Anonymous Posted on Jul 27, 2010

It seems as if the unit makes the room warmer. Is this normal?

1 Answer

Anonymous

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • LG Master 43,501 Answers
  • Posted on Jul 27, 2010
Anonymous
LG Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Nov 12, 2009
Answers
43501
Questions
0
Helped
10843845
Points
101584

Hi,
Yes the heat is a byproduct of the compressor running....there will be a slight overall heat gain...this is very normal and nothing to be concerned about....the dehumidifier passes the air over a cold coil to pull out the moisture but also discharges the heat into the room...so... the net result is heat gain in the amount of electrical energy the dehumidifier is using...

heatman101

Testimonial: "Thanks. The information was very helpful! "

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

I have a 30-pint KUL dehumidifier that works GREAT and is fairly quiet. My question is: the air that flows from the vent is lukewarm at best and sometimes warmer than that. If the a/c is on, this affe

A/C removes the heat found in the air and so gives out slightly warf flows but normally this is cooled of by water but that is why air con home units are vented to the outside atmos
tip

Dehumidifier is Freezing up and not working

If you are having problems with your dehumidifier freezing up them here are a few things that you can check and also a few things that may help you.

First check the ambient temperature of the room at the level of the dehumidifier. If it is below 65 degrees and you do not have a special low temperature dehumidifier then you are asking for trouble. Most units are only designed to work in temperature 65 or higher and will freeze if they are working at lower temperatures. Some even will not work well below 68 degrees F.

Many dehumidifiers will shut off when the coil starts to freeze to let them thaw, then they will restart when the coil is warm enough again. This can take an hour or so. Some will not shut down the compressor and when the dehumidifier coil starts to freeze it reduces the air flow and only compounds the problem.

Check the air flow over the coil. If the coil becomes dirty or the fan motor stops or even slows down a bit, you will get freezing. The dehumidifier is very dependent upon the proper amount of air going over the coil to keep the coil warm enough to not freeze. Any restriction will cause problems.

The final and worst thing that can happen is for your dehumidification unit is to develop a slight leak in the refrigeration system. This will cause the coils to run even colder then they would normally and this will create the same problems. If everything else check out then you may have to have the refrigeration system checked by a professional. The problem with this is that many of these units only cost a few hundred dollars and a service call can soon add up to more then the unit is worth.

Some things that you can do to help out a dehumidifier that is freezing up are:

Raise the temperature of the room and provide a bit of heat for the room as the dehumidifier is actually a very small A/C unit.
Raise the dehumidifier up off of the floor… the air is usually warmer when you go higher up in the room, hot air rises.
Clean the coils off so that the air can flow through them easier and keep them warmer.
Make sure that the fan motor bearings are oiled and that the fan is running freely. Even a tiny bit of resistance will slow the fan enough to make a difference.


By checking all these things out and making some small changes you maybe able to make your dehumidifier work much more effectively.

http://www.fixya.com/support/r3877515-dehumidifier_problems_dehumidifier

http://www.fixya.com/support/r4662409-dehumidifier_running_but_no_water_in

http://www.fixya.com/support/r4688381-dehumidifier_problem_shows_bucket_full
on Apr 30, 2010 • Dehumidifiers
0helpful
1answer

Coil_Freezes_Up on a model DDR4507EE danby dehumidifier

If the unit runs normally and the coils are just icing up, then that probably means the unit itself is actually working well, but you probably just have the settings turned up too high for the conditions.



Try turning down the setting on the unit so that it cycles on and off every few hours and does not run continuously.



Also try using some warm soapy water to clean off any dust or oily residue from the cooling coils in the rear of the unit. Remember to also clean the air intake filter while you are at it.



The ambient temperature in the room may also be a bit too low, so you can try adding some heat to the room if necessary. A dehumidifier will not work properly if the ambient air temperature is too low. Basically, the warmer and more humid the room is, the better they work. Since warm air rises, you can even try lifting the unit higher up off the cold floor onto a bench or table where the air is warmer.



You can click on the following link for a general operating and troubleshooting guide with additional tips on effective dehumidifier operation:


http://www.allergyconsumerreview.com/dehumidifier-advice-troubleshooting.html



I hope that was helpful to you, good luck and take care.




Joe.
0helpful
1answer

It runs but doesn't pick up moisture. The bucket is always empty.

