Jerry, you may have a low pressure output on the air pump behind the electric fan motor. There are 2 plastic plugs at the rear cover where the filter is. One is just a plug. If you have a low pressure air gauge say 10-20 psi max, you can remove this plug and screw it in that hole. Do not over tighten the gauge. The other plug increases air pressure when you turn it clockwise, counter clockwise to decrease. this model usually is set around 6 - 6.5 psi. If the pressure does not increase, it may be time to remove the rear pump cover and investigate the filters, rotor & carbon blades.
SOURCE: reddy heat/scheu kerosene space heater no ignition
Typical kero heater uses either a spark ignition or a hot surface. The hot surface igniter is very fragile. A small bump may break the elements. Flame is detected by a photocell, signal is sent to the lockout relay board. Change the igniter costs about 50 bucks.
SOURCE: Reddy Heater runs but will not ignite with bonnet attached.
First, let me say that the general principal of fuel delivery ***to the spark plug*** depends on several things.
On your heater the first step is to set the air pressure to specs. Instructions are on the www.reddyparts.com website. This pressure setting directly affects fuel delivery & fuel atomization
This nozzle rule will only apply if everything is correct as far as fuel delivery applies. The pump pressure must be correct- not almost correct. Set the pressure with a low-pressure gauge that registers12-15 psi max. A gauge with a higher scale just will not read close enough to satisfy the system. If the pressure is not correct, the above rule will not apply. Instructions for setting the pressure can be viewed at http://reddyparts.com/pressure.htm.
SOURCE: RM115 Reddy Heater forced air heater problem
I had close to the same problem i drain the tank added new fuel still no diffrence so i removed the filter going to the tank pick up flushed out with brake clean it work fine for half a day . I knew then i was on the right track . I went to the local hardware store and bought a tune up kit that had the filter in it,I replaced the filter going to the tank pick up and it's been working fine even in cold weather. Fuel quality has a big part to play in it's abbility to burn in colder tempicures.
SOURCE: 150,000 BTU propane Reddy Heater shuts off after ignition
Is there a frost line on your LP tank, if so you may need to replace the tank with a larger tank or refill your tank. This can happen if the tank your using is too low or too small (use 100 lb tank or greater). If there is no frost line it may be an issue with the thermocouple. The manufacturer offers a service manual and owner's manuals on there site. This should assist you... www.desatech.com Thank you
SOURCE: heater will not stay on rm60 reddy heater
When you say the heater is coming on does it actually ignite or is the motor just running until the safety circuit kicks it off? The air pump on you heater should blow at 3.5 to 4 psi which runs up to the nozzle which is a venturi which sucks the fuel out of the tank. The motor will generally run for 20 to 30 seconds trying to ignite. If the flame sensor does not sufficient flame during the time it shuts the motor off. Check these items and let me know what you find.
Here are a couple of tips that I
wrote that tell you how to troubleshoot a Torpedo or Reddy
heater...
Reddy
Heater - Troubleshooting Torpedo Heaters
Torpedo
Heater Pump Pressure Adjustment
heatman101
heater...
Reddy
Torpedo
heatman101
Here are a couple of tips that I wrote that tell you how to troubleshoot a Torpedo or Reddy heater...
Reddy Heater - Troubleshooting Torpedo Heaters
Torpedo Heater Pump Pressure Adjustment
heatman101
heatman101