Aube Technologies Aube 7-Day 40-500w Light Switch Timer  Logo
Posted on Feb 14, 2010
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
GFCI circuit Breaker Trips
I tyried to connect a 2400 watt timer to control exterior outlets but when I connect it the GFCI circuit breaker trips? what am I doing wrong the neutral is connected directly to the neutral block in the panel?
Anonymous
Level 3:
  • Master 565 Answers
  • Posted on Feb 15, 2010
Anonymous
Master
Level 3:
Answers
565
Questions
0
Helped
269755
Points
1490
The neutral for that circuit must be connected under the neutral terminal connection set screw_on_ the GFCI breaker. The (usually coiled) white wire that is permanently connected to the GFCI breaker is then connected to the "neutral block in the panel."
Cookmaster101 trips electric when switched on at wall socket
The washer tripped the breakeronce andORafter the breaker was reset it ran additional loads with no problem then it tripped the breaker again.Intermittent problems are always difficult to diagnose because the problem usually doesn't occur when you're making the checks.If the washer ran additional loads the problem will not be an electrical short with one of the washer parts. If the lid switchhad a short it wouldn't runadditional loads.if the additional loads used the same cycle as previously. A timer can have an internal short that might trip the breaker in heavy duty cycle but not the permanent press cycle.If you have access to a clamp on amp meter, see the image below, then you can check the amp draw of the washer. The washer normally will draw about 10-15 amps at start up and about 5-8 amps while running. The house breaker for you washer should be rated at 20 amps.If the washer is running and drawing less than 20 amps and the breaker trips then if can be a weak house breaker.Mid cycle the washer is most likely draining or spinning and if the bearing or pump locks up then the washer may draw additional amps to try to start and trip the breaker.The key to this problem is what the amp draw of the washer is when the house breaker trips.
To narrow this problem down, there arethree placesthat could be causing the( outlet)GFCI to trip, a malfunction in the washing machine, a problem with the downstream wiring (aka load side of the GFCI-other items connected on same circuit), or the GFCI outlet itself. If there isn't anything downstream, then plugging the washing machine into another GFCI outlet, or simply swapping out the outlet for a known good GFCI outlet, will identify if the outlet itself is faulty.
If the outlet trips when the washing machine isn't running and isn't even plugged in, then there's a fault in the wiring on the load side of the GFCI outlet.
If the issue is neither of the above, then running the washing machine and monitoring to see which step is occurring when the trip happens will isolate what part of the washing machine may be leaking current to a ground. It could be a certain water level, a motor being engaged, a transition step in the controller, etc
Beware some techs believe that mostWashing machines or any other motor should not be on a GFCI! Should be a dedicated single receptacle. If there are other outlets on the washer GFCI, replace that GFCI with a single receptacle and put the GFCI on the next jump in order to protect other outlets.
Another item to check isurlid switch which may have gotten moister inside and created a short_orbroken open and the rubber sealdried out over time, and the switch assembly will be exposed. water can splash onto the assembly, somehow causing the GFCI to trip. In any event, if you are having trouble with your washing machine stopping mid-cycle for any reason,test andreplacing the lid switchis probably a worthwhile idea, as it is cheap and easy to replace.
By the way my advice is freecuzGod is good!
Hi lg washer dryer combo trips safety switch as soon as plugged in and wall turned on
The washer tripped the breaker once and OR after the breaker was reset it ran additional loads with no problem then it tripped the breaker again.
If the washer ran additional loads the problem will not be an electrical short with one of the washer parts. If the lid switch had a short it wouldn't run additional loads.
To narrow this problem down, there are three places that could be causing the ( outlet) GFCI to trip, a malfunction in the washing machine, a problem with the downstream wiring (aka load side of the GFCI-other items connected on same circuit), or the GFCI outlet itself. If there isn't anything downstream, then plugging the washing machine into another GFCI outlet, or simply swapping out the outlet for a known good GFCI outlet, will identify if the outlet itself is faulty.
Beware some techs believe that most Washing machines or any other motor should not be on a GFCI! Should be a dedicated single receptacle. If there are other outlets on the washer GFCI, replace that GFCI with a single receptacle and put the GFCI on the next jump in order to protect other outlets.
Another item to check is ur lid switch which may have gotten moister inside and created a short_ or broken open and the rubber seal dried out over time, and the switch assembly will be exposed. water can splash onto the assembly, somehow causing the GFCI to trip. In any event, if you are having trouble with your washing machine stopping mid-cycle for any reason, test and replacing the lid switchis probably a worthwhile idea, as it is cheap and easy to replace.
By the way my advice is free cuz God is good!
Admiral washer. Did load of laundry, breaker tripped, and is still full of water. Reset breaker, and hear a small click after I pull knob to restart washer. Breaker trips. No leak, and outlet is good
If the washer ran additional loads the problem will not be an electrical short with one of the washer parts. If the lid switch had a short it wouldn't run the additional loads.
You don't say if the additional loads used the same cycle as previously. A timer can have an internal short that might trip the breaker in heavy duty cycle but not the permanent press cycle.
Coleman mach rv ac unit tripping breaker
If it trips the circuit breaker as soon as you turn the FAN on, suspect either a bad fan motor or a failed fan motor start capacitor. If you are able to turn the fan on but the circuit breaker trips as soon as the COMPRESSOR starts, it is possible that the compressor is seized.
If, on the other hand, the unit is tripping a GFCI (Ground Fault Circuit Interrupter) breaker or GFCI utility outlet, it is possible that neutral and hot are reversed at the outlet into which the trailer is plugged (happened to me this year at an RV park).
When put on a wash it trips the electric
Deawoo washing machin when start spin timer will triped elecricity
The washer tripped the breaker once and after the breaker was reset it ran additional loads with no problem then it tripped the breaker again.
Ground fault keeps tripping
1helpful
I got 2 wascomat gen5 that trips breakers only on rinse cycle
20 A AFCI Homeline trips intermittenly on a outlet circuit with no lighting on it. The circuit does have an GFCI outlet on it. Trips mabe once a week. replaced the breaker and it worked fine for about a...
You should not have multiple GFCI devices in any one circuit. Change out the outlet and label it
GFCI Protected if necessary...Your problem of nuisance trips should go away.
John
2helpful
Ground Fault circuit Breaker trips each time a load is applied
The most likely causes in their order of probability are: 1) water somewhere in the circuit causing the hot wire to ground; 2) a legitimate trip caused by a defect in a device plugged into the circuit; and 3) a defective GFCI breaker. In the first case, wait until it has been dry for about a week and see if it trips. In the second case, make sure there is nothing plugged into the circuit and try resetting. In the third case go ahead and put the regular breaker in, then put a GFCI outlet into the first box downstream from the breaker. If installed according to the directions, that outlet should protect all of the outlets downstream.