The fan doesnt go on

use this link to help you with your questions about the april aire 700. this link will have an owners manual as well. Hope this helps.


http://www.aprilaire.com/index.php?znfAction=ProductDetails&category=5&item=700
12/29/2010 11:36:31 PM • Aprilaire 700... • Answered on Dec 29, 2010
0helpful
1answer

When furnance turns on and

The first to check is if you are getting 24 volts to the solenoid valve and if you are getting 120 volts to the humidifier via receptacle.
12/29/2010 2:53:21 PM • Aprilaire 700... • Answered on Dec 29, 2010
0helpful
1answer

Replaced water panel and the

Sorry to read about your problem, I hope this helps you out.
did you hit the reset

Digital Humidifier Control (Model 700): (Automatic or Manual mode) Check system operation and reset Change Water Panel indicator by setting the knob to "Test/Reset". With HVAC blower operating and HVAC calling for heat, humidifier will operate for one minute. DO NOT LEAVE IN TEST MODE AS HUMIDIFIER WILL NOT OPERATE.

I tried to help you. Please help me and Rate/Vote on my response. We take the time to answer your question. take the time to rate us.Thanks and good luck

4 Thumbs - Very Helpful
3 Thumbs - Helpful
2 Thumbs - Somewhat Helpful
1 Thumb - Not Helpful
12/29/2010 4:11:45 AM • Aprilaire 700... • Answered on Dec 29, 2010
0helpful
1answer

My aprilaire won't turn on,

You need either a sail switch or current sensing relay to turn the humidifier on and off when the blower motor turns on. They both accomplish the same thing but in differant ways, a sail switch senses the airflow in the return air duct and a current sensing relay senses the current from the blower motor.
12/21/2010 9:21:00 PM • Aprilaire 700... • Answered on Dec 21, 2010
0helpful
1answer

Has been working well for past 5 years and now the

May be an issue with the solenoid valve. check for voltage at the valve. if there are error codes check the owners manual for cause. I am providing a link to the manual if you don't already have one. the last thing to check would be the control itself. the control and the solenoid valve are the 2 main items for the unit. hope this helps.
http://www.aprilaire.com/themes/aa/en/manuals/AA-Humidifier-Owners.pdf
12/21/2010 3:35:43 PM • Aprilaire 700... • Answered on Dec 21, 2010
0helpful
1answer

My Aprilaire humidifier is not working, even with

May be an issue with the solenoid valve. check for voltage at the valve. if there are error codes check the owners manual for cause. I am providing a link to the manual if you don't already have one. the last thing to check would be the control itself. the control and the solenoid valve are the 2 main items for the unit. hope this helps.
http://www.aprilaire.com/themes/aa/en/manuals/AA-Humidifier-Owners.pdf
12/21/2010 1:14:34 PM • Aprilaire 700... • Answered on Dec 21, 2010
0helpful
1answer

When my aprilaire humidifier turns on it leaks

A couple of things to check would be, Is the seal around the drain tube connector leaking where it connects to the unit itself. Is it possible too much water flow into the unit. It sounds like you have covered all other options.
12/20/2010 5:11:10 AM • Aprilaire 700... • Answered on Dec 20, 2010
0helpful
1answer

My 700A will not stop

Are you using a current sensing relay with this humidifier or a sail switch?
12/19/2010 3:00:05 AM • Aprilaire 700... • Answered on Dec 19, 2010
0helpful
1answer

The change water panel light

I'm not an hvac guy, but I'll throw this in...is it possible that the relay contacts are welded closed, even though the relay has open coils? With all the power off, try to see if that's the case, and change it, but check everything ahead of the relay to make sure there's no short drawing excessive current.
Hope this helps.
12/19/2010 1:58:22 AM • Aprilaire 700... • Answered on Dec 19, 2010
0helpful
1answer

My Aprilaire 700 humidifier isn't turning off from

bad thermostat it sounds like
12/17/2010 1:39:16 PM • Aprilaire 700... • Answered on Dec 17, 2010
0helpful
1answer

The humidifier is not coming on. I am not getting

Hi,
If you have an electric meter which I hope is how you determined that there is no voltage to the controller.... check for power coming from the furnace to the humidifier....that should be 110v power... then go to the transformer for the humidifier and check for 24v power coming off of the secondary of the trnasformer...
For most furnaces the terminal for the humidifier will only be powered when the blower is running...

if you have 120 v power going to the transformer and no 24v power coming out of it then the transformer is bad...if there is no 120v poweer then the board is bad...

heatman101
12/16/2010 9:43:01 PM • Aprilaire 700... • Answered on Dec 16, 2010
0helpful
1answer

Water is not getting to the humidifier

Check the valve to make sure its not corroded. You may need to replace it.
12/11/2010 3:21:49 PM • Aprilaire 700... • Answered on Dec 11, 2010
0helpful
1answer

What do we set the 700 Humidifier at

Hi,

That depends...
In mild weather you will want it at about 40% and then if it gets really cold where you are... like 0 or below then you will want to back it off to about 20%...

best gauge to tell is that is you are getting condensation on your windows then you have it too high...

