Heating & Cooling Logo
Posted on Nov 15, 2008
Amana gas fired warm air furnace. Blower (fan) works fine when thermostat set simply to "fan". When selector is moved to "heat", burner fires nicely but teh circulatior blower fan does not kick-on. Any suggestions?
Anonymous
Level 1:
  • Contributor 31 Answers
  • Posted on Nov 16, 2008
Anonymous
Contributor
Level 1:
Answers
31
Questions
0
Helped
34396
Points
40
Either bad run cap on motor or bad blower motor
Amana 90 furnace won't ignite. Inducer fan runs for 30 seconds then shuts off and nothing happens. Try to turn fan on at thermostat and nothing happens. Ac works fine.
Most likely one of two issues is occurring. Either the inducer fan is not providing enough draft because it is either spinning too slowly or the impeller is damaged, or the pressure switch that the inducer motor air flow is supposed to activate is not operating properly. If the pressure switch fails to activate, the furnace will not open the gas valve and fire the ignition believing that there is not sufficient draft the vent the combustion gases.
1helpful
2answers
1999 Goodman down draft natural gas furnace. It starts as normal, the burners fire and it warms up, but the blower doesn't start, after a couple minutes the burners shut down and the blower immediently...
IT SOUNDS LIKE THE FAN CYCLE RELAY OR BOARD IS NOT MAKING THE FAN COME ON WHEN IT SHOULD THE BURNER SHUTS OFF PROBABLY BECAUSE IT REACHES THE HIGH LIMIT.
Furnace blower runs after temp is reached
Is your tstat fan selector in auto?? Does the fan ever shut off?
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
1helpful
I installed an RTH2300 this winter to replace an old mercury thermostat. It worked fine for the heating season. I turned it to Cool for the first time today and my AC and furnace blower will not turn...
Maybe turn selector switch to off.see if every thing shuts off.if yes. turn FAN selector switch from (auto) to (on) mode.does the outside unit come on or does just the furnace blower only run ? the inside fan should be the ONLY thing on.if not, reverse the (G) & (Y) wires inside the new thermo.
Furnace fan will not turn on when in "Auto" mode. If switch to "Manual" mode on thernostat, fan will come on, but doesn't blow warm air.
depending on which make aand model of furnace the heating blower relay or heating blower switching device could be bad when you switch the t-stat to manual or on that energizes the cooling blower relay is it gas or electric?
2helpful
I have an early 80's mobile home with an "intertherm gas atmospheric furnace" pilot light is lit but can't get the furnace to "fire". Seems as though the limit control is stuck open. ...
If your pilot light is lit then I would first check your thermostat. Make sure it is on heat setting and fan is on auto, turn stat up to where it should be calling for heat. If you don't get burner to light remove front cover from thermostat and see if it has a mercury switch, if it does move temperature selector up and down and see if you can see a spark in mercury switch vial. If y ou cannot see a spark remove screws that attach t-stat to base.Remove carefully and disconnect wires that go to r and w terminals on stat base. Temporarily connect these two wires together. This should make burner light if you have power to thermostat. If burner does light disconnect wires and replace thermostat. Also if you have a volt meter check across these two wires and see if you have power there. Should be around 24 volts a.c. If your thermostat has a fan on setting try that. If fan runs you know you have power to furnace The gas valve needs 24 volts to operate and inside the electric control box in furnace there is a transformer to step down 110-120 supply voltage to 24 volts. If transformer is working you should be able to hear a low buzz or humming sound. You can also check across gas valve terminals when t-stat is set for heat, you should read about 24 volts. If you have 24 volts to gas valve and it is not opening then you need to replace gas valve. The main purpose of the limit switches is to turn blower on when temperature in heat exchanger reaches fan on temp,shut off blower after burner shuts off and heat in heat exchanger reaches fan off temperature, and limit if temperature exceedes set point without blower coming on. I hope this helps you. Thanks
Our Furnace doesnt seem to be working correct. We an: Air Pro BGM075128 and is Natural Gas. It will turn on when we turn up the thermostat.. but we never get any heat through the vents. There is a...
sounds like the blower motor is not working, if the furnace is actually lighting up and the burns are ignited. You should set your thermostat to auto, as if it is on fan then the fan runs all the time until you take it off of fan. I am a little confused and since I am not there I will give you a website that will walk you through the ignition process, this way we can eliminate flame sensor,ignitor, pressure switch,roll out switch, board,etc. I really hope this helps as I know what it is like to be in a cold house. Good Luck Tim
1helpful
No power to ac indoor fan motor
sounds like you might have a bad control board. try putting a jumper wire on the control board low voltage terminals R and G your fan should come on and run if you have 120v power to fan motor. double check that you do have 120 leaving board and going to motor. if no 120 bad board if you do have 120 bad motor. if it is the board it likely has a bad blower relay which is common in amana models and goodman equipment.