh,
See my 5/22/12 comments on my "overspeed fault" problem resolution [Generac 43903 standby Generator overspeed indicator on starting] . If it only runs for a few seconds and then quits, you may have a similar condition to the one my unit had. A good technician should be able to diagnose the problem and determine if you have a similar failure to the one I had, or one of the other causes suggested by RSG000.
0helpful
1answer

I have a generac 22kw model QT02224anan that will run for a few minutes then shut down , then the over speed led is lit. It only happens when it is under load or during a power outage. it goes through...

its possible the overspeed is set to sensitive. or your rpm are to high. these are preset in the factory as a safety, check your manual to ensure your rpm speed is in the pre set area. generators will do this under load when you have a big load on them or take a load off. the governor will some times over compensate causing it to trip on overspeed.
0helpful
1answer

I have an older 30KW Generac SG 030 1800rpm running on Nat Gas which I bought used. It has set up for several years. I installed a new PN0830890SRV master control board I bought from the local Generac...

need to calibrate the main control board. 83089. also is it overspeed or overcrank? if the board does not see the right rpm or is blow a certain threshold it will think it has not started yet and shut down on overcrank.
13helpful
2answers

Generac Guardian 15 kw overspeed fault

Did you remember to set the overspeed shutdown threshold on the control board?
Not finding what you are looking for?

116 views

Ask a Question

Usually answered in minutes!

Top Generac Power Systems Electrical Supplies Experts

Brad Brown

Level 3 Expert

19187 Answers

john h

Level 3 Expert

29494 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66980 Answers

Are you a Generac Power Systems Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...