Question about Kohler Electrical Supplies
Just got a kohler 38rcl generator with a rdc2 controller. can i set the controller to auto in order to exercise automatically even though set up for manual transfer for power.
SOURCE:
CarlGehrke
  • 169 Answers
SOURCE: Generac Guardian 15kW Generator
That sounds just about right, if the relay contacts get welded together it sometimes takes out the driver on the printed circuit board. As you found out, 12vdc from 23 to 194 makes the transfer switch move to the Generator position, relay not energized makes the ATS move to the Normal position.
You can make a nice test function by installing a 10 amp contact switch in series with either the N1 or N2 terminals. When the switch is open the generator thinks the Normal power has failed.
Regards,
Carl
Posted on Jan 26, 2009
CarlGehrke
  • 169 Answers
SOURCE: Gen. set won't auto start.
This sounds a little like a bad wiring problem between the transfer switch and the generator. But before I leap to any unfounded conclusions let's make sure I understand just which Guardian generator and transfer switch you have. The generator I think you have is an air conditioner sized box that has a 2 cyl air cooled Generac GT990 engine in it. The control panel has a 15 amp fuse, and maybe a 7 amp one, some LED indicators, a 3 position rocker switch (manual,off,auto), and a momentary set exercise switch. If you look inside your transfer switch there is the transfer mechanism, a single relay, either 2 or 4 fuses, and a terminal board where 4 small control wires connect to the generator. The control wires will be labeled N1, N2, 193, and 23.
If all of that is true then I'll also assume that the generator is blinking all of the LEDs and as soon as you put the rocker switch in the manual position the generator starts and the transfer switch moves to the "generator" position. It shouldn't do that, manual means switch the switch manually too. :-)
Let's take care of the exercise setting first. Switch the main output breaker of the generator to the "off" position, this prevents the transfer switch from activating even if the generator runs. Next put the generators rocker switch into the "Auto" position and wait at least 1 minute, if the generator starts we have to fix the wiring between the N1 and N2 terminals in the transfer switch and the matching terminals in the generator before we can proceede. If luck was with us and the generator is just blinking its LEDs at you, press and hold the set exercise switch for 30 seconds, you're reseting a "watchdog" type circut so it has to be for the whole 30 seconds. When you let go of the set exercise switch the LEDs should blink another 10 times or so, then the generator should start and run its exercise for 12 minutes more or less and then it'll shut down. At that time the only LED that should be lit is the green "system ready" one and it should be steadily lit. Remember to close the output breaker again.
Next let's address the transfer switch issue. If I've understood you correctly, the transfer switch moves anytime you turn the generator on. The only reason a regular old RTS type transfer switch could do this is that it's being commanded to transfer. It works like this, the 2 coils that move the transfer mechanism get powered by the source we're trying to switch to, once the switch gets into the position it's going a pair of limit switches disconnect it from the power supply so that the coil is only "live" during a transition. Spring loaded contacts hold the switch in either position once it's more than halfway towards either one. The relay inside the box is also in line with the limit switches so that if the relay is deenergised the switch will try to get to the utility position and stay there, it can't if there is no utility power to drive the transfer coil. On the other hand if the relay is energised, the switch will try to get to the generator position and stay there, if there is no power from the generator it can't because the generator is what drives that bottom transfer coil. So I think that for whatever reason the relay in your transfer switch is staying energized when we don't want it to be.
On the terminal board inside the transfer switch you should see terminals labeled 194 and 23, these are the power to the relay coil (194), and the ground to transfer signal (23). With the generator set to off, and a fairly quiet room, disconnect the wire from terminal 23, if you can hear the relay coil click on and off when you touch the wire to terminal 23 there is something wrong with the wiring at the generator end of things. You should also see 12 volts DC between terminal 194 and ground, this comes from the generator too.
If the relay didn't click back and forth above check it by using a short piece of wire to connect terminal 23 to ground, if the relay isn't energised when terminal 23 is grounded and deenergized when terminal 23 is open you either have a bad relay or a problem in the grounding of your system. To get a bad relay fixed for free call up Guardian, register the generator (you'll need proof of purchase), and get them to tell you where your nearest warrenty service person is. If you tell him about this post he'll bring a relay with him when he comes to you.
If you're satisfied that the relay in the switch is working properly, we're on the trail of a wiring problem at the generator end of things. If the generator has just been installed you should carefully check that wire 23 hasn't been connected to terminal 0 at the generator terminal block. It's easy to get this connection wrong when doing th e install. The other thing that can go wrong is that the wire can get pinched inside the conduit and short to ground. To check this disconnect both ends of wire 23 and measure between either one and ground, you should get nearly infinite resistance.
