The thermostat circuit is responsible for sending power to the compressor for normal operation. Make sure that the thermostat is working and not stuck on open position.
If you hear a hum then a click, that is the compressor short cycling. Put your hand on the compressor in the back, if it is very hot(don't burn yourself) then the compressor is dead and will need to be replaced. If the compressor is cold and not running, check for power through the t-stat and to the freezer. If there is power to the t-stat but not through it then replace the t-stat. If there is power through then there is a good chance the compressor is dead.
You will need a meter. I wouldn't worry too much about the light unless you realy need it. There is a good chance some moisture has got into the connection and ruined the switch. But if you have no light and no compressor running I would have to check where the main connections are for power to the freezer. If you have power to the receiving end of thempower cord then I would move to the t-stat to see if the contacts are closing when you turn it colder. If they do and you have power through the t-stat then move to the compressor. Pull the little black cover off of the compressor when the power is off for safety reasons, then plug it in and check for incoming power to the compressor. If it is there then you may have a faulty compressor or overload or relay. But that is a slim to nun chance. Probubally the compressor. To check the compressor pull all of the wires off of the compressor remembering where they go( unplug freezer first). Then use the ohm meter and chech across all three terminals. Two terminals will have a low ohm reading 1-5. Then the other will be 5-10 the the last will add up the the others if it woes not then the compressor is shot.
Contact a professional. The power supply source needs to be testing to the compressor and see if the power is fine, or if the compressor is faulty and not drawing needed power.
Please check the power feeds to compressor. Use Voltmeter to diagnostic the power. If the power there check the capacitor for malfunction. A defective capacitor usually dented or deformed. Otherwise need to change the compressor with new one
Good day, Sorry, no reset but if the compressor is not running, it could be the thermostat as well. You will need a VOM meter to check to see if power is reaching the compressor. If it is, it could be the compressor overload protector, the compressor start relay, which are both under a cover on the side of the compressor.
Yes a power brown out can cause compressor failure. More than likely If there was a power surge it is possible that the overload on the compressor opened. This is a safty device that helps protect the compressor. It usually resets itself but in the cause of a surge it may have burnt up. problem could also be in the relay or thermostat
simple stuff, you have a compressor a stat and power. check the receptacle to be sure you have 120 volts . then check the compressor with stat at max cold setting to see if you have 120 volts at compressor. if you do then compresssor is bad =new compressor or new unit. if no power to compressor then stat is bad= new stat. i always recomend new unit cause new stat or compressor wont fix a freon leak.... i have replaced a few compressors that died soon after due to a freon leak. good luck...
pretty basic stuff. power cord could be abaded . check to be sure power is reaching the stat with a meter. if it is then check to see if its reaching compressor with a meter, obviously the box is hot so sta t should be calling if power arrives at stat but doesn't come out stat is bad. if it gets to compressor but no run then the compressor start components or the compressor itself are bad. stat has a power in lead and a power out lead. if you check volts between terminals and show 120 the stat is open and bad. if it is set to max cold and failing to send run signalit has to be the stat. if you have power to stat and stat shows no voltage terminal to terminal then its closed and power is not getting to compressor, trace wiring and check .if power is getting to compressor the checjk start cap and relay . if they are good then compressor is bad , usually to expensive to replace.
check light inside .on? you got power. check compressor in back on? if no then you probably have a bad stat. open door and look inside for numbered dial. turn max hot to max cold back and forth. if compressor comes on you need a new stat probably. remember only a stat a compressor on these units. if its hot stat should send power to compressor. if power is arriving at compressor and not running then start relay and or start cap are probably bad. but if compressor is running and still no cool then your probably out of freon. unfortunitly these boxes are made with steel tubing in the cabinets. when you move them lots of times the tubing rusts and ruptures. then your all done. new freezer time. they are sealed to the point there are not even a place to apply gages to check charge. you can gently remove power and then stat and jump thermomstat to take it out of equation and if compressor runs you need a new stat. constant power comes in one side of the stat and when the sensing tube is heated it closes the points to the outlet side and puts power to the compressor. there may also be a ground wire usually green be sure to observe which two are power in and power out. usually side by side. good luck
sounds like an issue witrh the microprocessor to me as well, although you tried bypassing it it still didnt work its quite possible that the fan aand compressor are runnig on different voltagfe the 110v , new energy effient compressors are starting to run w/ 220, an inverter built into the circuit board could be steppin up power,