Six steps of start-up Shangchai generator set :
A.Unscrew the deflation screw on the fuel injection pump, use the fuel hand pump to remove the air in the fuel system, and fix the adjusting control handle on the throttle position of the suitable starting speed;
B.Pressthe generatorstart button to start the diesel engine. If the diesel engine can't start in 10 seconds (up to 15 seconds), it should wait for 1 minute before starting for the second time. If it can't start for three consecutive times, should check and find out the cause of the failure;
C.After diesel generator set start up, the no-load speed gradually increases to 1000-1200 r/min (note not to run at low speed for a long time). After the diesel engine is preheated, the speed is increased to the rated speed. When the outlet water temperature reaches 55 degrees Celsius and the oil temperature reaches 45 degrees Celsius, full load operation is allowed;
D.After starting the diesel engine, pay close attention to the reading of oil pressure gauge (2.5-3.5kg/C?in normal operation). If the oil pressure gauge does not indicate, stop immediately and check whether the ammeter has charge indication;
E.After the diesel generator set is put into normal operation, should observe the changes of water temperature, oil temperature and oil pressure at any time, and should handle the reading of power meter, frequency meter, ammeter and voltmeter in time if abnormalities are found;
F.When each instrument of the genset indicates normally, can turn on the load switch to send power to the load. With the change of load of the genset, if the frequency and voltage are not within the prescribed range, should adjust the frequency and voltage in time to maintain the rated value. It is strictly prohibited that the genset carry load at low speed, so as to avoid damage to the equipment.
SOURCE: no 12v output from aux terminals on a vfx 3648
Pretty sure it won't provide current to start anything. Just provides 12vdc at a low current to pull a relay in.
Manual say it is auto reset on the aux terminals for the generator start relay. 0.7 amps max.
http://www.wholesalesolar.com/pdf.folder/inverter%20pdf%20folder/Outback_fx_vfx_installationManual.pdf
If you still don't have the voltage there at the correct time (when called for), you unit is bad or has a fuse they don't mention in the manual. Remember!! This is a called for function so the voltage will not be there all the time, just when required as per the programming.