Heating & Cooling Logo

Related Topics:

Posted on Nov 23, 2008
Answered by a Fixya Expert

Trustworthy Expert Solutions

At Fixya.com, our trusted experts are meticulously vetted and possess extensive experience in their respective fields. Backed by a community of knowledgeable professionals, our platform ensures that the solutions provided are thoroughly researched and validated.

View Our Top Experts

Armstrong air tech 91 furnace problem

I have a light that is flashing three times which indicates that the pressure switch is open and should be closed. how do i close it?

  • bvn2002 Jan 22, 2009

    I had the same problem

×

1 Answer

Ken Bledsoe

Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

  • Expert 306 Answers
  • Posted on Nov 23, 2008
Ken Bledsoe
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

Joined: Nov 23, 2008
Answers
306
Questions
0
Helped
173321
Points
822

Sounds like the flue is plugged, I had same problem and opened up the draft fan and there was a dead bird restricting the flue. Furnace will never light if the pressure switch never closes as you have found out. Also has anyone moved the switch some are position sensitive meaning have to be in same position factory set the switch. I had one like that also switch was little crooked so I straighten it up and walla worked.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer
0helpful
1answer

Indicator blicks 3 times replaced combustion air switch but did not resolve problem. what do i do now?

There should be a diagnostic chart on the furnace door by the wiring schematic. If so see what the code reads for three blinks.
By the term "air combustion switch" I guess you are referring to the pressure switch. Most diagnostics blinking three times is just a dirty flame sensor. If this is the case the burners will light and go out within 4 seconds. If this is the problem carefully remove the flame sensor and clean gently with emery cloth, fine sandpaper or fine steel wool. Reinsert the sensor and enjoy your heat.
0helpful
1answer

Armstrong air furnace

Have you checked the flue inlet and outlet to see if it doesn\'t have a wasp nest or bird nest or rocks. check the hose that is attached to the pressure switch and the port on the collector box or inducer fan motor to see if it is clear. if you take the switch off and lightly suck or blow into the port it that will close the switch. If you have a manometer you can check the pressure differential. On the pressure switch it will say what pressure in will close at ...Example .52" WC. or 1.25"WC You would attach your manometer to the tube attached to the pressure switch and start the combustion blower to read the pressure. If you have over the reading and the switch didn\'t make you will need to replace the switch. if you have less than you have to make sure the flue is open. You can check the flue with a simple trick by unhooking the flue pipe from the combustion blower and then check the pressure and you may have to unhook the air intake also. If that doesn\'t work you could have a plugged secondary heat exchanger...... Good Luck.
0helpful
1answer

My dukane furnace flashes three lights on the internal circuit board inside the base unit. The error indicates a pressure switch issue. If i pull the tube leading to the unit and blow into it, the u

Most pressure switches run off of a vacuum not pressure, when the inducer starts it actually creates a negative pressure that closes the switch, most boards require the switch to be open on initiation then after the inducer starts it must close, you could **** on the tube and see if you hear it click, or test with a meter for continuity. Draft problems can cause carbon monoxide and kill so do not attempt to jump out a pressure switch or any other control other than for testing purposes. I hope this helps and if it does give me a thumbs up
0helpful
1answer

Armstrong GUK125D20-2B won't ignite

Did he check the Pressure switch was it filled whit water can you make the switch open on the pressure switch when blowing on it? Is the hose from the inducer motor opened and not blocked ? also if there is a block after the inducer motor it will not Ignite. If the Tech does not know how to check a pressure switch get a new tech.
0helpful
2answers

Why does the led on my furnace control bd flash three times

Hello, this indicates a open limit switch. A limit l switch will open when the temp in the heat exchanger gets too high and this switch shuts the Furnace down for safety. Usuaully a dirty filter, weak blower motor, dirty blower wheel will cause a limit switch to open.
0helpful
1answer

Gas Armstrong Ultra V Tech 91-Is green light supposed to flash?

Installed a new filter and furnace is running great now. The old filter was not that old, but we have been doing some remodeling and I figure that is what clogged it so fast.
0helpful
1answer

Armstrong v tech 91 furnace. will not make heat. when on unit runs continuosly no matter what thermistat is set at. could mother board be bad,replaced once already. cah this be done by the home owner to...

These furnaces goes thru 4--steps for complete run time.... step-1, the small draft inducer blower motor blows and prove thru the small air tube that sucks a switch close to tell the circuit board to go to step-2......the glow plug glows for 15 seconds and step 3 the gas valve opens and dump gas in the venturi tubes and lights off the glow plug and proves thru a flame sensor (pin with 1 electrical wire connection) on the last venturi tube which tells the circuit board to go to the last step 4--, to turn on the main blower fan after 90 seconds!. Where ever it stops at then thats where your problem is!
12helpful
5answers

High limit switch open on armstrong furnace

If you know where the high limit switch is you can always cut the two wires and wire them together causing the limit to close. But what you have to watch out for is why the high limit is not closing. That means in your return air either you have a dirty return air duct, dirty filter, or you don't have all your registors open to allow the heat to escape the heat exchanger. Just watch over riding the system. The high limit switch should either be on or behind the blower, in the middle of the system right under the heat exchanger. any other questions about hvac just ask.

David
Not finding what you are looking for?

990 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...