Question about Gb Electrical 100 Amp GE Load Center
I need to wire up a 3 phase compresser motor, 9 wires wired 480, to change to 240 volt hookup. right now it is wired 3 motor wires to each hot, no nameplate or wiring diagram.
    Problem Solver:
  • 9 Answers
Please verify the existing connections to determine if they fit the "High Voltage" configuration listed below. If they do (and they should), the "Low Voltage" configuration below is then correct for 240.
Jaypug
Low voltage ...
L1---1--6--7
L2---2--4--8
L3---3--5--9
High voltage ...
L1---1 4--7
L2---2 5--8
L3---3 6--9
Posted on Dec 04, 2013
2 Suggested Answers
6ya staff
SOURCE:
Steve
  • 3289 Answers
SOURCE: I need to wire up a baldor 3 phase motor 208-230/480 15hp and dont have the wiring diagram to know what wire is what or where to hook it to?
Hi Casey, I'm an electrician and can help you with this problem.
First, a disclaimer. Without the catalog number of the motor you have, or a wiring diagram for it, no one can tell you how to wire this motor with any certainty. With that said...
Nearly all single speed 3 phase motors have 9 leads (numbered 1 thru 9) and can be wired for either "high" or "low" voltage. Most of the time, high is 480 volts and low is 208/240 volts. Given that you posted the amperage as "41-38 / 19", I am 99% confident that 41 amps is at 208 volts, 38 amps is at 240 volts and 19 amps is 480 volts. Further below is the way to wire unless the motor manufacturer or name plate indicates differently. You will need to determine the voltage of the appliance this is going to be installed into. You should be able to find this on a name plate of the appliance - but it may provide a dual voltage spec here, too. If this is the case, you will need to *carefully* measure the voltage with a meter, or find out the voltage of the electric panel that feeds the appliance.
Once you have learned the incoming voltage, you will connect the motor as such when L1, L2 and L3 are the line voltage supply wires and wires 1 thru 9 match the numbers on the nine wires from the motor.
208/240 or "Low" volts:
Motor leads 4, 5 & 6 connected together and wirenut.
Motor leads 1 & 7 to L1 and wirenut.;
Motor leads 2 & 8 to L2 and and wirenut and lastly,
Motor leads 3 & 9 to L3 and wirenut.
480 or "High" volts:
Motor lead 1 to L1 and wirenut,
Motor lead 2 to L2 and wirenut,
Motor lead 3 to L3 and wirenut,
Motor leads 4 to 7 and wirenut,
Motor leads 5 to 8 and wirenut and lastly,
Motor leads 6 to 9 and wirenut.
The motor should be operated briefly or "jogged" to determine the direction the motor turns. If the motor rotation needs to be changed, simply swap any two "L" wires (swap L1 and L2, or L1 and L3, or L2 and L3). Test once more to verify rotation and when correct close the wiring compartment and complete the installation. Swapping the L wires will likely be much quicker and easier to do at the magnetic contactor instead of the the motor's wiring compartment. Either location is acceptable.
You should try to obtain the name plate data for this motor - if at all possible to to make sure of the voltage and wiring method. I hope this helps & good luck!
Posted on May 14, 2012
I just bought a double head notcher with 2-10hp 3 phase motors they were wired 480 volt I only have 230 volt 3 phase from a converter. I put 2 starters to match voltage and motor size.what's the prob.
talk with an electrician but I think that if you have 3 phase motors on 480 volts you will need an inverter that will handle 480 volts
as it stands now you only have 230 volts for 3 phase and that means that there is insufficient power to run the motors
however in cases such as this , a long talk with an electrician could save lots of money
Aug 03, 2015 | Air Tools & Compressors
PLEASE, I HAVE A WHIRLPOOL DRYER DWSR-ELE-2406026-CV54, THE QUESTION IS HOW MANY PHASE HAVE FOR POWER SUPPLY?
It requires two hot wires measuring 240 volts across them and 120 volts from either of them to the neutral connection. Some people refer to the two 'hots' as 'two-phase' and some refer to it as 'single-phase'. At any rate, you do NOT have three phase requirements with that dryer.
Most of the dryers have a 120volt motor which is why you need two hots and a neutral. To complicate matters, recent changes to the code now require 4 wires on newly constructed structures. Two hots, a neutral AND a bare ground wire.
Mar 05, 2015 | Whirlpool Dryers
May 13, 2012 | Gb Electrical 100 Amp GE Load Center
LP126HD3A rated for 265 volts AC single phase I have 240V ac single phase, how can I use this unit on 240V ac
You'd need to supply a "Buck-Boost" transformer to do this properly. Technically, the 265 VAC is one hot leg and neutral of a 480 VAC 3 Phase Y system that measures 277 VAC. The 265 number comes from this:
265 is the standard nameplate voltage for a 277 volt motor or AC unit.
