You definitely want to follow the manual procedure to avoid a possible load loss:
http://powerquality.eaton.com/Products-services/Backup-Power-UPS/9390.aspx?cx=3
9.1.4 Transfer from Normal to Bypass Mode
To transfer the critical load to Bypass mode:
C A U T I O N
In Bypass mode, the critical load is not protected from commercial power interruptions and abnormalities.
1. Press the CONTROLS pushbutton on the main menu bar. The System Controls
screen appears.
2. Press the BYPASS pushbutton on the System Controls menu bar.
The UPS transfers to Bypass mode and the critical load is immediately supplied
by the bypass source. If the bypass source is not available, the power processor
remains on and an alarm sounds.
3. The UPS is now operating in Bypass mode and the BYPASS status indicator is
illuminated.
The power module (PM) status indicates READY. The system is now on bypass
and the UPS power processor remains on.
At this point, you can operate an external bypass switch to get to maintenance bypass if needed.
If u have 80kva or 40KVA EATON 9390 then it's too easy to get ups into manual bypass because there is an dedicated manual bypass switch so u just have to turn input switchgear and output switchgear offf and at last turn on the manual bypass on
or u need any kind of information related EATON UPS SYSTEMS then u can contact me on my WhatsApp number +919871039174
eaton powerware online ups system model 9390 -80kva
Manual bypassing is almost similar to you are connecting main power directly. This mode setting changes depends up on the model of your ups. kindly provide the model