Question about Honeywell HE220A1019 Whole House Humidifier Humidifier
All troubleshooting checks out but still dry air.
Furnace clicks on, whole-house humidifier clicks on. Water comes through valve, trickles down pad (newly replaced), comes out clear tube below unit to drain. Everything looks and sounds great. However, humidistat reads 15%-20% no matter what setting the dial is on. Last winter read 35% all winter consistently with dial set to 40. If everything is working as it should, why is the humidity so low?
6ya staff
SOURCE:
Anonymous
  • 114 Answers
SOURCE: Installation problem
I WOULD CHECK TO SEE IF YOU HAVE ENOUGH V/A OUT-PUT ON TRANSFORMER. I DONT KNOW IF YOURS CAME WITH ITS OWN TRANSFORMER. IF IT DIDNT YOU SHOULD HAVE A MINIMUM OF A 40 V/A RATING STAMPED OR PRINTED ON THE EXISTING TRANSFORMER. IF THE TRANSFORMER IS EXTREAMLY HOT ... YOU MAY NEED A 75 V/A TRANSFORMER WITH THE SAME VOLTAGES. INCREASING THE V/A CANNOT DAMMAGE ANYTHING IT JUST GIVES YOU MORE POWER WHEN EXCESIVE CONTROLS AND WIRING ARE ADDED TO A HVAC LOW-VOLAGE (24v) CIRCUIT. IF YOU LIKE YOU CAN CALL ME AT 727-363-7071. I AM A RETIRED HVAC&R CONTRACTOR WITH 45 YEARS EXPERIENCE. I HATE THE NEW SENSORS THEY HAVE TO ACTIVATE THESE NEW HUMIDIFIERS. I USE TO WIRE THE HUMIDIFIER TRANSFORMER (SUPPLIED WITH HUMIDIFIER) TO THE LINE (110V) SIDE TO THE LOW SPEED ON YOUR BLOWER MOTOR. THAT WAY THE ONLY THING THAT INTERUPTS THE CICUIT IS THE HUMIDISTAT. YOU NEVER WANT THE HUMIDIFIER TO RUN IF YOUR SYSTEM IS NOT "CALLING FOR HEAT". NEVER TRY TO ENERGIZE THE WATER SOLENOID THROUGH YOUR HEAT WIRE(USUALLY SMALL THE WHITE WIRE) FROM THE THERMOSTAT. THIS WILL RESULT IN BURNING YOUR HEAT ANTICIPATOR OUT ON THE T-STAT.
Posted on Apr 28, 2007
Anonymous
  • 30 Answers
SOURCE: Install HE220 HoneyWell , humidity not increasing in the house.
You can try installing the water line to your hot water if it is installed on cold line for more humidification. You should make sure your humidistat is up line 6" @least from humidifier for proper humidification measurement.
Posted on Mar 04, 2008
Anonymous
  • 61 Answers
SOURCE: wiring problem
Sounds like you may have put 120v through a 24v solenoid and humidistat.
Is the HUM terminal on the furnace 120v or 24v?
If it is a 120v terminal you will need a 120x24v transformer and a new solenoid and maybe a new humidistat.
Posted on Jan 02, 2009
mrgrzz
Dale Koehn
  • 88 Answers
SOURCE: HE220A direct wiring to protech 62-24084 control board
it is best to use a seperate transformer for the hummidifier, but in some cases you can use the low voltage t-stat wire that runs your furnace, you will need to have one wire run to common, and the other to the heating side of your low voltage, normally its the red wire hooked to the w circuit of your terminal board, if you do decide to go with an extra transformer, make sure you you have it wired to bring on the humidifier only when the unit calls for heat, hope that helps
Posted on Jan 20, 2009
Anonymous
  • 8 Answers
SOURCE: Wiring issue with the Honeywell HE360A Humidifier
Maybe I can help. this is 24v so it doestn't matter which wire goes where so here goes. 2 wires from humidistat go to furnace, split one of the wires(not both) so they reach the yellow wires on the humidifier. with marettsconnect one of the split wires to one of the yellow wires. do the same to the other split wire and yellow wire. what you should get is one wire from humidistat to furnace then one wire from humidifier to humidistat and one from humidifier to furnace. hope this helps
Posted on Feb 04, 2009
Honeywell he220 humidifier problems
Try removing the cover, and manually cycling on the controler switch? Does the solenoid click on, next to the humidifier (the unit with the water line running through it, with wires coming out of it)? If it does click on, is water running down the water pad? It doesn't necessarily drain water when it's working correctly. All of the water SHOULD be getting evaporated into the air return duct.
If it's clicking on, but no water is running out, you should check the water supply saddle valve and make sure it wasn't turned off during servicing.
If it's not clicking on, you should test that you are getting voltage (12v-18v DC) to the solenoid. If you're not, check all wiring connections and make sure they're tight. If you still don't get power, you have either a problem with your control unit/humidistat, your DC power supply, or the control board on your furnace. You may need to call a HVAC technician at that point, depending on your comfort level/skill level in that regard.
When you say the solenoid "stays hot" do you mean it's physically hot to the touch? Hotter than the water lines running into it?
