Where can I find a Love 49 temperature control wiring diagram?

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Kenmore elite chest freezer control not working or illuminating. Good battery. Freezer is working.will replacing control panel fixit? What else may be bad?

It may be a sensor. Don't replace a control center unless you have determined it's bad. The sensor has to be wired to the board controller. Usually smaller cable with 2 conductors. If it has an alarm then there may g e as many as 6 or 8 or more wires going to the board. Using your wire diagram Find the sensor for temp. Sometimes the ohm value is given on the wire diagrams. You will also need the temperature at the point the sensor is connected inside. Your ohm reading should be close to the temp given in a table or from the manufacturer. If it's close sensor ok. Take next step.
0helpful
1answer

What is the standard defrost timer control setting

Usually every 6 hours will keep the evaporator coil clear of frost. I set the time at 45 minutes per defrost. This unit has a defrost termination control that kicks it out of defrost when the coil reaches a certain temperature. The defrost timer is only a backup if the defrost control fails.
2helpful
2answers

My freezer has power, but the fans are not going on when the door shuts and the temperature is rising.

The defrost termination/ fan delay control is a temperature-activated, single pole-double throw switch. ).
The control is wired into the refrigeration circuit. The control is located high on the evaporator where the frost is likely to clear last. The function of this temperature-activated switch is to terminate defrost when the evaporator coil has been defrosted, and to delay the evaporator fans from coming on immediately after defrost.
The coil must reach a temperature of 25* F. for the fan delay to close allowing the fans to operate.bobicehouse_38.jpg
0helpful
1answer

Freezer tempreture drop to -38F even when is set to #3

does the compressor ever stop running? If not, the trouble is in the controls. If it does, the temperature sensor is probably bad. Start there and let me know if I can be of further help.
0helpful
1answer

The compressor stop at 58

Change the temperature control.

http://www.acmehowto.com/howto/appliance/freezer/repair/tempcontrol.php
0helpful
1answer

I have a T-49 freezer with compressor running defrost timer board is showing in refrigeration mode. I have power on the #4 terminal going to the evaporator fans. Both door switches are closed. I am not...

most freezers have 2 controls. 1 is a defrost terminator and the other is a fan delay. the delay and the defrost terminator can sometimes be a "2 in 1" type switch. you would have to study the wiring diagram. The delay will not let the fans come on untill the evap reaches a preset temperature. take another look at the diagram. It may be that the evap is not getting cold enough. you may have a refrigeration issue.
0helpful
1answer

Need wiring diagram for GE model CA15DRN upright freezer-compressor relay busted & not sure which wires go to which terminal on compressor.

http://genet.geappliances.com/DocSearch/pdf/49-6545.PDF
The best I could come up with is this site for the user manual. Not able to find wiring diagram on this GE site. Hope this helps ya.
Nov 24, 2009 • Freezers
0helpful
1answer
Not finding what you are looking for?

127 views

Ask a Question

Usually answered in minutes!

Top True Freezers Experts

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66835 Answers

Are you a True Freezer Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...