If the machine's compressor runs when you switch it on, then turn the machine on maximum and let it run for an hour or so. Then check the coils in the back with your hand. If they are not getting cold at all, then there is a significant problem with the refrigeration process in the unit. It may have developed a leak and allowed your refrigerant gas to escape, or there may be another internal problem with the compressor. Either way you would need to have it serviced by a fridge technician, or more likely just replaced with a whole new unit since both options can potentially cost about the same.

If the unit runs normally and the coils are getting cold, then make sure they are not totally icing up which will impede the unit's performance. If your dehumidifier is freezing up then that probably means the unit itself is actually working well. The humidity level in the room may be relatively low and you probably have the unit turned up too high for the conditions.

Try turning down the setting on the unit so that it cycles on and off every few hours and does not run continuously.

Also try using some warm soapy water to clean off any dust or oily residue from the cooling coils in the rear of the unit. Remember to also clean the air intake filter while you are at it.

The ambient temperature in the room may also be a bit too low, so you can try adding some heat to the room if necessary. A dehumidifier will not work properly if the ambient air temperature is too low. Basically, the warmer and more humid the room is, the better they work. Since warm air rises, you can even try lifting the unit higher up off the cold floor onto a bench or table where the air is warmer.

Sometimes the drain tube leading to the bucket is clogged. You can often clean this out by inserting the pointy end of a long heavy duty plastic zip tie and jiggling it around a bit. Do not insert anything metal or sharp into the tube or you may damage it.

You can click on the following link for a general operating and troubleshooting guide with additional tips on effective dehumidifier operation:

http://www.allergyconsumerreview.com/dehumidifier-advice-troubleshooting.html
?
And here is a link to a tip from another Expert (Heatman101) which includes his very detailed troubleshooting guide for dehumidifiers:

http://www.fixya.com/support/r4662409-dehumidifier_running_but_no_water_in

I hope that was helpful to you, good luck.

If you choose to rate this solution using the Thumbs Up scale provided, I thank you very much for your time and consideration.

Joe.
0helpful
1answer

HUMIDIFIER SET FOR 35% NO CONDENSATE SEEMS TO BE RUNNING

If the machine's compressor runs when you switch it on, then turn the machine on maximum and let it run for an hour or so. Then check the coils in the back with your hand. If they are not getting cold at all, then there is a significant problem with the refrigeration process in the unit. It may have developed a leak and allowed your refrigerant gas to escape, or there may be another internal problem with the compressor. Either way you would need to have it serviced by a fridge technician, or more likely just replaced with a whole new unit since both options can potentially cost about the same.

If the unit runs normally and the coils are getting cold, then make sure they are not totally icing up which will impede the unit's performance. If your dehumidifier is freezing up then that probably means the unit itself is actually working well. The humidity level in the room may be relatively low and you probably have the unit turned up too high for the conditions.

Try turning down the setting on the unit so that it cycles on and off every few hours and does not run continuously.

Also try using some warm soapy water to clean off any dust or oily residue from the cooling coils in the rear of the unit. Remember to also clean the air intake filter while you are at it.

The ambient temperature in the room may also be a bit too low, so you can try adding some heat to the room if necessary. A dehumidifier will not work properly if the ambient air temperature is too low. Basically, the warmer and more humid the room is, the better they work. Since warm air rises, you can even try lifting the unit higher up off the cold floor onto a bench or table where the air is warmer.

You can click on the following link for a general operating and troubleshooting guide with additional tips on effective dehumidifier operation:

http://www.allergyconsumerreview.com/dehumidifier-advice-troubleshooting.html
?
And here is a link to a tip from another Expert (Heatman101) which includes his very detailed troubleshooting guide for dehumidifiers:

http://www.fixya.com/support/r4662409-dehumidifier_running_but_no_water_in

I hope that was helpful to you, good luck.

If you choose to rate this solution and Heatman101's tip using the Thumbs Up scale provided, I thank you very much for your time and consideration.

Joe.
1helpful
1answer

Our humidifier seems to be broken. Its fan will run constantly, but it is not pulling any moisture in to the bucket. I cleaned the filter and restarted, but is still not working.

If the machine's compressor runs when you switch it on, then turn the machine on maximum and let it run for an hour or so. Then check the coils in the back with your hand. If they are not getting cold at all, then there is a significant problem with the refrigeration process in the unit. It may have developed a leak and allowed your refrigerant gas to escape, or there may be another internal problem with the compressor. Either way you would need to have it serviced by a fridge technician, or more likely just replaced with a whole new unit since both options can potentially cost about the same.

