My son has condensate building up in his flue and running down into the furnace. It is a 2 stage furnace. The contractor who installed it blames it on the chimney. Is that likely?

  • Anonymous Mar 30, 2014

    flue kit head will not fit into chimney head

×

1 Answer

Paul

Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Novelist:

An expert who has written 50 answers of more than 400 characters.

Governor:

An expert whose answer got voted for 20 times.

  • Expert 144 Answers
  • Posted on May 13, 2010
Paul
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Novelist:

An expert who has written 50 answers of more than 400 characters.

Governor:

An expert whose answer got voted for 20 times.

Joined: Mar 30, 2010
Answers
144
Questions
0
Helped
90890
Points
313

It is for sure a venting issue, depending on where you are located, it sounds like the local building code inspector was not involved for an inspecton of the furnace replacement. When the flue condensates like that, it is usually because the flue is the wrong size, usually to big,or it is dumped directly into a masonary chimney, and the chimney was not lined to the top.
I hope this answers your questions, please rate me and let me know if I can help further.
Sicerely,
Paul Gibson

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
2answers

What can be done about a contractor that installed the wrong size flue liner down your chimney to your hot water tank

Did you have a city permit for the work? Did you have a written contract with the contractor? If the answers are no, you will most likely have to just get another contractor to install a proper flue. If you had a permit and written contract, call the contractor and tell them their work was incorrect and they will need to install the proper flue size. If they say no. You can always file a small claims court against them to pay for the fix.
tip

2 Stage Furnaces More Comfort and Save Money

Two stage hot air furnaces can save you money and make your high efficiency furnace even better. With your furnace running at low fire instead of cranking up to the highest heating output in mild weather you can be more comfortable while saving money.

Many people think that they are getting the best they can get by buying a high efficiency single stage furnace. What they often don’t realize is that they could do better yet and for a few dollars more have a high efficiency 2 stage furnace that could keep them much more comfortable.


There are 2 stage hot air furnaces that are now available that will only run at half fire if the full fire is not needed. With a two stage furnace in mild weather when only a little bit of heat is needed, the furnace will have longer run times on low fire. This will keep you room temperatures from getting too hot before the thermostat reacts and shuts the furnace off again. This will help to keep your temperatures from overshooting the set point and help to keep your home much more comfortable.

Many of these two stage furnaces also have variable speed blowers that run at a lower speed when heating on low fire. This will also help to save money on your electric bill, because these blowers use very little electric when running at these low speeds. Air noise from the blower running at a high speed is also reduced.

If you are thinking of replacing or installing a hot air furnace, make sure that you ask your contractor to give you a price on installing a two stage furnace. The price difference probably will not be much higher than a high efficiency single stage furnace. However the comfort of the two stage furnace coupled with the electric savings will make the extra money well worth it.

on Dec 14, 2009 • Heating & Cooling
0helpful
1answer

Furnace has water under it, why? Its a Dayton gas furnace.

There are several questions that need to be answered about what type of system you have, but i found this posting that may help:
As your gas furnace runs, is there water leaking at the base? Is the furnace's air filter wet, too?There are a few things that could be happening here. But if you have a high-efficiency furnace, here's the most common cause: a condensation leak.
We'll explain why a furnace creates condensation, and what's causing it to leak out of your furnace.
Note: You'll know if you have a high-efficiency furnace if:
  • The yellow energy guide tag says your furnace's efficiency is 90% or higher AFUE.
  • The vent/flue pipe is white PVC as opposed to metal.
Why a high-efficiency furnace creates condensation
How in the heck does a high efficiency furnace create condensation/water anyway?
It's all about how the furnace extracts heat from combustion gases.
A lower-efficiency furnace extracts some heat from combustion gases and then quickly vents them out the flue pipe.
But a high-efficiency furnace, to extract more heat, has 2 heat exchangers. These allow the furnace to extract heat from the gases for a longer period of time. This causes the combustion gases to cool and then condense.
That condensation then exits out your home through a drain. But if that water is pooling around the furnace, there's a problem preventing it from draining properly.
Causes of a condensation leak around a high-efficiency furnace
  • Clogged condensation tubing
  • Clogged condensation drain
  • Breaks in the condensation line
  • Issues with the condensate pump (if you have one)
You'll need a furnace technician to diagnose which of these is the issue and then fix it.
Other causes of leaking water around a furnace
If you have a conventional, standard-efficiency furnace...then its flue pipe may be incorrectly sized.
If you have a whole-house humidifier connected to the furnace...there may be an issue which is causing the humidifier to leak into your furnace. Your humidifier should be getting annual maintenance from a professional to prevent this.
0helpful
1answer

My high efficiency furnace has water (possibly condensation) running down the air intake pvc pipe into the furnace and all over the burner, gas valve, and wiring.

