I have a symmetra RM

The first thing is to make sure the interconnection between the main module and the extended run is properly making contact

Next is to verify the XR battery cabinet voltage is according the battery charging voltage (normally 137 Vdc). Power View will confirm this voltage.

My favorite is to load test the batteries module individually and make sure the batteries are good.

If there is a +/- 3 volts difference between the UPS and the extended run module E0 alarm would be indcated.
11/7/2016 9:47:26 PM • APC Symmetra RM... • Answered on Nov 07, 2016
0helpful
1answer

Symmetra LX with error code E0

Below are recommended steps that will help narrow down the E0 fault. First we will diagnose the XR Frame, the Anderson Connector, and the Communication Card. Then you will reseat the XR Communication Card. Then we will slowly introduce the batteries into the XR Frame to see if anyone of the batteries is causing the issue. Step 1: Remove all of the batteries from the XR Frame. Step 2: Disconnect the XR Frame from the UPS by removing both the Anderson connector and the RJ14 Communications Cable. Step 3: Reseat the Communications Card from the rear of the XR Frame. --> You may need a flat head screwdriver to remove the 2 thumb screws located on the far left and right of the card. --> You will also want to make sure that the Black Frame # selector (small black rectangle with a small white arrow)is switched to the correct number -- in your case 2. This switch is located on the card you just reseated. Step 4: Allow the UPS to see that the XR Frame was removed. --> You can verify this by using the Powerview display: Menu > Diags > Batteries > *here you will have the option to select 'FRAME 1 OF 1' or '1 OF 2' ... You want it to say 1 of 1. Step 5: Reconnect the RJ14 Cable. Step 6: Reconnect XR Frame, with no batteries installed. --> You will want to make sure that the XR Frame comes online by itself. You should see the frame number in red letters/numbers and you will see a green light on the Communications Card. If the XR Frame does not come on then you may have a problem with the Anderson Connector, the RJ14 Cable, or the Communications Card itself -- contact me for help here. Step 7: If the XR Frame is on, reintroduce the batteries into the XR Frame one at a time making sure that you can see the number of batteries increase in the Powerview Display. --> If the E0 error appears again after introducing a battery, then remove the battery, set it aside, and continue inserting the remaining batteries. Repeat this step if the E0 error appears with another battery. If the problem is fixed and you had to set aside batteries -- then all you will need to obtain replacement batteries -- contact me for a quote. After you follow these steps very carefully, you should know what is causing the error or have it fixed altogether. Let me know if this helped :-) If you need Datacenter, UPS, Surge, or Power Related help contact: [email protected] with Power & Systems Innovations 800.260.2259 or go to our website: http://psihq.com/ •• If this helped - click the green 'HELPED' :-) ••
11/7/2016 9:44:48 PM • APC Symmetra RM... • Answered on Nov 07, 2016
0helpful
2answers

How to replace an apc battery back up battery

Depend on model. For 600VA and above Go to APC site and check model of replacement battery. Peel open the front plastic panel and unscrew 2 screws of metal panel. Batteries can be slid out and replacement done when PC is online. Only two wires to disconnect and connect.
3/20/2024 8:29:54 AM • APC Computers &... • Answered on Mar 20, 2024
0helpful
1answer

APC USB2HUB-7P-1V. What is the correct power supply for a usb2hub-7p-1v please?

There is no data on it, just a picture on Amazon India. Contact APC or Newegg direct. Look at the label on the rear of the hub as it may have the input voltage https://www.google.com/search?q=apc+usb2hub-7p-1v+replacement+power+supply ..
2/25/2024 6:58:58 PM • APC Computers &... • Answered on Feb 25, 2024
0helpful
1answer

UPS BE500R-PH microcontroller pic16f716

6/8/2023 7:35:42 AM • APC Computers &... • Answered on Jun 08, 2023
0helpful
1answer

HELP! See details please

I would replace batteries, they do not have a long life. beeping The Back-UPS product has entered a low battery condition - This alarm indicates that the UPS has reached a Low Battery condition and will soon shutdown. The UPS can only operate on battery for a limited amount of time. clicking copy and paste link https://www.apc.com/us/en/faqs/FA158813/
5/26/2023 1:53:51 PM • APC Computers &... • Answered on May 26, 2023
0helpful
1answer

What is APC Event 255? It is beeping occasionally but not continuously.

