20 Most Recent
Intertherm 56000 Btu Gas Furnace Questions & Answers
Why does it start, then shut down followed by 3 clicks?
- Thermostat calls for heat
- Venter motor starts
- Air switch verifies vacuum
- Igniter sparks, or glows - depending on furnace
- Flame starts in burner
- Flame rod senses flame
- Burner continues to burn until thermostat stops calling for heat
By your description, I would polish your flame rod, it will be a metal rod that is insulated from the bracket that is screwed to the furnace case and it will have a single wire attached to flame rod,
Manual for model C7BAM03648C-C
According to the web, the model C7BAM03648CC is a Westinghouse refrigeration unit. Are you sure you didn't get the number from the top portion?
C7BAM Cased Vertical Coil
• R410 refrigerant-non-ozone depleting
• All aluminum micro-channel coil eliminates formicary corrosion
• Piston metering for all 13 SEER matchups
• Field installed TXV accessory for 14 SEER matchups
Recent Intertherm furnaces have "M" or "CMF" numbers.
Either way, you will probably have to contact a local dealer because their website is useless.
Intertherm Gas Furnaces
Intertherm furnace ignitor will not kick on
furnace operation= call for heat- inducer blower motor energizes- pressure switch makes- after a few seconds ignitor activates.
If this series of processes is not whats happening the furnace may be going into a code safety. Call to discuss further=913-557-9111
FURNACE WILL NOT CUT OFF
If you have a programmable thermostat do the batteries need replacing? Test and re-insert. While there check for any loose wires on it, or at the furnace circuit board. Also make sure none of the wires are touching and metal parts and getting chaffed or shorted. If they are the shot will keep the unit from shutting off and/or cause short cycling.
KW to BTu's
To convert KW to BTU use the following:
1KW= 3412.142 BTU/ hr
Hope this helps.
Bob
Furnace kicks out every so often, ran for two days this time, then kicked out on a pressure switch open, i have replaced the combustion motor ,pressure hose ,and pressure switch, runs for a while then
You are going to need a service man. A magnehelic gauge is needed to properly diagnose a pressure switch issue. Could be a blocked or restricted flue, a defective induced draft motor, cracked heat exchanger, restricted secondary heat exchanger, ect. ect.
Pilot light won't light
Will it initially light, then go out when you release the button?
If yes, then change/adjust the thermocouple or pilot size.
If no, then check that you have a gas supply, that the igniter is sparking, that the gas valve is allowing the pilot flow through.
Furnace lights blows heat in cycle, pops sensor on blower and continuosly blows air until button on sensor is pushed back in
If the sensor knocks the unit off and the the fan keeps blowing without a flame ,the limit (the sensor is a limit comptroller that turns off flame @ a set temp and allows the fan to run until the heat exchanger cools to @ set temp) has out lived its lifetime and needs to be replaced.the button is a manual reset that once reset would allow the unit to continue to run flame and blower at the same time after having been set once, if it is an ongoing problem and needs to be reset more than once then replace the limit control (sensor) in kind. (With the same mode and set-points for the limits)