heatman101
12/5/2010 4:46:44 AM • Aprilaire 700... • Answered on Dec 05, 2010
0helpful
1answer

My Aprilaire 760 humidifier will not turn on. I

you should have an upstream and a down stream sensor and maybe a remote sensor too. They could be the issue. Google aprilaire 760 humidifier installation instructions at aprilaire's site and see where and how many you have. It cold be the control module too. Try ehow.com too. good luck
12/2/2010 11:13:01 AM • Aprilaire 700... • Answered on Dec 02, 2010
0helpful
1answer

When does the humidifier fan start? Does the water

Humidifier should be powered from the furnace heating 24 volt terminals through a humidistat and then to your humidifier. The fan and the water solenoid on the unit should come on together. if the water is not turned on the fan should still run, unless the unit is not plugged in.
11/27/2010 1:34:13 AM • Aprilaire 700... • Answered on Nov 27, 2010
0helpful
1answer

Water does not deliver to the evaporator panel

3 things it can be, If the humidistat on the wall or installed in your return air ductwork by your furnace is not set high enough it may not be calling it on. set it higher until you here it click. If it is set high enough it should power a solenoid valve to send water to the panel. Solenoid may be bad. Make sure the water line feeding the humidifier is opened. Should be a small copper line from the 700 to a cold water pipe.
11/27/2010 1:14:20 AM • Aprilaire 700... • Answered on Nov 27, 2010
0helpful
1answer

Change water pad but change water panel light is

Turn the control knob to the
“Test/Reset” position until the “Change
Water Panel” light blinks to reset the
water panel change indicator timer.
(Blower must be operating and furnace
calling for heat.) Be sure to turn the
control knob back to the prior setting when finished
11/24/2010 4:13:55 AM • Aprilaire 700... • Answered on Nov 24, 2010
0helpful
1answer

Aprilaire 700. It works

It appears your Aprilaire model 700 is wired to only operate when your HVAC fan is operated by your thermostat. Your HVAC installer can wire the humidifier control to operate the humidifier during a heat call, fan call or to turn on the fan when there is a need for humidification. Please contact your HVAC installer to have them change the wiring.

Thank you for giving us the opportunity to be of service
Sincerely,

Brad Uselmann
Technical Support
Research Products Corporation
www.aprilaire.com
11/18/2010 4:17:05 PM • Aprilaire 700... • Answered on Nov 18, 2010
0helpful
1answer

Have aprilaire #760 ,changed water panel, and

Typically, we find that the most common reason that you start to see leaking from the humidifier is that the water panel is not changed frequently enough. We do recommend that the water panel be changed once every humidifying season. We find a majority of our customers do this maintenance typically at the start of the humidifying season.

Here are the things to check when troubleshooting a power humidifier, which is leaking:

1.Position Of Unit On Plenum
Is the unit level (let to right)?
Is it plumb (front to back)?

2.Feed Tube
Is the Feed Tube tightened or is there a crack in the tube?

3.Position Of Scale control insert-
Is the base of the scale control insert sitting firmly in the drain spud at the base of the housing?
Does the bottom of the scale control insert have a taper to it to direct water to the drain spud?
Is the Scale control insert positioned correctly? The scale control insert has a front and a back. The back of the water distribution tray has an indentation in it to allow for clearance of the nozzle, which is attached to the top of the base. If reversed, and forced into place, the water distribution tray will break off the nozzle attached to the water feed tube and potentially the housing, causing water to leak

4.Water Panel Assembly-
Are there aluminum strands hanging out of the scale control insert?
Is there a gap between the top of the water panel and the water distribution tray for air to go through?
Is the colored dot on the water panel, up?
Is there a consistent coating on the Water panel, or are there shinny spots or clumps of coating?

5.Water Entrainment (Water Blowing out of the Humidifier)-
Are there signs of entrainment? Mineral build-up on fan blade, shroud, inside of cover?
Is the static pressure in the plenum over .4w.c.? If so, entrainment and leaking could occur.

6.Missing Orifice
If there is no orifice in the unit, the water entering the system could flood the panel. To check
for proper water flow, a quart jar should fill at the drain line in about 2 ½ minutes for a red or blue orifice, 5 minutes for a white or yellow orifice.

7.Drain line-
Is the drain line plugged?
Does it have a good downward slope?
Is it teed with any other drain lines?

If the above items do not resolve the existing leaking we would recommend contacting the customer service line at 800-334-6011 for further technical support.

Regards,



Tracey Hadju
Customer Service Specialist
Research Products Corporation
www.aprilaire.com
11/18/2010 4:11:15 PM • Aprilaire 700... • Answered on Nov 18, 2010
Not finding what you are looking for?
Aprilaire 700 Humidifier Logo

298 questions posted

Ask a Question

Usually answered in minutes!

Top Aprilaire Humidifiers Experts

Paul Carew

Level 3 Expert

3808 Answers

Cindy Wells

Level 3 Expert

6688 Answers

john h

Level 3 Expert

29494 Answers

Are you an Aprilaire Humidifier Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

Aprilaire Humidifiers

  • Aprilaire Humidifiers

Most Popular Question

aprilaire humidifier 110

  • Humidifiers
Loading...