I have a compool 3400 system. The system has an error 4 code. I discovered that there is a red light fault on the air blower. Any help on how to proceed?

I have a compool 3400 system. The system has an error 4 code. I discovered that there is a red light fault on the air blower. I opened and connected the remote panel directly to the main panel board and the err code 4 was still present. So I put everything back to what it was and the system worked until the pump cut off and the again the error code 4 appeared on the remote panel along with the red fault light on the air blower. Any help appreciated!

1 Answer

Kenneth Simmons

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Master 1,239 Answers
  • Posted on Nov 02, 2019
Kenneth Simmons
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Oct 31, 2010
Answers
1239
Questions
1
Helped
752954
Points
4061

Manual has troubleshooting and system options info
below. It has info of how to reset the control panel and power center..
May help
https://www.manualslib.com/manual/967826/Compool-Cp3400.html?page=41#manual
Another version of the manual below
http://www.poolinspections.com/manuals/controls/compool_cp3400.pdf

Only other think I can think of has any work been done or something go on which could have damaged the communication cable. May want to look at cable and end connections.

Testimonial: "Hi Kenneth, Thanks for the information. No repairs were done on the unit but the system suddenly went dead after a thunderstorm. I disconnected the communication cable between the power panel and the remote pane and tested communications between the two panels using he test communication cable. No change, the fault is still present on the air blower. Then put everything back with the original communication cable to the remote and reset the power panel and the remote panel. The system worked properly. When the timer cycle for the pool pump was complete and the pump shut off, the fault appeared again. Again reset the power and the remote panels. Still getting an error 4 and a fault on the air blower."

5 Related Answers

Anonymous

  • 86 Answers
  • Posted on Mar 15, 2008

SOURCE: Fujitsu ASU9RLQ

check indoor unit sirkit board

Ad

Anonymous

  • 1665 Answers
  • Posted on Jul 04, 2008

SOURCE: Ice and Water not dispensing. Light button not working

http://www.repairclinic.com/0100_1.asp
There's an ice- or water-dispensing problem The ice and water-dispensing system of your refrigerator is quite complex. Many components work together to provide the ice and water. Aside from a simple problem of a leaky water tube or a jammed ice chute, most other components are not user serviceable. We suggest that you contact a qualified appliance repair technician for such repairs.

John Riley

  • 441 Answers
  • Posted on Jul 10, 2009

SOURCE: Fault Code 37 Intuitive Washer -

you have a clogged diverter valve, its blue and looks like a Y, it will need to be replaced, if you want call 1-888-936-7872 they can order the part and walk you thru replacing it

Jonah Oneal

  • 14092 Answers
  • Posted on Aug 30, 2009

SOURCE: Help with toyota corolla 2003 code P0420

CODE PO420 CATALTYLIC CONVERTER SYSTEM FAULT.ITS SAYING FAULTY CATALTYLIC CONVERTER.IF IT BEEN A WHILE IF YOUR CAR HAS A WHOLE LOT OF MILES ON IT.YOUR SPARK PLUG CHANGE IS DUE AT 120000 MILES. DUE A LITTLE TUNE UP CHANGE AIR FILTER AND FUEL FILTER.SEE IF YOU HAVE ANY ENGINE FAULTS BAD PLUGS DIRTY INJECTORS ANY THING UP SET FUEL SYSTEM CAUSE CAR TO RUN RICH.EXCESSIVE UNBURN FUEL WILL GATHER IN CATALYTIC CONVERTER CAUSE IT TO BURN OUT.SHORTING LIFE OF THE CATALYTIC CONVERTER.

ironian

  • 5 Answers
  • Posted on Aug 31, 2009

SOURCE: Renault Clio Sport 182 Air Con and fan blower fault

I also have a 53 clio with climate control and the fan stopped working. After being quoted £104 by dealership I decided to have a go myself. Bonnet up, remove driverside scuttle cover. Unplug fan resistor 7701051272 (large plug with black wire to fan)remove securing screws and resistor. Dismantled casing and peeled away gel from soldered side of circuit board around mosfet transistor-desolder and remove. Mine was a N342AD 75344G but the nearest I could get was HUF75337P3 from Maplin £1.68. This was the wrong 'package size' but I managed.Close the clamp slightly (before)to hold transistor firmly and then insert transistor and solder. Reassemble. After I got an email from a scrappy QUOTING £20 if you don't fancy the messing about.

image_icon_name.gifIan

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

My Carrier WeatherMaker 8000 furnace is blinking a red light 2 times pauses then blinks red 4 times with a pause between the 4 times

They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST

DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS

11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Low inlet gas pressure
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiatingstatus code recall. After one status code recall is completed component test will occur.

here is a link copy and paste

https://www.fixya.com/support/t6287232-carrier_8000ts


.
0helpful
1answer

Engine light wont go off,replaced oxygen sensor, 4 fuel injectors&fuel fliter &air flow meter , light still on

When the engine light is on (engine running) it means an engine management problem that is likely to affect emissions has been detected.
When this happens the system will switch on the light, store the fault and switch to the emergency get-you-home programme.

The first step in diagnosis is to use a scanner or code reader to discover what code the stored fault is.
0helpful
1answer

My indoor lg mini split unit the cool light flashes 4 time what's wrong

Indoor unit faults = CH04 or C4
Fascia LED's
- RED = None
- GREEN = 4 Flash
Contents = Drain Pump / Float Switch
Case of Error = Float Switch Open Circuit (High Level Water Alarm)
Indoor Status = Off

clean your condensate drain line you can do this with a shop vac,
Read more: http://dgoma.es/multisplit_lg/lg-multi-split-units-error-code/#ixzz34dr3Cu00
Follow us: dgoma on Facebook
0helpful
1answer

Compool cp3400

when the indoor control start the alarm , did you notice any error code display in indoor control like 170 ? POSSIBLE IS THIS control a pool only or pool and spa combination, did you have a pool heater connected to compool 3400 (PENTAIR)
Jun 14, 2013 • Pool & Spa
0helpful
1answer

Turn the console on, displays the xbox screen then screen goes off and a red light starts flashing on console, says system error

is this a single red light? if so, it is a E code error. if there are 2, it is a overheating problem. if its 3, it is a general system error which could be a number of things which you need to figure out the secondary error code to narrow down the problem.
to find the secondary error code:
1. after the red lights start flashing, hold down the "controller sync" button.
2. push the "eject" button 4 times and count the amount of red lights that flash. the red lights will begin to flash rapidly. secondary error codes are only 4 numbers. 1 light = 1, 2 lights = 2, 3 lights = 3 and 4 lights = 4.
after you get the code go to this website, and on the right hand side of the screen under "Xbox Repair Guide" select your PRIMARY error code (1,2,3 or 4 slow flashing red lights). then it will ask you to enter your SECONDARY error code, which is the one you discovered in the steps above.
this will give you a very narrowed down idea of what is wrong with your console, and will give us "questions answerers" a better idea on how to help ya out!
0helpful
1answer

My blower motor comes on but will not turn fan.

May be error code e-4. It's problem with blower motor mechanism fault. Replace if bearings worn out. or replace blower motor.
0helpful
1answer

Compool 3600 Spa side remote

Do not reset while the motor is running. Reset the CP 3600 when the power is on but with the motor off. OK.
4helpful
4answers
Not finding what you are looking for?

359 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...