If you've proved to yourself that all of the wiring is correct, and the generator is properly grounded, you probably have a broken control board in the generator. To get the control board replaced use the same procedure as the relay above.
If that doesn't get this resolved for you post a comment and we'll try a different approach.
Regards,
Carl
Posted on Mar 06, 2009
zonker7
  • 78 Answers
SOURCE: AUTOMATIC EXERCISE DOES NOT WORK EVEN THOUGH UNIT IS PROGRAMED
start here:
http://www.online-owners-manual.com/
Posted on Mar 21, 2009
  • 409 Answers
SOURCE: I have a kohler rdt-cfnc-0100b automatic transfer
sounds like the voltage sensor is either mis adjusted or burnt up. Also could be a wire disconnected on the voltage sensor board.
Posted on Mar 11, 2010
  • 909 Answers
SOURCE: 1975, 7.5 Kohler marine genset, runs only with the reset depresed
Can't search for a manual without model, type, serial, etc numbers...
A few things to take a look at:
1) Oil level / pressure sending unit. This is normally bypassed as long as the start switch is pressed. When engine starts, and switch is released, engine will die if sending unit is defective, or you are low on oil.
2) Exhaust temperature sensors. Older units were notorious for burning these up.
3) Cooling Water Temperature sensor. These cause trouble often, but mostly due to water pump impeller being eaten away by galvanic action and not able to pump water as effecively. End result is water temp higher than normal, which trips the switch, which kills the engine.
4) Alternator (generator) output not as it should. If output doesn't rise to proper level within a few seconds of engine start, the engine will be shut down.
5) Choke not working as it should
6) Bad fuel, bad fuel pump, clogged fuel filter.
Posted on Jun 12, 2010
How can I reset the "programmed exercise mode" on my Kohler 12 RES generator
You will likely need to reference your instruction manual for that specific control panel.
Aug 07, 2016 | Kohler 12 kW Emergency Power System -...
Gen runs when switch in auto even though power avail. Tried resetting ATS - waited 30 min. No luck. Only way to turn off is to move switch to stop/reset. Any ideas on what is broken?
have an electrician check the relay that is activated when the utility power fails
that is what starts the genset when it is in auto
it should also stop the get set when utility power comes back on
Nov 03, 2015 | Kohler 17RES 17 kW Generator
Why does my generator start constantly?
if a lightning strike was anyplace close (30 yds) it's a safe bet your gonna have to replace the control board in generator also Id have a qualifyed tech ck out your auto transfer switch ,I bet he''ll find that you fried your coils on your switch too , do that before changing control board cus if ya hook up a new one to a bad coil ya just bought two of them
May 24, 2014 | Kohler Electrical Supplies
Kohler exercise causes engine spikes and gasping for fuel.
On exercise it isn't under load, you may have too much gas pressure, have the gas pressure and fuel/air ratio checked on the mixer
Dec 16, 2012 | Kohler Generator 20kw 20res W/ 200 Amp...
Kohler automatic transfer switch RDT CFNA 0100B. I can set it to exercise and it will do so for several weeks then it forgets. No fault shown.
Product manual does not have troubleshoot section.
The operation might be normal, and within expected parameters, or it might have a glitch.
Suggest you contact Kohler Power directly:
http://kohlerpower.com/contactus/contactus.htm?sectionNumber=
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Sep 29, 2012 | Kohler 100-Amp Automatic Transfer Switch ...
Kohler 12 RES - Unit fails to start occasionally. Attempting a manual start by placing switch in run position, cause a loud click, but no cranking. The panel says CC. This morning I put a jump start...
I finally solved the intermittant starting problem on my Kohler 12 RES by replacing the strater and the starter relay. I was also experiencing the occassional OC indication, red blinking LEDs on the ATS, and intermittent non-starts during the weekly exercises. The problem happened during power outages a couple times also. If I flipped the start switch between auto and run quickly the generator would occasionally start. Once started, the generator runs fine. I ordered a new starter, which included the starter solenoid. By the way, don't worry about the genuine part thing..the old starter was a Delco made overseas. I ordered a new starter online for $85 (6744N) and it was indentical to the genuine Kohler starter. Replaced the starter and it improved the problem but did not totally solve the intermittent starting. Ordered the starter relay (GM49746) replaced it and the problem is solved.
May 09, 2012 | Kohler 12 kW Emergency Power System -...
