Hi, you shouldn't smell any gas until the pilot flame is etablished. The sequence of operation is the small inducer motor will start on a call for heat, Then on the motor you should have a poly type tube, clear, that runs over to a pressure switch. It is a round silver part that the hose connects to, The pressure from motor closes a set of contacts and you will hear a click. This is telling the electronic ignition to start to spark and light the pilot or hot surface ignitor, which ever you have. If you have no spark and the pressure switch is closed, you have a faulty ignitor board or module. To check the switch, it will have 2 wires going to it. Just take a piece of insulated wire and touch across the 2 terminals. It should fire up. If not, the module or board, ignitor has failed. You will need to take all of the numbers from it amd go to a appliance parts house to get a new one. Don't forget how it wires back in, or you will have more problems.
Sincerely,
Shastalaker7
A/C, Heating Contractor
Ok so here is a sequence of the heater lighting and the solution for your problem...
1. Thermostat calls for heat.
2. Draft inducer motor starts.
3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes.
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas.
Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning. Please see the pictures below to help you identify a flame sensor.
Thanks and I hope this helps. Feedback apprec.
gas.
Solution: You
inspect your ignitor closely for cracks. Make sure
problem or a limit, rollout switch problem. The furnace's