I just installed a Carrier Mini-Split and am getting an E2 error code. I have already replaced both boards in the outdoor unit IMP and Main PC with no luck. Any suggestions?
jaimetirado
Level 1:
New Friend:
Welcome Back:
Visited the website for 2 consecutive days.
  • Contributor 10 Answers
  • Posted on Jan 07, 2016
jaimetirado
Contributor
Level 1:
New Friend:
Welcome Back:
Answers
10
Questions
0
Helped
3799
Points
23
This is a Zero crossing detection error. This is alarm signal when the main chip can't detect over zero signal. When such failure occurs, the main control board must have fault.
5 Related Answers
Anonymous
  • Posted on Dec 22, 2008
SOURCE: My Heat will not work
the e2 code on a carrier comfort zone thermostat is indicitive of the external safety sensors which are located on your units ductwork in the attic. the e2 code are the hpt/ and lat sensor codes. the hpt is the heat pump temperature sensor and the lat is the leaving air temperature sensor. you can pull off the cover of the panel and behind it will actually give you all the fault codes associated with you carrier tsat.each sensor has a certain ohm rating and if its out of the range it will fail. now as to the reasons for failure, the indoor coil could be dirty, filters dirty, refrigerant charge incorrect.
Anonymous
  • 1902 Answers
  • Posted on Jun 01, 2009
SOURCE: Fujitsu mini split outdoor unit not running, but indoor unit is running after turnning on
Check the disconnect switch and make sure that both the fuses are good and not shot. If one is shot then the system wont work. There are two fuse. Also be careful due to you will be working around 210 volts
Anonymous
  • Posted on Mar 19, 2010
SOURCE: E4 error code on AUX mini-spit a/c unit
E9 Showing on my split unit a/c
Anonymous
  • Posted on May 21, 2010
SOURCE: ERROR CODE 5 FLASHES CARRIER SPLIT SYST. AIR COND. 42G250HP-1
5 flashing is ' compressor drive' and check the high pressure, condenser fan motor capacitor for proper running
Anonymous
  • Posted on Oct 25, 2010
SOURCE: I have a TCL split system air conditioner with error code E2
I have the same problem with my TCL unit. I have had the Tech out to day and I am told it is an internal senor in the unit that fails. I am informed by the tech that this is a very common fault with the TCL unit. Also if you live in Australia like me prepare yourself for a fight with TCL due to them not liking to honour the 5 year warranty. I would not recommend this product to anyone
What is PC4 error showing on wall mounted receiver Blueridge mini-split heat pomp system?
PC4 is an error code that indicates a communication error between the outdoor unit and the indoor unit of the system. This could be due to a faulty wiring connection between the two units, or due to a defective control board. You should check all wiring connections and, if necessary, replace the control board to resolve the error.
1helpful
Haier mini split E7 and exterior fan not working
On a Haier Split system a E7 error is a failure of the outdoor inverter PCB and the outdoor power supply PCB. Both will need replacing. Looking around $600 for those parts. Plus fitting. The indoor PCB is very unlikely to be needed.
Senville mini split air conditioner error code P 6,
Possible Causes of P6 Mini Split Error Code
Wiring Problem
Faulty IPM Board
Faulty Outdoor Fan Assembly
Compressor Malfunction
Faulty Outdoor PCB Board
A P6 may be caused by wiring mistake, faulty IPM board, faulty outdoor fan, assembly compressor malfunction, and faulty outdoor PCB.
How To Fix or Clear an P6 Mini Split Error Code
Power off the unit and turn off the breaker or disconnect.
Wait 2-3 minutes and power the unit back on.
H4 error code is shown on AC display what can i do to slove this problem
Full list of Gree Air Conditioner Mini Split Units Fault Codes. When error codes appear on the Gree air conditioner indoor display, this tells the user there is an issue with the Gree AC unit. The error code displayed will inform you of the issue or problem that is occurring with the air conditioner. Knowing what the error code means and its definition will help you to understand and troubleshoot the exact Gree air conditioner part that needs to be fixed, cleaned, repaired, or replaced. You can then clean, fix, or replace the Gree part yourself and save money. See below for all error codes that can occur on Gree Mini Split AC's.
Gree Mini Split Air Conditioner Error Codes - How To Fix
Gree Viero AC Mini Split PDF Owners and Troubleshooting Manual
GREE DUCTLESS AIR CONDITIONING & HEATING SYSTEM INSTALLATION MANUAL
Gree Mini Split Air Conditioner Part Names and Locations
INDOOR AND OUTDOOR UNIT
The Gree Air Conditioning Vireo System has onboard error code diagnostics. The outdoor unit will provide status indicators and the indoor wall unit and remote control will display error codes. The following is a summary of the codes with explanations...
