SOURCE: Goodman GMP075-3 ignition problem
OK, if the furnace is not lighting for even a few seconds, you have either a bad gas valve, bad wire, bad control module or no gas. The pressure switch is not the issue. Check all wires to the gas valve and look for 24 volts across them when the ignitor glows and you hear the click. Then test for 24 volts to ground. It could be a bad ground wire.
SOURCE: goodman gmnt100-4b wont ignite
I had the same problem. I had to remove a return air duct filter that i had installed and it worked just fine. The system needs plenty of air flow to operate.
Goodman gmp075-3 gas furnace and the flame cycles for 4 sec
SOURCE: Furnace ignitor comes on glows little red gas
Check your conection off the board to the initor and make sure the pins in the plug are set tight with the connection on the board. If you wire nutted the wiring together for the new ignitor you installed check these connection also. Make sure all wire strands at the wire nuts are in the wire nut and not touching or arching on the furances cabinate.
SOURCE: Gas furnace with Honeywell smart valve code error
Hello, it sounds like your Furnace might be shutting off due to your high limit switch.A limit switch will open when the furnace overheats due to low airflow, . check air filter, clean blower wheel, and check to make sure the blower wheel is running at proper speed and not dragging sometimes cause by a weak capacitor. Anything that restricts airflow will cause a limit switch to open.
1. Thermostat calls for heat.
2. Draft inducer motor starts.
3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes.
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas.
Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Please leave feedback... Thanks...
1.
2.
3.
closes.
4.
ignitor closely for cracks. Make sure you do not
limit, rollout switch problem. The furnace's control board