If the solenoid is getting hot, it probably has a bad coil, and if you continue to operate it, you will probably burn up your DC power supply.
If you're getting voltage, you have water pressure, and the solenoid is still not opening, replace the solenoid.
Jan 05, 2013 | Honeywell HE220A1019 Whole House...
I can't tell if it is working. The humidity reading in the house is 20%. When I open the humidifier, I see that the water is trickling over the filter but it doesn't seem to ever get saturated.
Hello, is there water going down the drain tube, if so then the humidifier is working. The pad does not really get saturated the water just trickles on the pad and the the fan blows it into the air duct. your outside air temp determines what your humidistat should be set at.
Outside Temperature -10 F 0 F 10 F 20 F 30 F Recommended Indoor
Relative Humidity
20% 25% 30% 35% 35%
Feb 23, 2011 | Honeywell HE360A1027 Whole House...
I don't think our h8908b honeywell humidifier is working. The house seems pretty dry. Kids are complaining of dry noses and throats. I have also been pretty dry nosed. How do I know if it is working? And...
Hello, if there is no water draining out of the humidifier than it is not working, The humidifier should turn on and off with the furnace, The best thing to do is have the humidifier tuned up by changing the water panel, making sure the there is voltage present the the solenoid valve, and making sure the water supply is getting to the solenoid valve. Let me know if you have any further questions I will be glad to assist you.
Feb 07, 2011 | Honeywell HE360A1027 Whole House...
Have an HE225A, B By-pass Flow thru humidifier about 9 yrs old. Just change the antimicrobial pad with recommended Aprilair 110/220 and when the furnace comes on, there is a loud, hum-like, vibrating noise...
Make sure the new pad you installed is in the right position. The pad is marked with a black dot about the size of a quarter. This end should be up for proper water flow through the pad.I fwater flow is being restricted at the pad the vibrating nosie that you are hearing is the dry portion of the pad vibrating agaist the platic housing of the humidifier. This noise stops once the pad has absorb enough water in this area of the pad.
Jan 23, 2011 | Honeywell HE220A1019 Whole House...
Our aprilaire humidifier is only 4 years old and it does not seem to be working. We have static in the house and when I did test mode it never drained water like it was supposed to. Any ideas what I can do...
Hope this helps, check and see if humidistat is set to 35% humidity and that bypass damper on humidifier is in the open position or winter position.(humidistat is usually located on cold air return duct near furnace). Next, replace humidifier media pad, remember to replace media pad (filter) annually, you also may want to clean any lime deposit out of humidifier housing with a solution of warm water and white vinegar before installing your new media filter.Remember to turn power off at side of furnace when cleaning humidifier and replacing media. Before installing new media turn power back on to furnace, set humidistat to the on position, turn furnace thermostat above room temp., and inspect humidifier to see if water is running from top,(you may want to have a bucket under humidifier when checking for water), if you see water running, turn power back off to furnace, properly install new media filter, reconnect humidifier cover & set humidistat to 35%. If you do not see water present, check water supply valve to humidifier and make sure its turned on. If water supply valve is open, then check water supply tubing for blockage.And the last things to check is to make sure all registers through out your home are open and not blocked by any objects, also make sure furnace filter is cleaned, if none of this works refer to installation manual to see if humidifier was sized and installed properly, Good luck.
Mar 03, 2010 | Aprilaire 600 Humidifier
Solenoid on Aprilaire whole house humidifier
the solenoid allows water to flow to jet that then runs down the pad the solenoid is control by the stat
Feb 23, 2010 | Aprilaire 700 Humidifier
House is dry though it's quite cold outside and furnace is running. Aprilaire is turned up to 35 (I have a dial, not a digital panel). the water panel is completely dry (should it be?)
unless the humidty in your home is higher then 35%. if it is then the humidifier would not run. try turning it up higher and see if it comes on. Do you hear a click in the humidistat? as you turn up the dail when you hear the click is when the humidifier should come on. Also remember your furnace must be running for the humidifier to come on. if you hear the click and the humidifier fan comes on but no water, you may have a clogged inline filter located in the solinoid valve or a bad soliniod. all parts for your humifier can be purchased from www.aprilaire.com
Feb 05, 2010 | Aprilaire 700 Humidifier
Water keeps running to Honewell 360A Whole House Humidifier
You may need to replace the valve that is wired to the furnace that controls the water flow
Feb 01, 2009 | Honeywell HE360A1027 Whole House...
Honeywell HE225 Humidifier will not draw water
Check for 24volts at the valve. Some techs install these so it only comes on when the furnace calls for heat. It should have its own transformer.
Jan 02, 2009 | Honeywell HE220A1019 Whole House...
Carrier SBP Humidifier is not working
I would suggest turning up the humidistat (usually located on the the return air duct to a higher setting and listening for a "click" noise on the supply valve. If you do hear a click but dont see / hear any water than the culprit is likely the valve itself.
Nov 22, 2008 | Carrier SBP Humidifier
Honeywell HE220A1019 Whole House Humidifier Humidifier Logo
283 people viewed this question
Top Honeywell Humidifiers Experts
Dennis
Simon Benzekri
Level 1 Expert
jdthefixer
Are you a Honeywell Humidifier Expert? Answer questions, earn points and help others