It means it was Event number 255 and the next one will be Event 266. You can read them on the computer is is connected to. If the beeping is annoying, you can reset it. https://www.apc.com/us/en/faqs/FA156611/#__highlight
2/15/2023 7:28:00 PM • APC Computers &... • Answered on Feb 15, 2023
0helpful
1answer

Where can I get transistor GP4063D/ IR 214 for APC UPS IS1244003099

You can purchase electronic components, such as the GP4063D/IR214 transistor, from various electronic component distributors such as Mouser, Digi-Key, Arrow Electronics, and more. You can also check with local electronics retailers or online marketplaces such as Amazon or eBay. It is best to check the availability of the specific component with multiple suppliers to ensure that you can get the component you need in a timely manner.
2/1/2023 6:08:59 AM • APC Computers &... • Answered on Feb 01, 2023
0helpful
2answers

I need to know where the serial number and model # is located on my APC mini chopper

you to www.apc.com, choose the country you are in, go to product and services, choose the model you have than check what ever you need for the product you have chosen, good luck
8/11/2022 7:22:25 PM • APC Computers &... • Answered on Aug 11, 2022
0helpful
2answers

APC BK650EI 650 VA 400 Watts (1) IEC 320 C13 (Surge Protection) (3) IEC 320 C13 (Battery Backup) Outlets Back-UPS CS 650 USB/Serial. It blinks random orange LED.

I say yes he manual shows ,setting sensitivity here. the sound like charger fail. Inside. inverter works, did you let it charge overnight first. and disable the beeper if annoying. is AC line voltage low? that too can beep. is this USA model 120vac or outside USA> also if the UPS is for another country that will be bad. 650EI , is not the E means European version"??? why skip country. >? and matters huge that. EI is 230vac version, and will be wrong used in 240vac countries and worse. yellow led only blink is low line AC as the manual tells my guess you bought the wrong UPS?> v2 docs but not told version page 2. https://download.schneider-electric.com/files?p_Doc_Ref=SPD_AHUG_990-9237_EN&p_enDocType=Quick+start+guide&p_File_Name=BU+UM+990-9237B+MN01+EN.pdf
6/20/2022 2:52:04 AM • APC Computers &... • Answered on Jun 20, 2022
0helpful
1answer

Hello, I am looking for a schematic diagram for APC 650 BK650 MC. Does any one have it? Thank you.

none officiallysome rare versions leak out, try googling for leaks there is no other way to find leaks, (confidential docs)
5/29/2022 11:13:13 PM • APC Computers &... • Answered on May 29, 2022
0helpful
1answer

My power supply APC UPS-ES 700 won't power on ,at all .

APC.com have many here. there are fuses inside that blow too. not just the rear breaker. fails with NO Loads cables connected at all? 1: batteries shorted or dead. short overload it . there is a battery fuse, easy or hard to find ,easy on my loved smt750C. the true model of you UPS is not front stamps but the rear label tells the truth. 2: turn it on with not batteries yet, some turn on with error light or on mine LCD hard text errors,. no bats. 3: that is about it besides bad PCB. ES-700 those pan-cake UPS. sure. batteries do fail for sure out of the blue. (plates inside can short) out of the blue. or one cell goes dry and open and dead. the battery fresh pulled will read 13.0vdc. (good UPS) not 10 not 1, not 0 13. or 12.8v min. rested 5 hours post charged. the brain inside (firmware) is not very smart. it see's any errors it does not like and turns off fast. blink of eye fast . it can. shorts , or battery seen shorted. or blows fuse, deep inside on PCB up to 400volts inside do not touch that with hands, lethal are you on 240vac? we are 120v here.
2/10/2022 12:31:15 PM • APC Computers &... • Answered on Feb 10, 2022
0helpful
1answer

Why won't the new battery allow the xs go on line

let it charge overnight, (new real or new from ebay not new) never assume it is charged new. make sure rear AC circuit breaker on it is not tripped makes sure battery fuse not blown make sure battery lugs not rusty. learn how to bench charge any AGM battery like this at 3amps max, ? (AND ATV CHARGERS IS WOW HERE) 2004 UPS, many were recalled for not having fuse. on the battery feed. and cause smoke. why use 15-04 -11 year old UPS>? MOST THAT OLD HAVE BIG PROBLEMS.
2/6/2022 12:26:30 PM • APC Computers &... • Answered on Feb 06, 2022
0helpful
1answer

