20 Most Recent Siemens 20 Amp Single Pole Breaker 120/240 Volt Questions & Answers
Can a 240 volt outlet be ran off this breaker and
You need 240 breaker:
Notice that your 240V breaker is twice as wide as regular 120V breaker.
Notice that both switches are tied together on 240V breaker, making this a double-pole breaker.
For more information about breakers and 120-240V circuits:
http://waterheatertimer.org/See-inside-main-breaker-box.html
http://waterheatertimer.org/B220C.html
1/25/2011 12:42:46 AM • Siemens 20 Amp... • Answered on Jan 25, 2011
Siemens QF230A keeps tripping after installation.
So likely you have a 3 wire dryer cord and a 3 wire branch circuit. The dryer neutral is bonded to the dryer frame and the third wire of the dryer plug.
There were code exceptions for dryers and stoves that allowed timer motor circuits to use the neutral as a current carrier and frame ground.
To use the GFCI for the dryer you will be required to add an additional conductor (new 3 wire+ground cable) and separate the neutral to frame bond in the dryer and use a 4 wire dryer cord.
Likely you also have some GFCI single pole breakers and replaced ungrounded receptacles with grounded (another code exception) and they work OK. The dryer and stove are different as there is current on the third wire where as on the ungrounded receptacle GFCI there is no 3rd wire.
In breif, the neutral (current carrier conductor) from the dryer must be isolated from the dryer frame and dryer ground (fault current carrier conductor).
Or just leave it the way it was.
Check with local authority with jurisdiction for local code requirements.
6/25/2020 12:19:41 AM • Siemens... • Answered on Jun 25, 2020
2answers
No electricity in all bathroom outlets
you may have agfi outlet in the circuit. the outlet has 2 push buttons in the middle. it maybe an outside outlet that is tripped some contractors hook up the circiut like that
11/25/2017 8:43:32 PM • Siemens... • Answered on Nov 25, 2017
How do I lock out a 200 amp Siemens circuit breaker ?
Check garvin Industries website. they offer a multiple of different lock systems for breakers
10/7/2017 8:37:47 PM • Siemens... • Answered on Oct 07, 2017
Siemens 200amp Load Centre will not reset and no power to box after a short in the bathroom?
It sounds like the breaker at the metering base is tripped. You will need to locate the meter base outside to find the breaker. You can also call your local utility company service provider and report a power outage. they typically will come out free of charge to verify power.
4/28/2017 12:13:52 PM • Siemens... • Answered on Apr 28, 2017
I have a Siemens Outdoor Load Center W0408ML1125. It has the neutral bar but not the ground bar. Where do I attach the ground?
Yes it's correct the Ground Bar connects to the metal box, scrape some paint off to make a good bond, this also requires 4 wires to be correct, green ground, white insulated neutral, black L1 and red L2
2/27/2015 2:02:50 AM • Siemens... • Answered on Feb 27, 2015
NEC code for 50 amp service panel
Don't think there is one that small. Are you asking the right question?
11/30/2014 11:59:07 PM • Siemens... • Answered on Nov 30, 2014
What are the circuit breaker part numbers for a Siemens Ite G3030MB1200 Panel
Go to any home store and ask them, they will have the breaker or one to use as a replacement
11/28/2014 3:21:05 AM • Siemens... • Answered on Nov 28, 2014
2answers
MY WIFE HIT HER SHOULDER
Flip each breaker all the way off and then all the way back on.. If that doesn't fix the problem, look for a tripped GFI (go around and press the reset button on any outlets that have the buttons "test" and "reset"). If that still doesn't work, you should probably contact an electrician.
9/15/2014 7:05:08 PM • Siemens... • Answered on Sep 15, 2014
0answers
Siemens 5sx21
Be the first to answer 1/10/2014 3:03:03 AM • Siemens... • Posted on Jan 10, 2014Be the first to answer
Activating shunt trip circuit on vl160n
A shunt is always energized and it has a purpose. The purpose is to bypass some of the load from the main circuit. It would be tripping due to overload
5/22/2013 11:39:43 PM • Siemens... • Answered on May 22, 2013
Breaker tripped and when reset still no power to outlets. there are 2 with gfci and 2 without niether gfci will reset whats up?
reset the GFCI and they will all work. The other two are down stream from the gfci.
4/7/2013 5:24:31 AM • Siemens... • Answered on Apr 07, 2013
I cant seem to set
http://www.buildingtechnologies.siemens.com/bt/uk/SiteCollectionDocuments/sbt_internet_uk/residential/instructions/rwb9_i.pdf
Here is the full manual.
If all else fails, try disconnecting power and reconnecting.
Or Reset.
You are on your own with either of the last two suggestions.
Gary
12/21/2010 6:31:21 PM • Siemens... • Answered on Dec 21, 2010
I have a Bulldog Pushbutton breaker box and one of
You cane replace that with the 20/40/40/20 as long as the wire size on the two 20 amp poles are at least 12 gauge wire. It is a very good possibility that the wire is #12 wire, but you will have to verify that for sure before installing that breaker.
All of those breakers are getting more difficult to find and I'm sure that the quad is even more difficult.
Hopefully you have the 12 wire and then it will be no problem and you will be in good shape.
heatman101
10/12/2010 9:58:31 PM • Siemens... • Answered on Oct 12, 2010
I want internal diagram or application of simens
The replacement for the 3UN8004 is a 3RN1010-1CM00 Here is a linke to the Siemens manual for this newer version.
http://support.automation.siemens.com/WW/adsearch/pdfviewer.aspx?HitsPerSite=10&ehbid=html_76%2Fehb%2F35681283%2Ehtm&lang=en&nodeid=38823237&siteid=cseus&query=3RN1010-1CM00 &page=1&view=new
8/27/2010 1:26:03 AM • Siemens... • Answered on Aug 27, 2010
I tried to replace my 15 amp 2 pole breaker with a
probably picked up wrong breaker for panel put then side by side for comparison if not same return get correct one
10/7/2009 3:00:33 PM • Siemens... • Answered on Oct 07, 2009
Siemens 20 Amp Single Pole Breaker 120/240 Volt Logo
2 questions posted
Top Siemens Electrical Supplies Experts
john h
CJ Rock
CJ Rock
Are you a Siemens Electrical Supply Expert? Answer questions, earn points and help others
View Most Popular
  • Siemens Electrical Supplies
Most Popular Question
240 volt outlet ran off breaker
  • Electrical Supplies