Question about Tork Spring Wound Interval Timer
How to connect a tork spring wound interval timer
Trying to connect the black and white wires from timer to pump wires and wires from breaker panel
  • TORK Master
  • 5,391 Answers
4 Suggested Answers
6ya staff
SOURCE:
Tom W
  • 760 Answers
SOURCE: Not sure how to wire my Tork 1103 timer
The L terminal would be for your "hot" incoming black wire. The X terminal would be for your load outgoing black wire. Connect both white neutral wires to the blank terminal (notice this feeds the timer motor. The other two terminals (1&2) are not necessary if it is a 110V single circuit.
Posted on Aug 03, 2010
Anonymous
SOURCE: Im installing a TORK 1103.. Im hooking this timer
Tork 1103 is mechanical timer with 125V 3 watt clock motor
Dial on front face rotates when clock has voltage
Dark and light colored pins connected to dial, and turn timer on and off
There is removable brass bar that connects poles L and 1
You have 4 wires:
Red >>> I'm not sure about this wire, is this Hot wire coming from tandem breaker?
Black >>> this is Hot wire coming from tandem breaker
White >>> this is Neutral wire
Bare ground
Test wires:
Please test Black and Red to bare ground to see if these are both Hot
Test Hots to white to confirm this is Neutral
Solution ASSUMES black and red are both Hot, and white is Neutral
You have 2 problems:
Prob 1) Clock does not rotate dial: so clock is bad -or- clock not wired correctly
Prob 2) You are able to control 4 plugs using manual override, which means load wires are correct
However, you want to wire timer 'without red wire' (which is confusing, since red wires are connected to outlets)
Solution Prob 1:
1) The diagram show the N or Neutral wire is connected to Unmarked pole on timer
2) Black Hot has to be connected to pole L
3) Unmarked pole and pole L must be wired with 120V as shown before dial will rotate
4) If wiring is correct and dial does not rotate, then clock motor is bad
5) If dial rotates, check outer rim of dial to see if you have dark and light pins for on-off functions
6) Notice that all the Neutrals connect on Unmarked pole
Solution Prob2:
Are you saying that the household wiring extends beyond the 4 plugs, so when you turn off the 4 plugs, it also turns off more plugs and switches farther down the line? If so, you need to wire plugs with separate hot wire.
Let me review features on timer which might help:
1) There is removable brass bar between poles L and 1
2) If brass bar is removed, then you need Hot wires on both L and 1... but you can jumper between L and 1 with short black wire
3) If brass bar is there, then one Hot connected to either L or 1 will power both clock and load.
4) Timer is DPST double pole single throw ... so you can control 2 different loads ... one load connects to Unmarked pole and pole X ... another load connects to Unmarked pole and pole 2
If brass bar is removed:
Jumper between poles L and 1 ... so only one Hot wire is used on your timer.
Below shows jumper on poles L & 1: hot to load is on pole 2
Posted on Oct 07, 2010
gotgeek2
Bob
  • 565 Answers
SOURCE: I have a tork 1101
This is for 120 volts ONLY. The incoming "main" black wire from the circuit breaker or source connects to terminal 1. Leave the bridge in place between L and 1. The outgoing black wire to the load connects to terminal 2. Both white wires connect to x.
Posted on Nov 11, 2010
Trying to connect a Tork A530 MW timer to a spa tub pump
  1. The white wire (neutral) in your feed cable from the electric panel should be connected to the white (neutral) wire going to the pump.
  2. This switch is wired in 'series' in the hot (black wire) leg. That means one black timer wire connects to the black wire in the feed cable from your electric panel and the other black timer wire connects to the black wire that goes out to the pump.
  3. I the diagram the switch is your timer and the light bulb is the pump. The switch is in series with the pump.
Nov 13, 2013 | Tork Spring Wound Interval Timer
Wiring for timer
T101P3 is ordinary 120Volt T101 mechanism inside a beige plastic box.
Rated 40 amp.
Three terminals A 1 2
Very small white wires that power the WG1570 clock motor are connected to terminals A and 1.
White neutral wire from breaker box connects to terminal A
Black Hot wire from breaker connects to terminal 1.
This will power the clock motor, which will switch the timer on-off.
Green ground wire and bare copper wires connect to green ground screw.
115volt motor should have 2 wires.
