Question about Nor-Lake Norlake Refrigeration 4' x 6' Kold Locker Walk-In Cooler - 6' 7'' High w/Floor
Walk in cooler cycleing
Went to start a walk-in cooler after years of down time. The compressor will run for about 10 seconds then shut off for about 30 seconds then run for another 10 & shut off for another 30. Any ideas?
  • Nor-Lake Master
  • 43,501 Answers
It has lost some freon and is not charged correctly...the unit is pumping down and shutting off on low pressure and then after being off a bit the pressure comes up and it restarts...
Need to check the charge and top it off and you will be good to go..
heatman101
Posted on May 28, 2010
Testimonial: "Thanx for the good advice."
    New Friend:
This walk in cooler was short cycling. runs 10 sec, then shuts off for 15 sec. Was low on freon. Problem was in evaporator coil. All U-bends started to leak, copper corrosion. I end up replacing fan coil. I hope that's was helpful.
Posted on Dec 16, 2018
    Director Badge:
    Uploaded 100 video answers.
  • Nor-Lake Master
  • 489 Answers
most likely that walk-in cooler is low on refrigerant (freon). I made video with the same issue. This refrigerator has small leak, i tried to find leak with soap bubbles, but no luck, so end up charging it with freon and add leak dye, so next time I can find that leak for sure.
Posted on Mar 13, 2016
SOURCE:
External unit on my walk-in cooler will not shut off. Seems to be due to the Ranco Pressure Sensor. How do I fix or adjust?
Diagnosing Walk-in Coolers & Freezers Problems
blog.uscooler.com/walk-in-cooler-freezer-problems/
Jun 7, 2013 - Diagnose Walk-in Cooler & Freezer Refrigeration Problems ... For many evaporator units, the ice isn't melted, or the water isn't .... It works for few days (2-3 days) and it stop and does not run until I shut off the power .... My walk in compressor seems to be running and not shutting off. .... outdoor ambient= 85
Maintaining & Cleaning Your Walk-in Cooler or Freezer
blog.uscooler.com/maintain-walk-in-cooler-freezer/
Jan 7, 2015 - Torn gaskets can let warm air infiltrate your walk-in cooler or freezer. Close the door when not in use. Do not block or prop the door open for extended periods of time. ... on suction lines between the condensing unit and evaporator coil. ... Make sure the lights are off when exiting the walk-in. ... clean walkin ...
[PDF]INSTALLATION & SERVICE MANUAL - Polar Leasing
Dec 10, 2015 | Refrigerators
I work for a schools district and a problem with our walk in. cooler is our condenser fan wasnt workin, dirty condenser coil. After I fixed those problems, my compressor is coming off on low pressure. It...
@50/300 I assume it's a med. temp R-22 pump down walk in. Head pressure sounds a little high, probably been overcharged to compensate for a restriction in the metering device (or malfunctioning TXV). Check the solenoid (if pump down), metering device, and filter driers first. If that fails, lineset restriction or non-condensables/water in the charge would be next on my list.
Sep 29, 2011 | Heating & Cooling
Refrigerator wont run. Clicking noise coming from main board preceded by a short humming noise every several seconds. Unplug for 30 minutes then plug back in and compressor starts up after several clicks...
That condenser fan motor needs to be replaced. You and doing the right thing as far as using a seperate fan to keep compressor cool,buy replacing the fan the compressor will run cooler and click off by being too hot as you have heard/seen.
Find your model number and call your local appliance parts store and see if they have a CONDERSER FAN MOTOR in stock
Gene
Aug 15, 2011 | Refrigerators
Freezer motor cuts in and out. Runs for about thirty seconds at a time. Now have red low temp light on and everything is defrosting. Sides of freezer used to be very warm and are now cold.
Good day,
Some kind of compressor problem. If it will run a true 30 seconds then it is either the start relay mounted on the side of the compressor hanging up and not releasing after the compressor starts or the main windings in the compressor are starting to short, causing the compressor to draw too much current followed by the protective overload shutting the compressor down.
The relay is pressed onto the compressor pins and can be removed.
A parts house should be able to test it for you. If bad, replace. If it tests good then the problem is internal to the compressor and would need the attention of a qualified tech.
P.S. If the unit is under 5 years of age, leave it alone and call for factory service. It may or may not be covered but if so it would be necessary to preserve the balance of the 5 year warranty.
Apr 27, 2010 | Frigidaire 20.3 Cu. Ft. Frost-Free Upright...
Goodman GSC130361DE premature shut off
im not sure what tstat you have? if you still have your tstat book it well tell you how to set it up. may be it was not programed when installed. i hope that helps
Apr 06, 2010 | Goodman CLQ30AR32 Air Conditioner
Craftsman 6hp 150psi 30gal won't keep running
It sounds like the internal circuit breaker in the motor is heating up and then the breaker trips to shut down the motor. This is the protection so you don't have a fire if the motor burns up. The smell you have is the coils in the motor. Sorry to say that you will need a new motor for this unit. I hope this helps out.
Jan 17, 2009 | Air Tools & Compressors
Kenmore
when its running how hot are the sides the starting amps are too high and 1.5 running amps ain't bad now the the cut in cut out are too high if you look on the dial that the mid point settings that's where you should have it not on 1 1 is hot set it on the straight line that's where you should do all your testing colder settings go up not down you could be overheating the compressor by making it come on too quick the freezer should be about -10 or so do you see any gaps in the gasket
Mar 31, 2008 | Kenmore 13.7 cu. ft. / 388 liter Upright...
Walkin cooler
Most Likely Low on Freon. Low Pressure switch shuts That Compressor Off.
Dec 29, 2007 | Refrigerators
Non stop compressor?
these units have a condensor cooling fan in the rear it appears that yours may be seized up.
Regards
Advisor
Nov 10, 2007 | Danby DWC283BLS Wine Cooler
Refrigerators Logo
274 people viewed this question
Top Nor-Lake Refrigerators Experts
Marvin
Marvin
Marat Brikov
Are you a Nor-Lake Refrigerator Expert? Answer questions, earn points and help others