Question about Powerware 9330 40 (A40401110031112) UPS System
1)can not power off ups 2)Normal indicators--no green when the UPS is operating in Normal mode 3)battery--no yellow indicators when the UPS is operating in Normal mode and no power support to equipment 4)Bypass--no yellow indicators illuminated,when the UPS at the Bypass mode 5)alarm--this red indicators is illuminated but no error show at the display
4 Suggested Answers
SOURCE:
tech240
  • 169 Answers
SOURCE: Bypass alarm flashing on a Powerware 9125 UPS
it is possible the bypass alarm is flashing because the i/p and o/p are not within range to switch without a break.
they need to be nearly equal in volts and freq so when the ups switches the ups o/p is continuous.
you should be able to check this with your ups software.
Posted on Sep 16, 2009
  • 45 Answers
SOURCE: UPS in bypass with alarm code 2 short beeps and 5 long beeps.
You can view the manual here: http://powerquality.eaton.com/Products-services/legacy/9150-info.asp
You can also contact the Eaton service department as they'll know this UPS better than anybody. They acquired Powerware years ago and kept the service personnel.
Toll Free: 1 800 843 9433
International: +1 919 871 1800
E-mail: LargeUPSTS@Eaton.com
Posted on Nov 09, 2010
  • 45 Answers
SOURCE: I, Bypass battery and nomral mode are blinking
Here is the link to all of the documentation:
http://powerquality.eaton.com/Products-services/legacy/9125-info.asp
You can also contact Eaton. Eaton bought Powerware 5-6 years ago.
Toll Free: 1 800 356 5737
E-mail (Hardware): SinglePhaseTS@eaton.com
Posted on Mar 01, 2011
Sukam 800VA inverter continuously beeping with 3 lights blinking. What could be wrong?
check batry voltage or 2nd problem in realay and capicitors or
3rd ic before that disconnect output line
May 05, 2014 | Computers & Internet
No output
You should start with Rotary switch on "Maintenance Bypass" position and Qf1 open.
Turn Rotary Sw to "Test" position and wait for self test to execute and UPS to turn on.
Once you get the Yellow lamp lit, it is asking for QF1 to close
Once closng QF1, if green LED is lit, turn UPS off by pressing gray button until it ask for confirmation, select Yes and press Return.
Turn Rotary Sw to Normal position, press On button and the green LED will illuminate.
If, after closing QF1, the green LED didn`t lit, turn Rotary Sw to Normal, press On button and wait for green LED to lit.
Thats`it...
if anything is not working well.. please let me know.
Mar 25, 2014 | MGE UPS Galaxy 3000 UPS System
Charging light flashes quickly between green and yellow. Normal?
No. Most UPS's should have a Solid Green Led on if the unit is running good. This might be indication that UPS has batteries that are not charging completely which mean they are depleting. How old is this UPS and the batteries? Have you changed the batteries yet? Need more info. Do you still have the manual. Always keep UPS manual handy. I have a ton of manuals but not for these little UPS. Mine are for 10kVA to 1000kVA 480v to 208v. Anyways hope I helped.
Dec 21, 2013 | Hi-Capacity Zoeller 510-0005 Basement...
Error light in my apc smart ups sc 1500va ups
1. Four beeps every 30seconds (On Battery LED will be illuminated)
This alarm indicates that the Battery PowerSupplied outlets are now supplying battery power as opposed to power from theutility. If the UPS determines that the input utility power is unsafe for yourcomputer equipment, the UPS will switch to battery power.
Note: Ifthe power disturbance is brief, you may only hear one or two beeps.
2. Continuous Beeping (On Battery LED will beilluminated)
This alarm indicates that a Low Batterycondition has been reached and that the UPS will soon shutdown. Once the UPStransfers to On Battery operation, it can only stay on battery for a limitedamount of time. The UPS will sound this alarm about two minutes before thebatteries are totally exhausted. Once exhausted, the UPS will shutdown and turnoff its output power to your equipment. If you hear this tone you shouldimmediately shutdown your computer to prevent data loss or corruption.