230 is standard name plate for 240.
200 is standard name plate for 208
460 is standard name plate for 480.
110 is standard name plate for 120.
Most electricians call the hot leg / neutral circuit "277V AC".
Some popular "Buck-Boost" transformers will convert 208 to 240 and 240 to 208 volt systems, and 240 to 277 and 277 to 240 volt systems - among many other variations. These are auto-transformers as the primary secondary windings share a connection. KVA ratings differ significantly from name plate because of this fact. You should contact a qualified electrician to not only size, but wire the transformer for you. Failure to install a Buck-Boost transformer - and running this unit on 240V AC mains will cause premature failure of motors - fans and compressor due to overheating. This can also result in a fire hazard.
I hope this helps and good luck!
Sep 06, 2011 | LG LP126HD3A Air Conditioner
I have Delco Model 2J2424r1, frame 56R, Series A84, phase 3 electric motor. What is the wiring diagram to run it under 230VAC?
If it has 9 leads and is a 240/480 volt motor the 1and 7 go to line 1. the 2 and 8 leads go to line 2 and the 3 and 9 leads go to line 3. the 4 5 and 6 leads are hooked together with a wire nut. To reverse rotation simply reverse any 2 of the line leads.. Prairie Dog........
Jun 15, 2011 | Leeson Reversible Electric Motor 3/4 HP
Tork 1104 is wired 120 vac. hot wire connected to L with jumper wire to 1.hot wire for outdoor lights connected to X. nuetral wires are wire nutted together. not connected to timer. clock not working....
The clock isn't working because the Tork 1104 clock motor requires 240 volts. Jumping the 120 volts over from terminal L to terminal 1 doesn't make it 240 volts. You need another 120 volt leg (180 degrees out of phase) to do that. The Tork 1103 timer is what you need, or change the 1104 clock motor to a 120 volt.
Dec 16, 2010 | Hardware & Accessories
Need to rewire from 480 to 240 need coolant pump diagram for colchester # 348337 3 phase motor
Assuming that the motor has 9 leads and the wire numbers are still on the wires, for 240 volt 3 phase connections:
Connect T1, T6, and T7 together with L1 (A phase)
Connect T2, T4, and T8 together with L2 (B phase)
Connect T3, T5, and T9 together with L3 (C phase)
If you're not sure which of the incoming wires from the supply are L1, L2, and L3, just pick one. If the rotation is wrong just swap any 2 (TWO) phase wires.
Jun 22, 2010 | Measuring Tools & Sensors
How to wire a 3 phace 5 hp baldor motor
the neutral or white is not used. if the fourth wire is a ground then it goes to the motor frame. if it is a dual voltage motor then here is the wiring: for 240 volt 3 phase connect 4-5-6 together and tape, 3-9 goes on L1, 2-8 together goes on L2, 1-7 together goes on L3. To reverse direction swap any two line wires. For 480 volts 3 phase: L1 goes on T1, L2 goes on T2, L3 goes on T3. Connect together T6-T9 and tape, connect T5-T8 and tape, connect T4-T7 and tape. again to reverse direction swap two line wires.
Oct 14, 2009 | Baldor 115v,1ph, 3,600rpm 7" 1/2hpbnch...
Need to change oven from 440 3 phase to 220 single phase hobart cn90 oven
It can be done with a transformer, 480/ 240 single phase transformer to get the lower voltage. Then the oven will require some wiring changes to get all the elements and controls connected to two hot wires instead of three. The transformed will be sized to the wattage rating of the oven. This is a only basic description of what needs to take place.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c
Sep 05, 2009 | Hobart Ovens
Voltage 1phase or 3 phase 240 volts BTUs M# 585epo36o75
Looking at the model number, it appears to be a 3 ton. (36,000 btu) Most all residential units are single phase and most all commercial are 3 phase. One way to tell, look to see if the compressor has a capacitor. 3 phase never use capacitors on the compressors as they are not needed. Some residential units have a "Dual" capacitor. That is, it has 3 terminals, 1 common, 1 for condenser fan motor, and 1 for the compressor. Also, this info should be printed on the unit's lable.
Good Luck and hope this helps.
May 09, 2009 | Amana Comfort Zone 12M32PBEH Air...
Gb Electrical 100 Amp GE Load Center Logo
153 people viewed this question
Top Gb Electrical Electrical Supplies Experts
Fahr Quad
Marvin
Marvin
rd2xpld
Are you a Gb Electrical Electrical Supply Expert? Answer questions, earn points and help others