If the unit runs normally and the coils are getting cold, then make sure they are not totally icing up which will impede the unit's performance. If your dehumidifier is freezing up then that probably means the unit itself is actually working well. The humidity level in the room may be relatively low and you probably have the unit turned up too high for the conditions.

Try turning down the setting on the unit so that it cycles on and off every few hours and does not run continuously.

Also try using some warm soapy water to clean off any dust or oily residue from the cooling coils in the rear of the unit. Remember to also clean the air intake filter while you are at it.

The ambient temperature in the room may also be a bit too low, so you can try adding some heat to the room if necessary. A dehumidifier will not work properly if the ambient air temperature is too low. Basically, the warmer and more humid the room is, the better they work.Since warm air rises, you can even try lifting the unit higher up off the cold floor onto a bench or table where the air is warmer.

You can click on the following link for a general operating and troubleshooting guide with additional tips on effective dehumidifier operation:

http://www.allergyconsumerreview.com/dehumidifier-advice-troubleshooting.html
?
And here is a link to a tip from another Expert (Heatman101) which includes his very detailed troubleshooting guide for dehumidifiers:

http://www.fixya.com/support/r4662409-dehumidifier_running_but_no_water_in

I hope that was helpful to you, good luck.

If you choose to rate this solution using the Thumbs Up scale provided, I thank you very much for your time and consideration.

Joe.
0helpful
1answer

Dehumidifier won't fill up with water and makes

If the machine's compressor runs when you switch it on, then turn the machine on maximum and let it run for an hour or so. Then check the coils in the back with your hand. If they are not getting cold at all, then there is a significant problem with the refrigeration process in the unit. It may have developed a leak and allowed your refrigerant gas to escape, or there may be another internal problem with the compressor. Either way you would need to have it serviced by a fridge technician, or more likely just replaced with a whole new unit since both options can potentially cost about the same.

If the unit runs normally and the coils are getting cold, then make sure they are not totally icing up which will impede the unit's performance. If your dehumidifier is freezing up then that probably means the unit itself is actually working well. The temperature or humidity level in the room may be a bit low and you may have the unit turned up too high for the conditions.

Try turning down the setting on the unit so that it cycles on and off every few hours and does not run continuously.

Also try using some warm soapy water to clean off any dust or oily residue from the cooling coils in the rear of the unit. Remember to also clean the air intake filter while you are at it.

If the ambient temperature in the room is a bit low, you can try adding some heat to the room if necessary. A dehumidifier will not work properly if the ambient air temperature is too low. Generally, the warmer and more humid the room is, the better they work.Since warm air rises, you can even try lifting the unit higher up off the cold floor onto a bench or table where the air is warmer.

You can click on the following link for a general operating and troubleshooting guide with additional tips on effective dehumidifier operation:

http://www.allergyconsumerreview.com/dehumidifier-advice-troubleshooting.html
The rattling noise may just be the coils vibrating against each other. Sometimes you can gently bend the coils apart slightly so they don't rattle, just dont bend them too much or you might damage them.

I hope that was helpful to you, good luck.

If you choose to rate this solution using the Thumbs Up scale provided, I thank you very much for your time and consideration.

Joe.
1helpful
1answer

Units is running but there is not any water being collected?

If the machine's compressor runs when you switch it on, then turn the machine on maximum and let it run for an hour or so. Then check the coils in the back with your hand. If they are not getting cold at all, then there is a significant problem with the refrigeration process in the unit. It may have developed a leak and allowed your refrigerant gas to escape, or there may be another internal problem with the compressor. Either way you would need to have it serviced by a fridge technician, or more likely just replaced with a whole new unit since both options can potentially cost about the same.

If the unit runs normally and the coils are getting cold, then make sure they are not totally icing up which will impede the unit's performance.
If your dehumidifier is freezing up then that probably means it is actually working well. The humidity level in the room is probably just relatively low and you probably have the unit turned up too high for the conditions.

Try turning down the setting on the unit so that it cycles on and off every few hours and does not run continuously.

Also try using some warm soapy water to clean off any dust or oily residue from the cooling coils in the rear of the unit.

The ambient temperature in the room may also be a bit too low, so you can try adding some heat to the room if necessary. A dehumidifier will not work properly if the ambient air temperature is too low. Basically, the warmer and more humid the room is, the better they work.Since warm air rises, you can even try lifting the unit higher up off the cold floor onto a bench or table where the air is warmer.