3. Continuous Beeps for 30 seconds (BackUPS OFFICE 250 and 280 ONLY)
This alarm indicates the unit has detected anOverload condition after it has performed a self-test during start-up.
4. Continuous Two-Tone Beep
This alarm indicates a severe Overload wasdetected while the unit was on-battery operation. This tone will continue tosound until the unit shuts down.
5. Continuous Tone (On Battery LED will beflashing)
This alarm indicates that the battery-poweredoutlets are overloaded.
6. Continuous Tone (On Line and On BatteryLEDs flashing) Back UPS OFFICE 350,400, and 500 ONLY
This alarm indicates that an internal UPS faulthas occurred.
Dec 08, 2011 | APC Smart-UPS SC 1500VA UPS System
Hi! Per our UPS problem is when open 3 or 4 hours, then auto Off the UPS. please let me know what the problem. And i need to change the PCB board or just repair the PCB board? Thanks Regards
If you unplug the unit and it powers your PC for 3 or 4 hours then turns off, it is because the batteries are empty and this is normal. If it is plugged-in with power and shuts itself off after a few hours, then the battery cells may be in need of replacing. You can purcase an inexpensive replacement battery here: http://www.upsforless.com/browseproducts/Powercom-Replacement-Battery-Kit-BNT-500A-BNT-500AP-BNT-600AP-BNT-800AP-KIN-425CSU-KIN-625CS.HTML
Dec 01, 2010 | Powercom BNT-600AP (bnt600ap) UPS System
The unit beeps
I am getting these directly from the user manual (available here: http://www.apcmedia.com/salestools/ASTE-6Z7VAQ_R3_EN.pdf)
Issue: On Battery - UPS is supplying battery power to the load connected to the Battery outlets.
Visual Indication: Power On LED - ON (off during beep)
Audible Indication: Beeping 4 times every 30 seconds
Stops When: UPS transfers back to Power On operation, or when UPS is turned off.
- OR -
Issue: Sleep Mode - During On Battery operation the battery power has been completely exhausted and the UPS is waiting for utility
power to return to normal.
Visual Indication: None
Audible Indication: Beeping once every 4 seconds
Stops When: Utility power is restored, or if utility power is not
restored within 32 seconds, or the UPS is turned off.
All other issues are CONSTANT tones, which you did not specify, or there are no audible tones associated with it.
Apr 07, 2010 | APC Back-UPS ES 350 - UPS ( external ) -...
How to take ups in manual bypass mode.
You definitely want to follow the manual procedure to avoid a possible load loss:
http://powerquality.eaton.com/Products-services/Backup-Power-UPS/9390.aspx?cx=3
9.1.4 Transfer from Normal to Bypass Mode
To transfer the critical load to Bypass mode:
C A U T I O N
In Bypass mode, the critical load is not protected from commercial power interruptions and abnormalities.
1. Press the CONTROLS pushbutton on the main menu bar. The System Controls
screen appears.
2. Press the BYPASS pushbutton on the System Controls menu bar.
The UPS transfers to Bypass mode and the critical load is immediately supplied
by the bypass source. If the bypass source is not available, the power processor
remains on and an alarm sounds.
3. The UPS is now operating in Bypass mode and the BYPASS status indicator is
illuminated.
The power module (PM) status indicates READY. The system is now on bypass
and the UPS power processor remains on.
At this point, you can operate an external bypass switch to get to maintenance bypass if needed.
Oct 14, 2009 | Eaton PW9390 UPS System
APC Back-UPS ES 350 - when powered on has a blinking green light Is this normal
A blinking green light is likely an indication that the internal battery is nearing the end of its usable life cycle. If it's over 3 years old this is likely the case. To test, plug something in to the battery outlets and pull the plug of the UPS from the wall. If you get a short runtime (or none at all) it's the battery. Batteries are under $20 and can be found here: http://www.batteryinternational.com/apc-backups-es-be350u-ups-battery-ups-batteries-f1.html
Oct 06, 2009 | APC Back-UPS ES 350 - UPS ( external ) -...
