Computers & Internet Logo

Related Topics:

A
Anonymous Posted on Jul 15, 2015

A Eaton 9315 ups 80kVA has Inverter failure and AC Output Over voltage. Any help?

1 Answer

Gruber Power Services

Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Mentor:

An expert who has written 3 tips or uploaded 2 video tips.

  • Expert 176 Answers
  • Posted on Jul 29, 2015
Gruber Power Services
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Mentor:

An expert who has written 3 tips or uploaded 2 video tips.

Joined: Aug 24, 2011
Answers
176
Questions
3
Helped
95508
Points
221

Sound like IGBT. It's a black block looking device mounted directly on the heat sink of the inverter leg. Remember you have 3 legs total to check. If I remember right there are 3 IGBT's per leg. You could also have blown a DC capacitor.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

I have a new Eaton 9390 40kva when i want to start normally it go to bypass mode and give two alarm 1:alarm:configuration alarm 2:notice:ac output under voltage i need to solve it? THANKS

Because till u have alarm of configuration error in your system it won't accept the command it will always go into bypass u have to remove configuration error from ups system only then you are able to use ups system in online mode I can help u to fix it don't worry this is my WhatsApp number feel free to contact me Okk +919871039174
0helpful
1answer

I mistakenly connected energy source at the AC inverter output .Inverter is 5KVA cyberpower inverter.After correcting the connection, It cannot switch from DC to AC( fault signal is displayed on its...

John,

It's shorted out, either replace the part or buy a new one.

If you need UPS, Surge, or Power Related help don't hesitate to contact me!
Daniel • [email protected] • Power & Systems Innovations • 800.260.2259 • www.psihq.com
0helpful
2answers

Is the fuse in a powerware 9135 user replaceble

There are numerous fuses (rectifier, inverter, charger, battery) on the 9135 that are located internal to the unit and not readily accessible to the user. Generally a blown fuse is accompanied by another component failure which caused the fuse to blow in the first place. As a result, additional troubleshooting and testing is usually required to identify the root cause of the failure. This of course leads to soliciting the services of a technician who has access to the schematics, test equipment, and parts to initiate a repair. Without the schematics, it's like working in the dark. For complete support, please contact Eaton (Eaton bought Powerware so now it's the Eaton 9135):

Toll Free: 1 800 356 5737
E-mail: [email protected]

www.eaton.com/9135

0helpful
2answers

Xantrex Inverter/Charger has no AC output

HI

Checking AC Output
1. After the battery voltage and connections have been checked, disconnect the inverter.s AC output wires from
the power distribution system and connect a light to the AC output of the inverter/charger.
2. Disconnect the remote panel to eliminate it as a possible problem.
3. Turn the inverter ON using the power switch on the front panel of the inverter. The 100-watt light should
illuminate. Measure the voltage at the AC output wires using the multimeter. The reading should be 114.126
VAC or approximately 230 VAC if the unit is an international model. If the light does not illuminate, there is
a problem with the inverter. Contact Xantrex technical support.
0helpful
2answers

Hi we have problem with 6kva 9120 eaton ups,

Maybe you have many overvoltage situations at your area, that the UPS can't handle. It's a good idea to put before the ups an overvoltage protection or a stabilizer. Ask the manufacture for the overvoltage protection of the ups that can handle.

Stelios.
1helpful
2answers

How to take ups in manual bypass mode.

You definitely want to follow the manual procedure to avoid a possible load loss:

http://powerquality.eaton.com/Products-services/Backup-Power-UPS/9390.aspx?cx=3

9.1.4 Transfer from Normal to Bypass Mode
To transfer the critical load to Bypass mode:
C A U T I O N
In Bypass mode, the critical load is not protected from commercial power interruptions and abnormalities.
1. Press the CONTROLS pushbutton on the main menu bar. The System Controls
screen appears.
2. Press the BYPASS pushbutton on the System Controls menu bar.
The UPS transfers to Bypass mode and the critical load is immediately supplied
by the bypass source. If the bypass source is not available, the power processor
remains on and an alarm sounds.
3. The UPS is now operating in Bypass mode and the BYPASS status indicator is
illuminated.
The power module (PM) status indicates READY. The system is now on bypass
and the UPS power processor remains on.


At this point, you can operate an external bypass switch to get to maintenance bypass if needed.
0helpful
1answer

Hi i jus need box and speaker specs for the dual 2 ohm 10pw3

General Information Manufacturer: Eaton Corporation
Manufacturer Part Number: 103004248-5592
Manufacturer Website Address: www.eaton.com/EatonCom/Markets/NorthAmerica
Brand Name: Eaton
Product Series: PW3105
Product Model: PW3105 700
Product Name: Powerware PW3105 700VA Tower UPS
Product Type: Standby UPS
Technical Information Plug/Connector Type: NEMA 5-15P
Receptacles: 4 x NEMA 5-15R - Battery Backup System
Switching Time:
  • 6 ms
  • 6 ms
Dataline Protection: RJ-45 Internet
Power Description Load Capacity: 700VA/420W
Input Voltage: 110V AC
Input Voltage Range: 0V AC to 160V AC
Output Voltage: 115V AC
Frequency:
  • 50Hz
  • 60Hz
Management Overload Protection: Circuit Breaker
Interfaces/Ports Interfaces/Ports: 1 x USB
Battery Information Batteries: Maintenance Free Sealed Lead-acid
Backup/Run Time: 3 Minute 420W Full-load
Physical Characteristics Form Factor: Tower
Dimensions:
  • 4.4" Height x 11" Width x 7" Depth
  • 4.4" Height x 11" Width x 7" Depth
Weight: 9.7 lb
Miscellaneous Certifications & Standards:
  • Safety: UL 1778 3rd Edtion/CSAC22.2 No107.3, Designed to meet UL497A
  • EMI: FCC Class B
  • Software Included: Powerware LanSafe Software
    Green Compliance: Yes
    Green Compliance Certificate/Authority: RoHS
    0helpful
    1answer

    How to determine the age of my 9315 and pbIII?

    Call Eaton/Powerware and provide the serial number.
    Not finding what you are looking for?

    659 views

    Ask a Question

    Usually answered in minutes!

    Top Eaton Computers & Internet Experts

    Ngoro

    Level 3 Expert

    3523 Answers

    Brad Brown

    Level 3 Expert

    19187 Answers

    NOEL
    NOEL

    Level 3 Expert

    8606 Answers

    Are you an Eaton Computer and Internet Expert? Answer questions, earn points and help others

    Answer questions

    Manuals & User Guides

    Loading...