You can click on the following link for a general operating and troubleshooting guide with additional tips on effective dehumidifier operation:

http://www.allergyconsumerreview.com/dehumidifier-advice-troubleshooting.html

Hope that was helpful. Thank you very much and good luck.


Joe.
6helpful
1answer

Goldstar Dehumidiflier coil freezes

Hi, If you are having problems with your dehumidifier freezing up them here are a few things that you can check and also a few things that may help you.

First check the ambient temperature of the room at the level of the dehumidifier. If it is below 65 degreesand you do not have a special low temperature dehumidifier then you are asking for trouble. Most units are only designed to work in temperature 65 or higher and will freeze if they are working at lower temperatures. Some even will not work well below 68 degrees F.

Many dehumidifiers will shut off when the coil starts to freeze to let them thaw, then they will restart when the coil is warm enough again. This can take an hour or so. Some will not shut down the compressor and when the dehumidifier coil starts to freeze it reduces the air flow and only compounds the problem.

Check the air flow over the coil. If the coil becomes dirty or the fan motor stops or even slows down a bit, you will get freezing. The dehumidifier is very dependent upon the proper amount of air going over the coil to keep the coil warm enough to not freeze. Any restriction will cause problems.

The final and worst thing that can happen is for your dehumidification unit is to develop a slight leak in therefrigeration system. This will cause the coils to run even colder then they would normally and this will create the same problems. If everything else check out then you may have to have the refrigeration system checked by a professional. The problem with this is that many of these units only cost a few hundred dollars and a service call can soon add up to more then the unit is worth.

Some things that you can do to help out a dehumidifier that is freezing up are:

Raise the temperature of the room and provide a bit of heat for the room as the dehumidifier is actually a very small A/C unit.
Raise the dehumidifier up off of the floor… the air is usually warmer when you go higher up in the room, hot air rises.
Clean the coils off so that the air can flow through them easier and keep them warmer.
Make sure that the fan motor bearings are oiled and that the fan is running freely. Even a tiny bit of resistance will slow the fan enough to make a difference.


By checking all these things out and making some small changes you maybe able to make yourdehumidifier work much more effectively.
2helpful
1answer

Danby Dehumidifier Model # DDR557HE Serial # 0107030704369 --Does not collect water and cxontinues to frost up

Hi,
If you are having problems with your dehumidifier freezing up them here are a few things that you can check and also a few things that may help you.

First check the ambient temperature of the room at the level of the dehumidifier. If it is below 65 degrees and you do not have a special low temperature dehumidifier then you are asking for trouble. Most units are only designed to work in temperature 65 or higher and will freeze if they are working at lower temperatures. Some even will not work well below 68 degrees F.

Many dehumidifiers will shut off when the coil starts to freeze to let them thaw, then they will restart when the coil is warm enough again. This can take an hour or so. Some will not shut down the compressor and when the dehumidifier coil starts to freeze it reduces the air flow and only compounds the problem.

Check the air flow over the coil. If the coil becomes dirty or the fan motor stops or even slows down a bit, you will get freezing. The dehumidifier is very dependent upon the proper amount of air going over the coil to keep the coil warm enough to not freeze. Any restriction will cause problems.

The final and worst thing that can happen is for your dehumidification unit is to develop a slight leak in the refrigeration system. This will cause the coils to run even colder then they would normally and this will create the same problems. If everything else check out then you may have to have the refrigeration system checked by a professional. The problem with this is that many of these units only cost a few hundred dollars and a service call can soon add up to more then the unit is worth.

Some things that you can do to help out a dehumidifier that is freezing up are:

Raise the temperature of the room and provide a bit of heat for the room as the dehumidifier is actually a very small A/C unit.
Raise the dehumidifier up off of the floor… the air is usually warmer when you go higher up in the room, hot air rises.
Clean the coils off so that the air can flow through them easier and keep them warmer.
Make sure that the fan motor bearings are oiled and that the fan is running freely. Even a tiny bit of resistance will slow the fan enough to make a difference.


By checking all these things out and making some small changes you maybe able to make your dehumidifier work much more effectively.

Take care
Not finding what you are looking for?

147 views

Ask a Question

Usually answered in minutes!

Top LG Dehumidifiers Experts

Cindy Wells

Level 3 Expert

6688 Answers

ZJ Limited
ZJ Limited

Level 3 Expert

17989 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a LG Dehumidifier Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...