Connect white wire to terminal A
Connect black wire to terminal B
http://waterheatertimer.org/How-to-wire-T104-Intermatic-timer.html#T101
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Aug 21, 2012 | Intermatic T101P3 Pool Timer IndoorOutdoor...
I have a new GE 15306 Mechanical Time Switch and need to wire it up to 2 white and 2 black wires that I had on my old timer. I need more information on the wiring than is on the diagram on cover of metal...
http://waterheatertimer.org/images/GE-15306-wiring-250.jpg
http://waterheatertimer.org/GE-timers-and-manuals.html#15306
GE 15306 is a version of 120Volt Tork 1101 indoor-outdoor timer sold at Home Depot under GE name and number.
You have 2 cables.
One cable comes from Breaker box, and other cable goes to Load (light, fan, motor, pump).
Each cable has black and white wire.
1) Cable from breaker box: Black wire H Hot connects to to terminal L.
Notice there is a metal bridge that connects terminal L and terminal 1.
If metal bridge is missing, use a jumper wire and connect L and 1.
White N Neutral from breaker box connects to terminal X.
2) Cable going to Load:
Black connects to terminal 2
White connects to terminal X.
So both white wires are on terminal X.
Jul 14, 2011 | General Electric GE 56941 24-Hour Outdoor...
How do you wire, wires from sprinkler to unit and wire from power
You posted under R8806 Intermatic sprinkler timer:
http://www.intermatic.com/products/timers/mechanical%20time%20switches/sprinkler%20irrigation%20timers.aspx
To see image of timer:
http://www.drillspot.com/products/85291/Intermatic_R8806R101C_Irrigation_Sprinkler_Timer
If this is not your product, then add a comment
You did not say if timer is 120Volt or 240Volt.
This information is on the door.
R8806P101 is 240Volt timer has 4 terminals from left to right. 1-2-3-4
240V Hot wires from breaker connect to terminals 1 and 3
Wires going to pump connect to terminals 2 and 4
R88 series 120Volt timer has same terminals as above.
120V Black hot wire from breaker connect to terminal 1
White neutral wire from breaker box connects to terminal 3
Black wire going to pump connects to terminal 2
White wire going to pump connects to terminal 4
Fixya also offers live phone support for a price.
Fixya phone expert can answer your questions by asking which timer you have and what circuit you are trying to control.
Dec 18, 2010 | Intermatic R8806P101C -...
Wiring of the 2-5-10-15 timer to a jucuzee bath tub it has three wires black blue green. Thanks. Terry.
First thing to consider is size of Load.
Leviton countdown-timer Load rating is 1800 Watt, 120Volt.
Look inside Jacuzzi at rating plate on motor.
Rating plate on motor should give Volts, Watts and Amps.
Formula Volts x Amps = Watts.
Sometimes motor shows VA which is Watts
Is Jacuzzi on 240Volt breaker or 120V breaker?
Leviton countdown timer is not for 240V load.
A) If 120Volt electric Load checks out, here's how to wire timer if 1 cable enter box.
Timer-black-wire connects to jacuzzi-black
Timer-white-wire connects to ground.
Timer-green connects to ground.
Timer-red connects to jacuzzi-blue.
B) Here's how to wire timer if 2 cables enter box.
120Volt cable coming from breaker box has black, white and bare copper wire.
Timer-black-wire connects to black-wire-from-breaker
Timer-white-wire connects to white-wire-from-breaker-box.
Timer-green and jacuzzi-ground connect to ground
Timer-red-wire connects to jacuzzi-black-wire.
Jacuzzi-blue-wire connects to white.
I am puzzled why this wire is blue if circuit is 120Volt.
Nov 26, 2010 | Leviton Timer Switch 2-5-10-15 Minutes, 4...
How to wire a 1104 series time switch
8896f6e.jpgTork 1100 series
Tork 1103 can control 120V or 240V Loads (fan light motor)
It can control 1 or 2 different Loads
Tork 1103 has 5 screw terminals
L 1 Unmarked X 2
The Tork 1103 has a 120V clock motor that consumes 3 Watts and costs $3.50 per year to operate.
