My Kipor KDE16STA3 shows p03 error after 15 min runing and shuts down after 3 sec.The voltage drops to 30,40 whta's happening?

1 Answer

Claude Kayser

Level 3:

An expert who has achieved level 3 by getting 1000 points

Top Expert:

An expert who has finished #1 on the weekly Top 10 Fixya Experts Leaderboard.

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

  • Kipor Master 9,098 Answers
  • Posted on Oct 31, 2015
Claude Kayser
Kipor Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Top Expert:

An expert who has finished #1 on the weekly Top 10 Fixya Experts Leaderboard.

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

Joined: Jun 15, 2015
Answers
9098
Questions
0
Helped
5063514
Points
28436

[PDF]DIESEL GENERATING SET

www.kipor.com/upload/spec2011053011590766.pdf
3/KDE16STA3/ ..... P-03 Undervoltage: Indicating voltage higher (lower), the generator will self- braking. P-04 Generator ... KDE16STA3 KDE19STA KDE19STA3.

[PDF]2

www.kipor.com/upload/spec2011061109073968.pdf
P-03. Decrease load less than the related load, turn on the breaker. P-04. Replace the fuse of the same type. Check the circuit and inserter. Replace the starting ...

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
3answers

I HAVE A KIPOR 7000 TD generator suddenly stops and shows E-04

Hi,

Usually when errors come up, you can reference the product manual to find out the specific meaning of your error. So, please do this first. If you don't have the manual, please call the manufacturer of your product (ie Kipor) in order to gain information of the meaning. In the mean time, I would advise to shut down the generator or at least use a air volatility detector until you determine the meaning of the error.

Thank you.
0helpful
2answers

What is the p03 code for kipor generator

P01 oil pressure alarm
P02 frequency alarm
P03 voltage alarm
P04 unit overload alarm
P05 start-up fault alarm
P06 emergency shutdown alarm
P07 charging fault alarm
P08 unit overheating alarm PRE-H unit preheating instruction START unit start-up instruction.

Cummins generator and Perkins generator at website: www.dieselgeneratortech.com. power range is 20kw to 3000kw.
0helpful
1answer

Hi. I have a Hayward H350FDN pool heater that is Doing this: • Turn on and Temp at 65 • On for 3 1/2 min then shuts down • Restarts and then on for 5 min, shuts down • Restarts and then on for 2 min,...

it almost sounds like the temperature sensor is in the wrong place. that or the flow is inadequate for the heater to run. if you have a sand filter, put it on 'whirlpool' or 'recirculate' and try to run the heater.
0helpful
1answer
0helpful
1answer

Samsung TV no sound no picture backlight on and off

Check voltage at the power board. After 120 volts enter the TV, there is fuse then a small high voltage transformer, then a 100 uf rated at 450 volts capacitor. There should be 390 volts DC at the capacitor. Without this 390 volts the TV will shut down.
0helpful
1answer

Sanyo DP32640 LCD TV volume will suddenly spike to full, last 3-4 secs., shuts down, restarts at the original settings, holds 5-10 mins., repeats at 5-15 min. intervals

Set has a poltergeist in its main board where you have the setting electronics. Prices have dropped to such a point on this size set that it is simply not worth a repair.
0helpful
3answers

My Kipor KDE19STA3 shows lower voltage on one of three phases in control pannel and keep shutting down. Voltage is actually OK on all 3 phases, if I measure it with my voltmeter. I need to adjust measuring...

There is no way to adjust voltage on just one phase. I would check voltage sensing leads and check to see if there is a way to calibrate. Otherwise it sounds like a logic problem.
0helpful
1answer
Not finding what you are looking for?

1,141 views

Ask a Question

Usually answered in minutes!

Top Kipor Electrical Supplies Experts

john h

Level 3 Expert

29494 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66831 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Kipor Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...