Bypass LED on the ups is on
This an excerpt from the UPS's manual:
The Bypass LED illuminates indicating that the UPS is in bypass mode. Utility power is sent directly to connected equipment during bypass mode operation. Bypass mode operation is the result of an internal UPS fault, an overload condition, or a user initiated command through an accessory. Battery operation is not available when the UPS is in bypass mode.
Jul 19, 2009 | APC Smart-UPS 1000VA UPS System
Belkin UPS F6C800 Problem
My name is Vikram Kumar Thumu, from India-Hyderabad. I have seen your message on the issue related to Shutdown of UPS whenever there is a Power Surge. I would like to provide my suggestions on the issue. I hope that this should work for you and will resolve the issue.
I see that you are using
Generally, the issue happens if you are not using the UPS as per Manufacturer specifications or if it is overloaded frequently then UPS  shutdowns
To isolate the issue, I recommend you to check and go through below information.
If you see ON BATTERY a Yellow LED OR Flashing Yellow
LED with Audible Alarm (Beeping) then it means this condition for the On-Battery LED can indicate 1of 2 problems: They are:
1. The UPS is on battery backup and an intermittent audible alarm is on. The UPS will begin shutdown procedure.
2. Battery is low. The UPS will sta rt shut down. The buzzer sounds an audible alarm .
if you see a Solid Red on your UPS , then it means that UPS is either fault or overload.  It happens if there is a issue with UPS. The LED will be lit continuously and the unit will sound an audiable alarm for 10 seconds. Other cause could be with Battery is weak or Bad, the Battery needs to be replaced under this condition.
If you use a Flashing Red LED, then it means that battery is trying to give more power than it should. It happens then UPS is overloaded.
Let me tell you,,,,
Only data sensitive equipment such as a computer, monitor and external drive should be plugged into these outlets. Battery power is automatically
provided in case of a power outage. Power (AC or battery) is not supplied to these outlets when the UPS is switched off. (Do not plug surge protectors or power strips into the battery back up outlets).
 Most Important factor that effects the issue is that,
Caution: Never connect a laser printer or scanner to the backup outlets of UPS with other computer equipment. A laser printer or scanner draws significantly more power when in use than when idle. This may overload the UPS.
And caused the UPS to shutdown whenever there is Power Surge
To isolate the issue further, let me tell you the way where you can test the UPS if it is fine or not.
1. Charge the UPS for around 4 hours, and try below steps.
To Conduct a Self Test
Use the self-test to verify both the operation of the UPS and the condition of the battery. In normal utility power, push the On/Off/Test
button less than 2 seconds and the UPS performs a self-test function. During the self-test, the UPS operates in back-up mode.
Note! During the self-test, the UPS briefly operates on- battery backup power (the on-battery LED comes on). If the UPS passes
the self -test, it returns to on-line operation. If the UPS fails the self-test, it immediately returns to on-line operation and lights the replace battery LED. The loads are not affected. Recharge the battery overnight and perform the self- test again. If the replace battery LED is still on, the battery will need to replaced.
This should resolve the issue for you.
 If you need any further assistance on the issue, you can mail me at thumuvikram@rediffmail.com . I'll be glad to help you.
Bye.
Oct 28, 2007 | Belkin (F6C800-UNV-PL) UPS System
Powerware 9330 40 (A40401110031112) UPS System Logo
Top Powerware Computers & Internet Experts
Marvin
Marvin
geekyshrink
geekyshrink
Level 1 Expert
B.Th. Pluijm
B.Th. Pluijm
Are you a Powerware Computer and Internet Expert? Answer questions, earn points and help others