Panasonic heat pump cs-te12hke control cable has had the neutral and control wires cross connected (2 and 3). The indoor unit starts and errors with code H11. Was installed by electrician who has crossed wires, he doesnt know that I have checked what he did wrong. Will this have caused damage to the unit, either indoor or outdoor? Should i demand new indoor and outdoor units?

  • Anonymous Mar 13, 2014

    cut off outdoor unit

×

1 Answer

Anonymous

Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Governor:

An expert whose answer got voted for 20 times.

Hot-Shot:

An expert who has answered 20 questions.

  • Expert 52 Answers
  • Posted on Jun 08, 2009
Anonymous
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Governor:

An expert whose answer got voted for 20 times.

Hot-Shot:

An expert who has answered 20 questions.

Joined: May 07, 2009
Answers
52
Questions
1
Helped
52124
Points
122

I would not do anything just yet It might be more prudent to call Panasonic help line, and explain your findings I feel that the system will not have suffered any damage if the control cables have been simply wired incorrectly if that is the problem, try and find a call number from your installation paperwork, good luck.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

On a Panasonic air conditioner split system cs-e12jkr is not turning on timer light blinking done a code check and H33 come up what can I do to fix this cheers

This error is:
Indoor / Outdoor wrong connection
Check that the wiring between the indoor and outdoor have not been crossed over, ie make sure that the same color wire connects the same terminal number on both the indoor and outdoor. After that, check that you are getting full supply voltage to the system. High resistance somewhere in the circuit may not provide sufficient power. Corroded isolator contacts or wire terminals for instance.
1helpful
1answer

How do I remove the Main PCB from an LG ArtCool C12AWR or disconnect air sensor of indoor unit ?

Disassembly - Indoor Unit
Disconnect the unit from power supply before making any checks.
Be sure the power switch is set to "OFF".
To remove the Grille from the Chassis.
• Set the up-and-down air discharge louver to open
position (horizontally) by finger pressure.
• Remove the securing screws.
• To remove the Grille, pull the lower left and right
side of the grille toward you (slightly tilted) and lift it
straight upward.
1. Before removing the control box, be sure to
take out the wire screwed at the other end.
2. To remove the Control Box.
• Remove securing screws.
• Pull the control box out from the chassis
carefully.
3. To remove the Discharge Grille.
• Unhook the discharge grille and pull the
discharge grille out from the chassis carefully.
4. To remove the Evaporator.
• Remove 3 screws securing the evaporator(at the
left 2EA in the Eva Holder, at the right 1EA).
• When repair, do not damage the Caution label.
• Unhook the tab on the right inside of the chassis
at the same time, slightly pull the evaporator
toward you until the tab is clear of the slot.
5. To remove the Motor Cover
• Remove 2 securing screw.
• Pull the motor cover out from the chassis
carefully.
6. To remove the Cross-Flow Fan
• Loosen the screw securing the cross-flow fan to
the fan motor (do not remove).
• Lift up the right side of the cross-flow fan and the
fan motor, separate the fan motor from the
cross-flow fan.
0helpful
1answer

Panasonic mini split air conditioner css9nkua. what does run code h99 mean?

H99: Indoor heat exchanger anti-freezing protection
Causes: - Insufficient refrigerant;
- Air filter dirty;
- Clogged cross flow fan.
0helpful
1answer

Panasonic CS-A12DKD Air conditioner does not

This could be an inoperative reversing valve or bad reversing valve solenoid coil.
0helpful
2answers

Laing circulation pump for Saratoga spa. Put in new pump but now tripping GFCI.

Check your wiring! If it wasn't tripping before and now it is, you have your hot and neutral crossed or neutral and safety ground crossed. You can not draw current via the safety ground, that is what caused the GFCI to trip, it senses current being drawn in that wire.
1helpful
1answer

I have an LG split system air conditioner model number LSZ244VN-4 it is coming up with a fault code of CS after it has been running for approx 5 minutes

There is no CS code. Please read as C5.
Fault Code 05 and 53 (CH05 is displayed at indoor unit, 53 is displayed at outdoor unit)
This fault code indicates a communication error between the indoor and outdoor units; this is usually caused
by wiring errors or condensate pumps connected to the inter-connecting cable.
The communication between the units is a fluctuating DC voltage commonly called a serial signal, it can be
easily lost if the wiring is not done correctly. If there is a communication error fault CH05 will appear within 5
mins of powering up the system.
Testing
• Check Outdoor and Indoor Power Supply Voltages ( 230V ±10% ) and correct as necessary.
• Check for any mis-wiring or loose connections and correct as required.
• Check the resistance between communication line and GND. (Normal: Over 2M).
• If one Indoor unit operates normally Outdoor PCB is generally normal.
Turn on the power and start the indoor unit in cooling, set the temperature to 18ºC; the serial communication
signal will only be present for the first 3 mins of operation.
Set your meter to DC Volts, Test between terminals 5 (Red probe) and 2 or Earth (Black probe) of the outdoor
unit, you should see a fluctuating 0-72 Vdc.
If the Voltage is not present disconnect the terminal 5 cable, test the Voltage between this wire (Red probe)
and 2 or Earth (Black probe), you should see a steady voltage in the range of -0.1 to -10.0 Vdc. If No Voltage
is present either the cable or Indoor PCB must be faulty. This can be determined by checking the voltage
output on the Comms terminal of the Indoor unit, with the Comms wire disconnected. If No Voltage is present
the Indoor PCB must be faulty, if present, cable must be at fault.
0helpful
1answer

Panasonic air conditioner CS-E24GKR...The unit stops and the timer indicator blinks. Also displays error code H 11...Help...Please...its hot in here

H-11Indoor / outdoor abnormal communication. Check • Internal / external cable connections
• Indoor / Outdoor PCB
1helpful
1answer

Connecting new 5 wire low volt to an old 4 wire L/Volt

You will have to change out the thermostat wire if you do not have another wire in the sheath you can use.
You must have 2 wires for 24 volts hot and neutral. Usually red and blue.
Yellow for the compressor contactor.
Orange for the reversing valve.
White for the indoor heat coil relay.To bring on indoor coil when in defrost mode.
0helpful
1answer

Panasonic cs-pw9gke i need wiring diagram

Split A/C-Cold:

You need four wires(two #10 and two #12) to the outdoor unit, leaving you house, and three wires(#10) coming from the breaker to tye indoor unit inside your house.

Split A/C-Cold and Hot:

You need five wires(two #10 and three #12) to the outdoor unit, leaving your house, and thee wires(#10) coming from the breaker to your indoor unit inside your house.

This ypical arrangment(all of them use three wires fro the breaker), yet there are other units which may require 6-7 wires connected to the the outdoor unit depends on the added features to the unit.

Regards,

Gulftecheng
Not finding what you are looking for?

535 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...