franklin payton Posted on Mar 29, 2015
Answered by a Fixya Expert

Trustworthy Expert Solutions

At Fixya.com, our trusted experts are meticulously vetted and possess extensive experience in their respective fields. Backed by a community of knowledgeable professionals, our platform ensures that the solutions provided are thoroughly researched and validated.

View Our Top Experts

My gas furnace is working but the led light will not stop flashing, is it suppose to keep flashing.

It's a day & night furnace, model #N8MSL/N8MSN PS 80. it's blowing Hot Air fine, but the LED light will not flashing?

1 Answer

tractorman44

Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

  • Expert 484 Answers
  • Posted on Mar 29, 2015
tractorman44
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Vice President:

An expert whose answer got voted for 100 times.

Joined: Oct 18, 2014
Answers
484
Questions
4
Helped
205784
Points
843

A steady heartbeat on the circuit board USUALLY means normal operating condition.

5 Related Answers

muttandjeff

Allen Neal

  • 359 Answers
  • Posted on Jan 01, 2009

SOURCE: furnace not blowing air

this may sound not useful but the first thing to try is turn off the breaker or fuse to the feed for the furnace for 1 minute and turn back on and listen and note exactly what it does from there and will have better idea how to help and this might fix the problem try and let me know th results

Ad

Anonymous

  • 5 Answers
  • Posted on Jan 17, 2009

SOURCE: High limit switch open on armstrong furnace

If you know where the high limit switch is you can always cut the two wires and wire them together causing the limit to close. But what you have to watch out for is why the high limit is not closing. That means in your return air either you have a dirty return air duct, dirty filter, or you don't have all your registors open to allow the heat to escape the heat exchanger. Just watch over riding the system. The high limit switch should either be on or behind the blower, in the middle of the system right under the heat exchanger. any other questions about hvac just ask.

David

Anonymous

  • 534 Answers
  • Posted on Apr 16, 2009

SOURCE: Furnace blows cold air, ignitor won't glow.

ok this is going to sound funny but it seems as though the polarity is reversed going into your furnance. to correct this proiblem you first need to unplug the unit and where the cord goes into the furnance at that connection disconnect the two wires. Once theses are disconnected switch the wires .All you are doing is reversing the way the electricity flows into the circut board. I would wager that is the problem

Anonymous

  • 1420 Answers
  • Posted on Dec 01, 2009

SOURCE: Carrier Gas Furnace runs fine randomly stops blowing LEDs flash

That blinking light may be the diagnostic light. Count the blinks next time it fails. Carrier units will have two different blinks depicting the error code such as one blink followed by a pause than 3 blinks giving you an error code of 13. Then look at the wiring diagram, it will have an error code chart telling you where to start with your diagnosis. You already know that if you remove the cover it erases the error code, so look thru the small window first.

Anonymous

  • 1214 Answers
  • Posted on Dec 14, 2009

SOURCE: it keeps turning off but the green led light goes

Please provide a manufacturer name and model number.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Red light keeps flashing on 50e47-170 how do I fix

The red flash is flashing in a pattern, should be a diagram on the furnace panel that shows trouble shooting codes.... led on means you at least have power...
0helpful
1answer

Lennox 80uhg3-75a-3 igniter sometimes doesn't light , left LED slow flash, right LED solid.

Should be a trouble code on the panel or in the literature book that came with unit. More than likely it's on the inside or outside of the blower panel. This will indicate Red light on Green light slow flash = what trouble code or issue it's having. Most common problems with a gas furnace is the flame sensor needs cleaning. There is a little rod that sticks down into the flame when the burners ignite. It's the only thing the flames will come in contact with besides the furnace itself. It will have 1 wire connected to it. Clean that rod with a piece of light grit sand paper. Don't take much force to clean it so try not to damage it by shining it to look like new. Cycle and see if it will hang in there. Hope this helps!
0helpful
1answer

Will not ignite. LED Code 31

Could well be the inducer motor Google carrier 31fault code there are 3 video's on this on u tube
1helpful
1answer

York Diamond 90 furnace blows cold air

There maybe a few issues. They have multiple safeties on furnaces. With this in mind this process to find the problem would take a Technician to check these safeties. It could be a flame sensor or thermocoupler each senses a flame or heat to keep the gas going. Also the damper for the flue must open for the gas to stay on. There may be more safeties on this and each safety sends a 24 volt current back to control module in order for the gas valve to stay open. If these aren't being met it will try around three times and go into a lock out mode which will keep gas shut off entirely.
1helpful
1answer

I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye

Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes

A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61

1helpful
1answer

Suddenly not working im not sure if there even is a pilot to be lit

Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
A sampling of various failure codes on a furnace:

Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.

Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.

Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.


Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.

Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.

Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.



Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.



See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.



Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.

Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.

If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61

0helpful
1answer

The green auto light keeps flashing on the head unit of my a/c and i can not turn the unit on. It has power, it does work, every now and then the green auto led stops flashing and i can use the unit with...

Need model and make of unit? Take off the bottom door of your furnace and there will be a label on the inside or the outside of the door it will tell you what the flashed mean.

1helpful
1answer

Trane gas furnace with White Rodgers 50A50-474 board is flashing a 2 flash code which is a system lockout. The furnace blower contines to run, but the heat stops. I can reset the furnace and the system...

If this is a direct vent unit, check the PVC air intake at the furnace for debris. There is a screen at the furnace connection and as cold air enters into the burner chamber it frosts up on it. If there is any blockage, it restricts the air inlet. If the furnace ignites, it melts the frost and works fine. It happens mostly at night. Let me know if you find this. Thanks.
0helpful
2answers

I have a goodman GMP 125-5 furnace. I have

sounds like the primary limit typically behind the gas valve its larger then the others, rectangle in shape with 2 wires going to it. be careful if your bypassing limit this can create a very hazardous condition
1helpful
1answer
Not finding what you are looking for?

430 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...