GREE AC DIAGNOSTIC ERROR CODES
Gree Vireo Mini Split Air Conditioner Error Code F0
Refrigerant Leakage Protection
1) Refrigerant leak(s).
2) Indoor coil temperature sensor not calibrated.
3) Refrigerant flow is restricted (ex. valve, exv, debris)
Outdoor Unit Red Light Indicator - 9 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E1
System High Pressure
1) Over charged with refrigerant.
2) Blocked or dirty outdoor coil.
3) Extreme outdoor ambient conditions
Gree Vireo Mini Split Air Conditioner Error Code E2
Indoor Anti-Freeze Protection
1) Low return airflow.
2) Indoor fan speed is too low.
3) Indoor coil is blocked or dirty.
Outdoor Unit Yellow Light Indicator - 3 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E4
Compressor High Discharge Temperature Protection
Please refer to the malfunction analysis (discharge temperature, overload) in service manual.
Outdoor Unit Yellow Light Indicator - 7 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E5
Overcurrent Protection
1) Supply voltage is unstable.
2) Supply voltage is too low and system load is too high.
Outdoor Unit Yellow Light Indicator - 5 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E6
Communication Malfunction
1) Communication cable is wired incorrectly between indoor and outdoor units.
2) Indoor or Outdoor control board malfunction.
Outdoor Unit Yellow Light Indicator - Continuous On
Gree Vireo Mini Split Air Conditioner Error Code E8
High Temperature Resistant Protection
1) Incorrect refrigerant charge level.
2) Refrigerant metering device malfunction.
3) Compressor malfunction.
Outdoor Unit Yellow Light Indicator - 6 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code EE
EEPROM Memory Malfunction
Control board malfunction.
Outdoor Unit Yellow Light Indicator - 11 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code C5
System Configuration Malfunction
1) No jumper cap inserted on the control board.
2) Incorrect or damaged jumper cap on control board.
3) Indoor and outdoor units are not compatible.
Gree Vireo Mini Split Air Conditioner Error Code Fo
Pump Down or Gathering Refrigerant Status
Optional Service Mode
Outdoor Unit Yellow Light Indicator - 17 flashes and 1 sec Off
NOTE: All of the Gree Air Conditioner Model Numbers below are applicable for the error codes on this page...
Gree AC Vireo Models: VIR09HP115V1A, VIR12HP115V1A, VIR09HP230V1A, VIR12HP230V1A, VIR18HP230V1A, VIR24HP230V1A, VIR30HP230V1A, and VIR36HP230V1A.
Gree Mini Split Air Conditioner Error Code Charts
Gree Mini Split AC Remote Control Button Names
Gree Mini Split AC Remote Control Icons Display Screen
Gree Mini Split Air Conditioner Air Filter Cleaning Procedure
Need help with error codes on your Gree AC? Please leave a question below and we will be happy to help.
My hitachi inveter split ac green light 9 times blinking and ac not working
Get the model number of your mini split unit (on tag on indoor unit and outdoor unit) Google hitachi error codes. You should be able to pull up a code list for that unit. I believe it may be a communication problem between the indoor and outdoor unit. Possible bad connection of wire going from outdoor to indoor unit
How to check MSG12HRN1W MINI SPLIT SYSTEM electronic board
If your mini split was installed to meet most building codes, an inside disconnect switch should have been installed. This switch breaks the power and signal from the outdoor unit to the indoor unit. It is not the same as the outside disconnect to the compressor (outdoor unit). If it was turned off, the inside unit would be dead. Look for a disconnect switch inside your room. By code is should be within 15 feet of the inside unit.
My mini split system had an E2 code...replaced indoor pipe sensor...indoor unit works but outside unit does not...no other error codes, just motor not working outside
Check the outdoor unit to ensure power is available to it, and the contactor is closing on a call for cool 24-28 volt is present at the contactor coil to activate it.
Soleus dual mini split KFMHP18 fault error F1
F1 error code is a communication failure between the outdoor and indoor units. Check all inter-connecting wires. They should be minimum 14g stranded wire. Make sure all electrical connections are tight. These units are manufactured by CHIGO, you may try to contact them.
Top Carrier Heating & Cooling Experts
Ronny Bennett Sr.
Ronny Bennett Sr.
Jay Finke
Jay Finke
Mike Cairns
Mike Cairns
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others