Will not issue a start signal all of a sudden. How to test to see if it is the switch or the gen. panel
I have a Kohler 12RESM1 whole-house generator with a 200AMP RDT, MPAC 500 Automatic transfer switch (ATS) in my home. The system was installed in 2006 and has been working great since. Several weeks ago I began noticing that the weekly tests weren't occurring on schedule and that the generator would initiate a starting crank for a couple seconds several time a day. The false starts began occurring more frequently as time progressed. (BE very careful!! You will be killed if you are not careful!! ) In order to isolate the trouble between the ATS and the generator, I disconnected the 2 start circuit wires from the ATS controller (2 wires on green connector). The problem stopped, which led me to believe the problem was the ATS controller board. The controller board in my ATS is a GM35950. After removing the board (BE very careful!! You will be killed if you are not careful!! ) and doing a little troubleshooting, I determined the trouble was the set of .47F 5V super-capacitors. These are the 2 black oval-shaped cans behind the relays that appear hot-glued together. I ordered 2 new caps from Digi-key (approx. $4.00 ea). The P/N is PB-5R0V474-R. Replacing the supercaps cured the problem. Don't be fooled, these capacitors are .47 farads, not .47 microfarads, thus the reason they're called Supercaps. They function similar to a battery in this application. Oh by the way, I ordered a couple extra Caps. They have a 1000 hour life expectancy, so I suspect I'll need to replace them again in 6-7 years. Good Luck, I wouldn't advise attempting this job unless you have the proper soldering equipment and are experienced with electronic repair. There's a company that will repair the board for $170. Try googling "Kohler GM35950 repair".
Jan 30, 2011 | Kohler 200-Amp Automatic Transfer Switch...
What is the proper proceidure to set exercise timer on a briggs generator model # 01938 and what year was this model manufactured? thank you
http://www.homegeneratorsystems.com/service_support/manuals/index.cfm?rd=1
This link will take you to their site where you can download their manual.
Setting Exercise Timer
The Home Standby Generator is equipped with an exercise
timer that will start and exercise the system once every
seven days. During this exercise period, the unit runs for
approximately 20 minutes and then shuts down. Electrical
load transfer DOES NOT occur during the exercise cycle
(unless an utility power outage occurs).
A switch on the control panel is labeled “Set Exercise”
(depicted on page 10).The specific day and the specific time
of day this switch is pressed is programmed into the
control board memory.This date and time is then used to
automatically initiate the system exercise cycle.
To perform the Set Exercise procedure:
1. Choose the day and time you want your Home
Standby Generator to exercise.
2. On that day and time, set the AUTO/OFF/MANUAL
switch to OFF.
3. Press and hold down the “Set Exercise” switch for two
seconds.
4. Set the AUTO/OFF/MANUAL switch to AUTO.“Set
Exercise” is complete.
For example, if you press the “Set Exercise” switch on
Sunday morning at 10:00 AM, the unit will run an exercise
cycle the following Sunday at 10:00 AM (+/- 1/2 hour).
NOTE: “Set Exercise” will only work if the unit is in the
Automatic mode and this exact procedure is followed.The
exerciser does not need to be re-set if the 15 Amp fuse is
removed or changed.The exerciser will need to be re-set if
the 12 Volt DC battery is disconnected.
If you want to change the day and time the unit exercises,
simply perform the “Set Exercise” procedure at the exact
weekday and time you want it to take place.
• To prevent possible injury that might be caused by such sudden
starts, always set the AUTO/OFF/MANUAL switch to OFF.
• Remove the 15 Amp fuse before working on or around the
generator or transfer switch.
Nov 12, 2009 | Briggs & Stratton 12,000 Watt Bi Fuel...
My Kohler 17RES has stopped doing it's scheduled weekly exercise. How can I get it exercising again?
On your Automatic Transfer Switch ( the little gray box you see on the right in the picture above) you have two blue buttons. One is a Manual test switch. The other has a clock on it and this is your exercise set button. Hold it down for a FULL 3 seconds if you want it to excercise without a load (not powering your home) Hold it down for a FULL 6 seconds if you want it to exercise with a load every week. Your generator will start and run for 20 minutes, and then shut down. Now every week your generator will exercise at the time and day that you pushed the set button.
Aug 08, 2009 | Kohler 12 kW Emergency Power System -...
Electrical Supplies Logo
116 people viewed this question
Top Kohler Electrical Supplies Experts
Sheldon Dedek
rjivaro
J. Bradshaw
Are you a Kohler Electrical Supply Expert? Answer questions, earn points and help others