You'll need a manometer to check inlet and outlet gas pressure to confirm the valve is opening upon receiving voltage. Since you have replaced everything else you're likely to find that even though the 24V is present at the valve and the inlet pressure is fine you are not getting any manifold pressure - the valve is bad.
John
PROBLEM #1 - HOT SURFACE IGNITOR DOES NOT GLOW RED
(Remember to wait for purge time, 17/34 seconds, on models so equipped).
Possible causes
A. No main power
B. Faulty transformer
C. Faulty thermostat
D. Faulty limit switch
E. Faulty blower interlock switch
F. Faulty hot surface ignitor
G. Faulty ignition control
Solution
Step #1
Perform normal system checks of main power, transformer, thermostat, limit
switch, blower interlock switch, and replace faulty component.
Step #2
With power on and thermostat set at its highest position, check voltage
between "TH" and "TR" on HS780 ignition control. If 24 volts is not present
check output at transformer. If no, replace transformer. If transformer
checks out OK look at other controls in the 24 volt circuit I.E.: thermostat,
limit switch, blower interlock switch. Check for 120 volts between "neut"
(L2) and "120" (L1). Check for 120 volts at the ignitor across "IGN" and
"IGN" terminals on the HS780 ignition module. If 120 volts is present,
replace ignitor. If no, replace the 780 series module
PROBLEM #2 - IGNITOR GLOWS RED BUT MAIN BURNER
WOULDN'T LIGHT
Possible causes
A. Improper ignitor alignment
B. Faulty ignition control
C. Faulty gas valve
D. High inlet gas pressure
E. Polarity reversed
F. No earth ground
Solution
Step #1
Check for availability of gas at gas valve. Make sure the manual valve
upstream of the gas valve and the gas valve are in the full on position. Also
make sure gas is being supplied to the system at the proper pressure, too
high will lock-up the valve.
Step #2
Check proper polarity of "NEUT" and "120" on the ignition control by reversing
the wires, if reversed gas valve will not open. If this does not solve the
problem, replace wires as they were.
Step #3
Check for proper ignitor position.
Step #4
Check for a good earth ground by using a meter connected between L1
and furnace chassis. Should read 120 volts, if no, check and/or repair ignition
ground wire or ignition control mounting screws.
CAUTION POLARITY MUST BE OBSERVED
Step #5
Check for 24 volts at the gas valve terminals; "1" and "2" on a 7200 series,
"M" and "C" on a 7100 series, "TH" and "TR" on a 7000 series. If yes,
check wire integrity or change the gas valve. If no, change the 780 series
ignition module.
That is pretty much all of the troubleshooting required.
Thanks for choosing FixYa,
Kelly
The
oven control supplies voltage to the oven igniter/gas valve circuit. When the
oven control is set to Bake, voltage is supplied to the oven igniter which
should glow bright red to almost white hot. Once the igniter comes on and
begins to glow it must pull enough current to cause the gas valve to open so
the burner can ignite from the igniter. I added an image below with the theory
of operation. Click this link:--http://media.fotki.com/1_p,swbbsqrsgstsqkkxgtqsskgwtqkq,vi/wrgtsbrktxwdfwfbgdg/1/1303472/5961857/image5576034710104836299img-or.png
----Open
the broiler drawer and then set the oven control to bake and watch to see if
the glow bar igniter glows or not. If it does not glow, the failure could be a
broken Igniter, failed oven control board or gas valve. If the igniter is
glowing red, then it can be possible that gas valve is faulty. To see how
igniter looks. See the fig below:--
To order this part click the link below:--
http://www.repairclinic.com/PartDetail/Hot-Surface-Glow-Bar-Igniter/1990?modelNumber=911.30469894
Also to confirm, check to see if the igniter is getting 120 volts
when it's turned on. If it gets 120 volts, then your safety gas valve is bad
because it's not letting the neutral go through. Otherwise, if it's NOT getting
120 volts, your control board shorted out and you need a new control board.
But as you mentioned that control board is replaced. So igniter should get 120 volts.
If valve is faulty. But if igniter is not glowing then its faulty igniter
confirmed.
To see how gas valve looks,
please click the link below:---
http://www.repairclinic.com/PartDetail/Gas-Safety-Valve-Assembly/251898
In most of the cases the igniter is faulty, because gas
valve getting faulty is very rare. But still getting the voltages checked, will
confirm. These will help. Thanks. Helpmech.