First, check the drainline from the furnace. You have a 90% gas fired furnace. Where 80% furnace has 1 heat exchanger, yours has 2 heat exchangers. And the second heat exchanger will cool the exhaust enough, that it ends up below the dew point, and your furnace outlet/exhaust will condensate. This drain is probably stopped up. Now, I've installed and service many of these systems and I've only seen the piping at the roof you described once. And that was when the roofers replaced the roof, damaged the furnace flue pipe, and tried to repair it themselves. Normally, and this may not apply to yours, we tie in the exhaust/supply lines about 2-3 ft. above the furnace. Then 1 pipe goes through the roof. Thus 1 pipe is a kit that has an inner liner & outer pipe(2 pipes in 1). Now I'm not sure if this is a problem or normal for your system, but it may be worth looking into. You should be able to find it in the installation manual, or call a local parts house that sells your brand, or as your tech. And if it's just your drain, forget all about the piping I mentioned. Hope this helps!
1helpful
1answer

Just replaced pressure switch on intertherm m1mb gas furnace but still codes "pressure switch open"

CHECK FLUE FOR OBSTUCTIONS AS WELL AS COMBUSTION AIR INTAKE FIRST. THEN CHECK TO SEE IF THE FURNACE DRAIN IS OPEN AND NOT CLOGGED [ONLY IF YOUR FURNACE IS A CONDENSATING HIGH EFFICIENCY MODEL, typically the flue pipe will be 2 or 3 inch pvc pipe] over the years more often than not, it is an obstruction or poor drainage which will not prove the pressure switch to allow the burner to ignite. in rare cases the furnace control board could be bad as well.TRY DISCONNECTING FLUE AND COMB. AIR AT FURNACE JUST TO SEE IF FURNACE WILL IGNITE. HOPE THIS HELPS!!!!!!
2helpful
1answer

Colman mobile home gas furnace to use in my garage/shop

generally speaking a sealed combustion system is inherently more safe than a system that draws it's combustion air from it's ambient location. however, it cannot be considered 100% safe in a potentially hazardous location. The actual system that would be used in a "code compliant" installation would be a 100% outside air unit.
That being said, you can install this in a garage, the vent that you are referring to (if it is a standard mobile home system) is generally directly above the unit and usually no longer than about five feet. It also requires a listed and labeled termination "cap" If you install 90 degree angles or extend the vent too far you will have issues with condensation in the piping that will cause the pipe/ heat exchanger to fail prematurely.
If the system is a 90+ efficeint unit then the PVC venting is generally allowed to be about 30 feet long, with a 1/4 inch per foot pitch back to the unit for condensation, also the general mfg. instructions allow either 2- 90 degree or 4 45 degree fittings in the line. hope this helps
0helpful
2answers

I'm considering installing a Goodman LP Gas Furnace:sizing? Ops?

Gerge, if you go to website www.energycodes.gov
you can do a heat load calc yourself. Basically, you figure out the sizes of walls, total area of glass. total doors to outside, ceiling area and types of building materials used. It is pretty easy and then you will know for sure. The contractor should be suppling you with one but if not use this, it is free!
0helpful
2answers

We have a old house and the gas hot water heater and the central heating unit is vented out an old chimney and the heater is building up condinsation, how do i vent the heating unit out the wall, unstead...

actually if you vent your furnace by code, it would probably be cheaper to have a chimney liner installed up the old masonry chimney. you may be able to buy a kit and do this yourself. any time a new furnace with a draft inducer on it is installed, it must be vented into the proper flu material. if it was vented into your chimney, it may not have be installed by code for your area. you may talk to the instaled if they are still available and maybe that can return and do it correctly. if you leave this vented into your masonry chimney, the acid content of the exhaust will ruin the chimney. a liner will also get rid of the water problem you have.
3helpful
2answers

Carrier air handler tonnage?

That is a fairly large difference. It is usually ok to have the inside evap. coil and blower up to 1 ton larger than the outside condenser. That will make the unit slightly more efficient as well as less likely to freeze up on low airflow situations. It is not recommended to install a new condenser on an old evap coil. There has been a lot of changes to the design of the coils in the last little while. For example a 10 year old 2 ton coil may only have 3 cubic feet of volume but a new 2 ton coil may have 4 cubit feet of volume.

There are many factors that may have infulenced the decision on what size condenser to install. Many of which can only be done by visiting the home and doing alot of work, checking the duct sizing bioth supply and return, inspecting the insulation and windows of the home etc. etc. Most of the time that never gets done. You can blame the contractor for not doing a complete check, but at the same time you can blame the customer because many contractors that are that good loose the job to a cheaper bid that did not no any of the research. It is a catch 22 for everyone involved.

There is ALOT more to sizing equipment that many people think, sadly that also includes many HVAC contractors. Way too many people use "rule of thumbs" or flat out "guess".

Sorry for the rant but your queston can only be answered by a good well educated HVAC contractor visiting your home. That type of a contractor is getting hard to find these days in such a price competetive world.
0helpful
5answers

Ignitor glows, but no gas

Most likely either a bad board or no gas to gas valve. Bleed out all air in the gas line. Check for 24 volts at both gas valve and circuit board terminals leading to gas valve. No voltage = bad board.
Not finding what you are looking for?

136 views

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...