Possibly a tstat issue. Run system until satisfied, once satisfied indoor fan shuts down compressor still runs remove tstat face plate and see if compressor shuts down. Another issue could be a sticking contactor for compressor. With a meter you could check at the contactor to see if you lose your 24volts for cooling but contactor remains pulled in.
Do you hear a click sound as the compressor shuts down? If so that is the clixon (heat sensitive circuit breaker) that is opening and shutting down the compressor when it overheats. You have not had the AC filled with refrigerant so overfilling the unit cannot be an issue.
And if it is not overfilled overheating is caused by excessive current going into the motor which could indicate a problem with the motor windings..
OR, If the thermostat is faulty it could be prematurely shutting down the compressor. If you jump (bypass) the therm and unit does not shut off then you have found the culprit.
My central AC unit decided to stop on the hottest day of the year. It would start and run normally for a few minutes and then the blower would shut off. After checking the breakers, thermostat and overflow shut off (did not have one) I saw something about a blower motor capacitor. This was easy to get to and replace and my last hope before waiting for someone to come fix it. The capacitor cost $4.04 with tax and had my AC working again. Needless to say I was beyond happy. I hope this can help others with a similar problem.
I had the same problem,if you do not monitor that you will make matters worst and burn the Compressor.your problem is the blower unit it has three speed sometimes four.it needs to be changed..
possably a problem with the outside condensor fan motor. Pls check
1.) when unit is running is the outside fan motor also runnng. My guess is the outside fan is locked bad motor ect. Unit would only run maybe 30 seconds before cycling on its overload
Goodman unit you can use a 1/4 hp or 1/3 hp cond. fan motor but it does sound like a cap. Replace cap first. Its very easy to do just open up panel and replace the silver bullet with terminals out the top. It will say on the side what size it is like 40uf 5uf or something like that. Thats most likely your problem. Russ
which fan shuts down? Outside condensor fan? Or blower inside? If its the outside condensor fan motor you probably have a bad run capacitor or a bad condensor fan motor
Capacitor, dirty condencer coil causing the motor amps to run too high. But most likely worn bearing on blade side of motor causing it to pull to one side causing it to over heat and shut down. Sleve bearings should have no side play.
Is the condenser fan (outside) turning? You mention that it's hot but don't say if it's turning or not.
These fan motors normally run pretty hot, but not so much that they shut down due to internal thermal overload protectors.
Both the compressor and the fan have termperature overload protectors to keep them from burning out the motor in the event of an overheated condition. The condenser fan must be running or high freon pressure will put an excessive load on the compressor and it will 'kick out' the high-temp overload protector.
Turn off the unit by pulling the outside disconnect (in a small box near the outside compressor unit) or flip the AC breakers in the breaker box. Wait about 30 minutes for the unit to cool off and turn it back on. If the compressor and fan both run for awhile then kick back off, or the fan motor seems to be working under excessive strain, you've probably got a bad motor start condenser (inside the unit) that little round can that is connected through the fan motor wiring. If it's swollen or leaking, it's almost surely defective and even if it's not, excessive load on the motor is a classic sign of a bad start condenser.
You can usually find these at electrical supply stores, well-stocked hardware stores, or most certainly at an HVAC parts house. Be sure to replace the old one with one of the EXACT same value (in voltage and Microfarads (mF) capacity. The shape may be a little different, but as long as the electrical characteristics are the same and is rated at the same or higher voltage than the original, it will work.
Connect the new condenser, mount it to the frame, and restart the unit. This should take care of the problem.