Questions & Answers for: superheat subcooling

Question about Carrier Heating & Cooling

1 Answer

superheat Subcooling - The difference between the temperature of the Small copper line (Liquid Line) and the high-side (red) gauge temp on your manifold Superheat - The difference between the temp. of

Ad

Question about Heating & Cooling

2 Answers

subcooling temperatureof about nine degrees. You have too high of a superheat reading. verify that the bulb for the txv is correctly positioned and insulated. if it is then you need to remove the bulb

Ad

Question about CKL60AR60 Air Conditioner

1 Answer

superheat and subcooling close to spec. superheat right on. subcooling a few degrees high. 20 temp split across evap. problem compressor amps very low. about 7 amps on 90 degree day. is this a problem

Question about CW-1006FU Air Conditioner

1 Answer

...superheat. Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, ...

Question about 12AJA3601AH Air Conditioner

1 Answer

...on many factors. Based upon the info you have supplied, I would guesstimate that the operating pressures would be in the neighborhood of 350/160 to start and get the subcooling and superheat in

Question about 12AJA3601AH Air Conditioner

1 Answer

superheat verses subcooling give discription superheat is the difference of line temperture at suction of the compressor to the pressure converted to temperture for freon used in system. subcooling is

Question about 12AJA3601AH Air Conditioner

1 Answer

superheat subcooling Where can we find the superheat for a Delfield SSDTR1-SH. It is not in the service manual. the model says that this is a cooler/freezer combination unit. super heat has to be ...

to check these. Superheat and subcool will tell you if your unit is properly charged and if you metering device is working properly. A typical superheat and subcooling value is around 10 to 15 degrees

Question about CLQ36AR49 Air Conditioner

1 Answer

...superheat and subcooling to check for the proper operation of your system when the compressor is running. I ran into a case just yesterday, the breaker kept tripping. Unit had the same readings as ...

...by a txv not metering properly, or an overcharged system. You will need a tech who can determine superheat and subcool for your refrigerant system. Find a tech who can determine these values. ...

Not finding what you are looking for?

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating & Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...