20 Most Recent
Goodman GMS807034ANA Heater Questions & Answers
Blower comes on , then flame thing, but wont turn
OK, I think the flame thing may be an igniter. So the inducer turns on, the igniter glows but the gas valve does not open so there is no ignition. Sounds like you may have either a bad gas valve or a bad circuit board. You will need to check for 24 volts at the gas valve. If you get voltage but no ignition, replace gas valve. If you get no voltage at gas valve, replace the circuit board.
1/23/2011 12:41:11 AM •
Goodman...
Answered
on Jan 23, 2011
My vent motor assembley motor, makes a humming
This motor is no good and needs to be replaced. humming means it is getting power to it but is it getting enuff? I think from the sound of your problem the brushes are bad or it could be a worn armature. When the power is disconnected does it turn freely it probably does. If it doesnt and is still stiff you could oil it to free it up and then it may work
1/16/2011 12:10:18 AM •
Goodman...
Answered
on Jan 16, 2011
We have a goodman split unit, It was below
The symptoms seem to be related to the main blower motor and/or it's capacitor. Turn the system off for a couple of minutes and then turn just the fan on while the thermostats heat setting is in the off position. If the lights still dim then replace the motor and capacitor. The clicking noise is the fan relay.
1/1/2011 6:38:16 AM •
Goodman...
Answered
on Jan 01, 2011
No heat, but the fan
Sorry to read about your heater problem.
Chances are you have a defective glow rod, this is the electronic pilot lite for the system, i would guess its not lighting the gas for heat
THIS IS A GAS PRODUCT, INCORRECT REPAIR CAN CAUSE A EXPLOSION, AND DEATH CAN OCCUR. IF YOU DO HAVE THE PROPER TOOLS SUCH AS MANOMETER AND LEAK DETECTORS, I SUGGEST YOU CONTACT A SERVICE COMPANY.
I tried to help you. Please help me and Rate/Vote on my response. We take the time to answer your question. take the time to rate us.Thanks and good luck
4 Thumbs - Very Helpful
3 Thumbs - Helpful
2 Thumbs - Somewhat Helpful
12/29/2010 11:29:18 PM •
Goodman...
Answered
on Dec 29, 2010
Gas heater doesn't stay on longer than 5 minutes.
It sounds to me that your air flow is restricted somewhere. The first thing to check is your air filter. If that gets real dirty your restricted air flow will cause the hi-limit(hi temperature limit switch) in your heat exchanger compartment to over heat and open up your gas valve electrical circuit,thus, shutting off the gas to your burners. After the hi-limit switch cools down the furnace will go back to heating again then it will overheat again(you get the picture?) If it keeps cycling on and off like that the house will never get warm if it is cold outside. If your air filter is reasonably clean(you should be able to see light thru it easily) then the secondary heat exchanger could also be dirty, this is located above the indoor fan housing, you would need to pull the indoor blower assembly out of the furnace and look up above. The secondary heat exchanger looks similar to a radiator will fins. You can use a medium stiff plastic brush to brush the dirt,hair, whatever off of it. Another problem spot would be the cooling evaporator coil (if you have central airconditioning) located most likely above the furnace in the plenum(if your furnace is in a basement). This usually is difficult to access if an access cover wasn't installed when the airconditioning was installed. I would recommend an experience service tech to clean it for you. Also make sure all you supply air registers and return air registers are open . These are the things I would check first. Good luck!!
11/20/2009 12:47:18 AM •
Goodman...
Answered
on Nov 20, 2009
Bad control board?
This is a good one! I would check for a blocked vent or intake pipe first. Also check to make sure the condensate lines are free of moisture or debris. What is the code for three blinks?
10/22/2009 3:31:55 PM •
Goodman...
Answered
on Oct 22, 2009
Circuit board fuse keeps poping
Traced wires and found the wires to the humidifer were the cuprits. I beleive the solenoid may be no good. After disconnecting the wires to the humidifier, A/C and Heat are working fine now .
5/29/2009 4:25:24 PM •
Goodman...
Answered
on May 29, 2009