1) You have to have a white Neutral wire from breaker box connected to Unmarked terminal no matter if you are controlling 120V or 240V Load
2) You have to have a black Hot wire from breaker connected to terminal L no matter what load
If you have 1 Load 120V:
Terminal L black hot from breaker
Terminal 1 no wire
Unmarked terminal white neutral from breaker
Terminal X black wire going to Load
Terminal 2 no wire
White wire going to Load connects to Unmarked terminal
So 2 white wires are on terminal 2
If you have 2 Loads 120V (Load1 Load2)
Terminal 1 jumper your black hot from Terminal 1
Terminal X black wire going to Load1
White wire going to Load1 connects to Unmarked terminal
Terminal 2 black wire going to Load2
White wire from Load2 connects to Unmarked terminal
So 3 white wires are on terminal 2
If you have 2 Loads 240V
Unmarked terminal white neutral from breaker (no other wires connect to this terminal)
White wire going to Load1 connects back to 240V breaker
White wire from Load2 connects back to 240V breaker
If you have more questions, add a comment and I will help
Oct 30, 2010 | TORK Variable Cycling Timer 8601
I have a 110 Pool Pump and I am trying to wire it into a Tork1103NC timer. From the pool pump I have a black, white and green wire that I need to wire into the timer. Can you tell me what position those...
Here is Tork 1103 wired for single load.
1) The green pump wire and bare copper wire go to green ground screw
2) Pump black wire goes to pole 2, the NO (normally open) pole
3) Pump white wire goes to unmarked screw
4) Black from circuit breaker goes to pole L
The T1103 comes with a removable brass bar that connects pole L and pole 1
If that removable brass bar is not there, then add a jumper between pole L and pole 1 as shown in diagram above
5) White neutral from breaker box goes to unmarked pole (all whites connect to unmarked pole)
In your case, pole X is not used. Pole X is NC or normally closed > which means the power is ON continuously until timer turns on, and when timer turns ON, the NC pole turns OFF
Oct 11, 2010 | TORK Variable Cycling Timer 8601
Wiring program timer switch model t1905 intermatic
Normal 0 false false false MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;} See timer manual at Intermatic: click on T1905 to see pdf manual:
http://www.intermatic.com/products/timers/mechanical%20time%20switches/24%20hour%20dial%20with%20skipper.aspx
T1905 has 4 screws: NO normally open > NC normally closed > COM > Clock
NO screw is on left
NC screw is 2nd from left
COM is 2nd from right
Clock is on right
A) How to wire t1905 for 125V
You will have four wires >> a Black and White from breaker box; and a Black and White to load
1) Black hot wire from breaker connects to COM
2) White neutral wire from breaker box connects to Clock
3) White neutral wire to load connects to Clock
4) Black wire to load connects to NO -or- NC screw [one of these screws will have no wire attached]
NO turns 'off' with times set on timer
NC screw turns 'on' with times set on timer
If you want your load to turn 'on' when timer clicks 'on' then connect Black wire to NC screw
B) How to wire t1905 for 240V
You will have four wires >> 2 hot wires from breaker box; and 2 hot wires to load. These wires might be Black and White or Black and Red
2) Red or White hot wire from breaker box connects to Clock
3) Red or White hot wire to load connects to Clock
4) Black hot wire to load connects to NO -or- NC screw [one of these screws will have no wire attached]
If you want your load to turn 'on' when timer clicks 'on' then connect black wire to NC screw
Sep 10, 2010 | Intermatic Timer T1905 24 Hour Dial 120V...
I have a Tork 1101. I am confused by wiring diagram. Please help.
http://waterheatertimer.org/Tork-timers-and-manuals.html#1101
1) Tork 1101 has 120Volt clock motor, making this 120Volt timer.
2) 120Volt circuit has 1 black hot wire and 1 white neutral wire and 1 bare ground wire. Ground wires connect to green screw and to each other.
3) You have two cables, each cable has black, white and ground.
One cable arrives from breaker box.
One cable goes to Load (light, fan, motor, pump etc)
4) Cable arriving from breaker box:
a) Hot black connects to terminal L.
There should be a brass connector plate that connects terminals L and 1. If this plate is removed, then add a jumper wire from terminal L to terminal 1.
b) white connects to terminal X
5) Cable going to Load
a) Load black connects to terminal 2
b) Load white connects to terminal X along with other white wire.
Aug 20, 2010 | TORK Variable Cycling Timer 8601
Tork Spring Wound Interval Timer Logo
129 people viewed this question
Top TORK Hardware & Accessories Experts
Thomas F. Schneider
pawnpower
Are you a TORK Hardware and Accessory Expert? Answer questions, earn points and help others