OWNERS MANUAL FOR BR1500LCD

apc.com (step 1 tell them your country first, seems you did not.) most easy question on earth . and answered. in usa most APC were banned in jan 2022, a horror here, most discontinued are still supported with manual and software. not deleted. for even 10 or more years.(found it) i can not decode your model (i guess BR is the code) on the rear or side off UPS is a white sticker or service tag for sure and you did that I see. and on such tag is the real model number even encoded for country . and your unstated countries voltage line input. APC BACK-UPS RS BR1500LCD 1500VA/865W UPS System(2006 made) are you in barbados posted to N.Amercias'/ if yes learn to only go to APC site for your country of find nothing you will..... seems not sold in many countries but is old. https://download.schneider-electric.com/files?p_File_Name=ASTE-6Z7VAU_R0_EN.pdf&p_Doc_Ref=SPD_ASTE-6Z7VAU_EN&p_enDocType=Quick+start+guide
2/5/2022 6:55:23 PM • APC Computers &... • Answered on Feb 05, 2022
0helpful
1answer

APC BACK- UPS ES 500 IS NOT SWITCHING ON !

the batteries are bad now. for sure parked like that. kills themn.
2/5/2022 3:55:12 PM • APC Computers &... • Answered on Feb 05, 2022
0helpful
1answer

Model 420 Pro. Why is output only 84 VAC?

no real model told , off rear sticker, (tell sticker model first) 420va no country told no line voltage told in your country Did you buy the ups from wrong country(oops) and it has higher input voltage spec and yours is lower input? (real) nobody can guess what's up there. history and all that and location, voltages are not the same word wide at all nor frequency 50/60Hz did you buy a used UPS. if yes from where ebay, and from wrong country or it ran for years and fails now. or outputs overloaded on it.
2/5/2022 3:47:12 PM • APC Computers &... • Answered on Feb 05, 2022
0helpful
1answer

I have a APC BR600CI-IN ups.its battery not getting charged then i installed a new battery.but create same problem after 2 days.i need to know which component is bad.ic TNY 275 pn?

international model (i) in Europe are you speaking english./? the main board is bad apc does not sell:
  • spare boards
  • nor schematics
  • nor BOM (bills of materials)
they do have service contracts out of warranty .$$$$$
  1. buy new one. whole
  2. buy used one good.
are 2 choices.
2/5/2022 3:29:39 PM • APC Computers &... • Answered on Feb 05, 2022
0helpful
1answer

I have ups from APC (SRT 8000 va) when me make upgrade to the ups the laptop turned off and upgrade does not completed and I can't upgrade ups again because it is turned off, no response ,help

ok , modern like mine but way bigger, 8kw (va) So let me guess you did the UPS FIRMwARE update? I just did min yesterday. no problem UPS wired to internet router. UPS battery must not be bad, <<< read 3 times. all loads removed. no laptop needs UPS a laptop has its own inside. UPS is now dead? as you may know all things made on earth with firmware (or BIOS) when updated, can cause it to brick, vast ways. 10-20 ways on PC but on this UPS mostly 3 ways. not following the manuals instruction step by step, guessing fails battery bad. UPS has other errors, , the log file errors must NONE, using powerchute app to see them. or internet dies mid stride. bad luck there.
2/5/2022 3:26:45 PM • APC Computers &... • Answered on Feb 05, 2022
0helpful
1answer

Model RS 1000. IC 19 is burning. What is replacement?

APC does not produce BOM s ever. bills of materials, (a secret so china can not steal the design,dig) nor real schematics. i bet those caps are shorted. and QA19 is the victim not cause. 99% of the time bingo. or got hit by lighting or plugged in 120vac UPS to 208v line. oops, that be BAD, buy used UPS on ebay and use it for spare parts ,as APC does not sell FRM this level, (devices on PCB )
2/5/2022 3:11:43 PM • APC Computers &... • Answered on Feb 05, 2022
Not finding what you are looking for?
APC Symmetra RM 6kVA UPS System Logo

2 questions posted

Ask a Question

Usually answered in minutes!

Top APC Computers & Internet Experts

Cindy Wells

Level 3 Expert

6688 Answers

Grand Canyon Tech
Grand Canyon Tech

Level 3 Expert

3867 Answers

Rob Hill
Rob Hill

Level 3 Expert

1480 Answers

Are you an APC Computer and Internet Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

APC Computers & Internet

  • APC Computers & Internet

Most Popular Question

symmetra lx error code e0

  • Computers & Internet
Loading...