I have a 20RESAL Kohler generator. It starts but will not transfer. I get a comm error message. Where do I start looking to find the problem?

Posted by on

Ad

1 Answer

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Kohler Master
  • 2,010 Answers
Ad

6 Suggested Answers

6ya6ya
  • 2 Answers

SOURCE:

Hi there,
Save hours of searching online or wasting money on unnecessary repairs by talking to a 6YA Expert who can help you resolve this issue over the phone in a minute or two.

Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.

Here's a link to this great service

Good luck!

Posted on Jan 02, 2017

Ad
  • 77 Answers

SOURCE: ERROR MESSAGES

nthemba- all the error codes you see indicates phone line condition or error at reciving fax's end. For more details you can refer to

http://h10025.www1.hp.com/ewfrf/wc/document?docname=bpu02549&lc=en&dlc=en&cc=us&product=79477&rule=17804&lang=en

Posted on Oct 10, 2008

CarlGehrke
  • 169 Answers

SOURCE: kohler 12kw generator starts but shuts down after 3sec

Your gas pressure is too low and you may not have a large enough supply pipe. You need at least 10 inches of water column with the engine running to operate an LP vapor fueled engine. Because the engine is starving for fuel, its governor opens the throttle to WOT (so it goes to high revs) but there isn't any fuel to make horsepower with so the output voltage falls and the undervoltage alarm trips.

Carl

Posted on Dec 03, 2008

mamicheddy
  • 79 Answers

SOURCE: Hello, I have a Kohler Marine Generator that says OC on the menu when I try to start it. Any ideas?

OC stands for Over Crank. How long does it take before the genset starts?

Posted on May 07, 2009

  • 5603 Answers

SOURCE: kohler confidant 4 generator service manual and wiring diagram

First thing is to check oil level as low oil pressure will shut it down.

Posted on Aug 11, 2009

  • 2 Answers

SOURCE: The monitoring system of our Kohler propane

The monitoring system of our Kohler propane generator has sent a "UU" message. What does this mean as it causes the generator to shut down 10 seconds after starting? Also how can this be corrected?

Posted on Jun 02, 2011

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Service manual 20resal


Contact Nixon Power Services in TN they can supply you with one

Oct 11, 2013 | Kohler 20resa 20kw Home Emergency Backup...

1 Answer

We just installed the Kohler 20RESAL in a open air enclosure behind my clients house and when it's running it's incredibly loud. You certainly can't talk to anyone if you are standing next to it and the...


No be careful !!! the muffler is designed to give a certain engine back pressure and emissions. Changing this or piping it out can increase back pressure to dangerous levels. If you build an enclosure make sure the air flow in and out is sufficient and the hot air out does not get sucked back in as cooling air (short cycle) engine damage and fire can result !

Sep 24, 2013 | Kohler 20RESAL - 20kW Home Standby...

1 Answer

First start up


Try disconencting the remote start wires between the transfer switch and the generator, if ot still does it you have a bad control board. If it stops, then check the transfer switch for correct wiring of utility and generator power wires, also check with an ohm meter if the run contacts in the transfer switch are closed, that would indicate loss of sensing, or bad board

Jul 19, 2013 | Kohler Electrical Supplies

1 Answer

Kohler 20resal 100amp transfer switch RXT will not auto start?


Disconnect generator remote start wires in the ATS. Put an ohm meter across the remote start terminals in the ATS and kill utility power, you should here a click in the ATS and the ohm meter should indicate close to zero ohms. If it does then your ATS is fine and the problem is gen control board or wiring between the two. If it does not show that value, then the start relay in the ATS is suspect.

Feb 12, 2013 | Kohler Generator 20kw 20res W/ 200 Amp...

1 Answer

My Generator will not start up


Will it start manually? if so remote ATS issue, if not check battery

Oct 27, 2012 | Kohler 20RESAL - 20kW Home Standby...

1 Answer

My gen starts and runs for 1 min or so then dies restarts then dies again and again. if i start it under load ( turn on air con) it will run for 10 min then die allen


Is there a fault?? All UL listed generators including Kohler are required to lockout on a fault on shut down. This really sounds like a problem with your 2-wire auto start connection between your automatic transfer switch and genset. RDT model automatic transfer switch it is the 2 middle wires on the green connector and terminals 3&4 in the generator. close to run and open to shut down. Any open at any time will cause the unit to shut down. The 12 will shut down instantly upon an open because your 5 minute cool down is built into the transfer switch.

Jun 27, 2011 | Kohler 12 kW Emergency Power System -...

1 Answer

The monitoring system of our Kohler propane generator has sent a "UU" message. What does this mean as it causes the generator to shut down 10 seconds after starting? Also how can this be...


The monitoring system of our Kohler propane generator has sent a "UU" message. What does this mean as it causes the generator to shut down 10 seconds after starting? Also how can this be corrected?

May 28, 2011 | Kohler 12 kW Emergency Power System -...

2 Answers

I have a Kohler 12RESM1 propane generator with oc/uu code


U need to make sure that the relay driving ur auto start stay closed all thru the crank cycle.

Feb 04, 2010 | Kohler 12 kW Emergency Power System -...

2 Answers

Overcrank error message


The 'overcrank' error simply means it tried to start but never actually started. It cranked for an extended period. Check the fuel and starting issues you would normally check to start the engine.

If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c

Mar 31, 2009 | Kohler 12 kW Emergency Power System -...

Not finding what you are looking for?
Electrical Supplies Logo

Related Topics:

176 people viewed this question

Ask a Question

Usually answered in minutes!

Top Kohler Electrical Supplies Experts

Sheldon Dedek

Level 3 Expert

909 Answers

rjivaro

Level 2 Expert

158 Answers

J. Bradshaw

Level 2 Expert

121 Answers

Are you a Kohler Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...